Use of 60 Hz m/cs on 50 Hz system

03/06/2010 12:30 PM

We are in the process of getting a lot of MV induction motors as part of equipment supplies by an overseas company. All their induction are designed for 460V/ 60Hz, which we in India need to operate at 415V/ 50 Hz. I have two questions: (a) what are the major issues in running these directly on our 50Hz system and (b) if indeed there is any issue (say like saturation etc), what's the most sound techno-commercial approach to the problem.

Many thanks in anticipation

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#1

Re: Use of 60 Hz m/cs on 50 Hz system

03/06/2010 1:14 PM

As long as the V/f is maintained constant, the motor stator laminations / core is safe.

Speed ofcourse is going to be lower as it is proportional to frequency.

Torque is proportional to square of V and hence will be lower.

Motor cooling will be lower as the shaft mounted fan is going o run at lesser speed. Hence, temperature rise of the motor will be higher and may call for derating.

That's all I can think of with my limited knowldge of motors.

__________________
Raghunath
Reply Score 1 for Good Answer
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#2
In reply to #1

Re: Use of 60 Hz m/cs on 50 Hz system

03/06/2010 2:55 PM

This is one of the common questions asked in CR4. There is a very good general discussion on this topic in thread http://cr4.globalspec.com/thread/33399. Hope you will find the required information.

Here is the summary of this discussion:

In order to keep the flux within limits, a linear V/F ratio must be maintained. If the frequency is reduced by 10%, the voltage must also be reduced by 10%. Since the flux remains the same, the torque capacity remains same and thus the power rating of the motor also drops by same %. Provided the voltage is dropped by the same proportion as the frequency, it is OK to run a 60Hz motor on 50Hz. The speed will be reduced by the reduction in frequency and the power capacity will also reduce by the reduction in frequency.

Maintaining V/f (voltage / frequency) will maintain same magnetic flux. However due to 17% reduction in frequency (50/60)

- The motor turns 17% slower.

- The internal current goes up by 17% to maintain the same flux.

- The power (watt) goes down by 17 %

- The mechanical cooling is less, because of 17% less rotation of fan.

- The result is a higher current, than designed and the insulation of the electrical wiring deteriorate much quicker, unable to dissipate the heat, which after sometime results in a burn-out.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Reply
Member

Join Date: Nov 2007
Posts: 7
#3
In reply to #2

Re: Use of 60 Hz m/cs on 50 Hz system

03/06/2010 10:46 PM

Many thanks MS for the prompt response. The various technical issues relating to use of 60 Hz machines on 50 Hz system are well explained. But my real question is what is the most techno-commercially viable option if i were to use the machines without sacrificing on the speed, flow rate, head etc of the original machines. Would a VVVF or say a FCMA (flux controlled magnetic amplifier) ensure that and if so what spec do I draw up for these?

Regards

Tilak

Reply Off Topic (Score 4)
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#4

Re: Use of 60 Hz m/cs on 50 Hz system

03/09/2010 7:35 PM

Most of the problems are burnt windings, due to less everything, just about 17-20 % of what you can expect from a 60 Hz net. Heat dissipation will keep you busy replacing these. A frequency converter 50 to 60 may help.

__________________
Plenty of room here
Reply
Member

Join Date: Nov 2007
Posts: 7
#5

Re: Use of 60 Hz m/cs on 50 Hz system

03/10/2010 12:20 AM

Thank you all for your responses.........the answer to my fundamental question, however, is still elusive....and that is:- is there a techno-commecrially sensible solution that will allow me to have the same Head/Flow/Throughput of the driven machines if I were to use the 60 Hz drive motors on 50 Hz system. Any specific charecteristic VVVF drive or FCMA (Flux conterolled mag amp) etc? Shall look forward to some help on these lines.

Tilak Ghoshal

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6
In reply to #5

Re: Use of 60 Hz m/cs on 50 Hz system

02/14/2023 6:29 AM

No, there isn't.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Reply to Forum Thread 6 comments