I am working on the earthing of a gas power station,when the resistivity test was done some years ago it was laterite that was present in the chosen location.later on the location was sand filled with white sharp sand and now i am looking for the best possible way to reduce the soil resistance.What i have in mind is to add more rods in parallel,but, my big question is how to add them in parallel and how do i knw how many rods(test wells) i need to add to make up and get the required resistance i want.presently i have not gotten to this level yet but i think i should plan ahead.
Design details(in accordance with laterite sand)(IEE std 80-2000)
Total enclosed area-43500
soil resistivity-143.29
RmS value of symetrical fault current-31.5KA
size of conductor -150mm2
duration of fault current for sizing conductor-0.5 sec
surface resistivity-500 ohm metre
spacing between conductor mat-7m
no of concrete test well -4
rod lenght-3m
diameter-2cm
resistance of earth grid (calculated)-0.33 ohms |
|
NB
can anyone help me with a soft copy of the IEEE standard 80?i'll be very pleased.you can send it to benotype@yahoo.com |
|
|