Utility Bill and System Load

03/17/2010 10:32 AM

I have a utility bill for a site. It says the demand is 113kW. If the site is using 480V.. Does that mean the load is 135.91A?

113,000 / 480 * 1.732 ?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#1

Re: Utility bill and load on system

03/17/2010 11:16 AM

You need to allow for Power Factor, Captain, which will make it more. Divide by the cosine of the phase angle between the voltage waveform and the current waveform. Also, I'd drop some of those least-significant-digits if I were you.

__________________
Good moaning!