earthing of current transformer

03/06/2010 4:30 PM

why we must earthing one secondary side of current transformer

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Member

Join Date: Nov 2007
Posts: 7
#1

Re: earthing of current transformer

03/06/2010 11:12 PM

I think it's a safety precaution against possible 'open circuit' on the CT secondary side, which can lead to generation of dangerously high voltage.

Tilak

Register to Reply
Commentator
India - Member - New Member Engineering Fields - Electrical Engineering - New Member Technical Fields - Technical Writing - New Member

Join Date: Feb 2010
Location: India
Posts: 92
Good Answers: 2
#2

Re: earthing of current transformer

03/07/2010 12:26 AM

It is provided to flow the earth fault current.

Register to Reply
Anonymous Poster
#3

Re: earthing of current transformer

03/07/2010 1:35 AM

Check previous threads. covered many times.

Check your text book,

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#4

Re: earthing of current transformer

03/09/2010 8:47 AM

During a secondary open circuit on one CT, a very high transient voltage would appear across all the three phase CTs as they are interconnected through the loads. If you earth one terminal of the secondary of all the three phase CTs, the insulation need to be done only for phase voltage and not for line voltage. This greatly reduces the size and insulation cost of the CT. There is a dedicated IEEE Standard on this topic.

Register to Reply Score 1 for Good Answer
Power-User

Join Date: Oct 2008
Location: Jakarta Indonesia
Posts: 123
Good Answers: 7
#5

Re: earthing of current transformer

03/13/2010 2:14 AM

Dear all,

CT Primary and secondary is linked though stray capacitance and resistance of insulator.

If CT secondary is not earthed, the primary voltage may induce high potential in secondary winding. Too keep the secondary voltage as we wish such as 110V against the earth, secondary must be earthed.

Regards

__________________
Akihito Shigeno @ JGC-Indonesia
Register to Reply
Register to Reply 5 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard