Motor Effeciency

03/16/2010 5:32 AM

Is the effiency of a LT motor(415V,3Ph,50Hz) will be decreased after rewinding? If so how much will be counted percentage wise for future loading of the motor. No staggering of cores have been done during rewinding process.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#1

Re: Motor Effeciency

03/16/2010 8:07 AM

If the rewind shop is good at what they do there should be no degrading of the motor.

Some motor winding designs can be improved on as well so it may be possible to increase the power and or efficiency of a motor at times as well but only the rewind shop can tell you if your motor is capable of having that done.

Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#2

Re: Motor Effeciency

03/17/2010 3:26 AM

your motor should be rewound exactly the same, the rewind shop if they don't have a coil layout should take the motor coils out one by one, note how they are fitted into the stator and copy the layout making notes and drawings in case they get this motor again. By copying and ensuring they have the same CSA of wire used, the same number of turns in each coil, the coils are installed as they came out, then there will be drop in efficiency.

If there is a problem with the gap between the rotor and stator, then that will have an adverse effect on the motor efficiency

__________________
The square root of nothing is what you make it!
Register to Reply
Anonymous Poster
#5
In reply to #2

Re: Motor Effeciency

03/19/2010 2:25 AM

I am agreeing with Brich...so not to derate efficiency, motors should be rewind with the same manufacturer's winding data; such as lenght of winding coil, original insulation or if not much higher insulation than the manufacturer. You should also take good care of the motor laminated slots when rewinding so as to get back the rated efficiency.

Register to Reply
Power-User

Join Date: Jul 2008
Location: UK
Posts: 205
Good Answers: 50
#3

Re: Motor Effeciency

03/17/2010 6:09 AM

Yes, the efficiency will drop, how much it drops will depend on the disassembly, reassembly and curing process and temperatures used. The characteristics of the stator will be affected resulting in an efficiency drop in the order of 2 to 5% depending on care taken and the process used.

This means an original motor of 88% could now be 85% efficient, as a rough guideline.

If the process is harsh and less well controlled, particularly the oven and temperature gradient control, this could be much worse than above.

__________________
Something new every day!
Register to Reply
Power-User
Belgium - Member - New Member

Join Date: May 2007
Location: Flanders (Belgium)
Posts: 343
Good Answers: 21
#4

Re: Motor Effeciency

03/17/2010 6:52 AM

During more than 30 years, we repaired electrical motors. We never had problems with less efficiency of a repaired motor.

Mostly we also use copper wire and isolation material which can stand a higher temperature. Isolation classe H against isolation classe F or B.

In those cases the motor will survive much longer an overload before burning, in case there is something wrong with the machine driven by this motor.

The motor protection has much more time to react, before the motor burns.

Also when heat exchange is not good because it is a hot sunny day outside, the motor will last longer.

In some cases we actually change and improve the type of winding (one layer versus two layer winding) to obtain less 5th and 7th harmonics.

This gives us a better motor after rewinding.

Register to Reply
Register to Reply 5 comments
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); brich (1); MalcolmK (1); rudy.leurs (1); tcmtech (1)

Previous in Forum: 200-kW Mill Motor and 250-kVA Genset   Next in Forum: Current Transformer
You might be interested in: Cores and Tubes, Motor Repair Services, IP Cores

Advertisement