Transformer Sizing Calculation

03/17/2010 11:19 AM

Hi,

Can anyone please help me in finding out the absorbed load, continous load and intermittent load of different motors ranging from 996kW to downwards. For transformer sizing calculation which of these loads are to be considered. The transformer is mainly to feed motor loads ranging from 996KW to downwards and few lighting loads.

Thanks.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#1

Re: Transformer Sizing Calculation

03/17/2010 12:07 PM

If it already exists, then you need to do a survey. Are there any on-site meter readings to help, Captain, and what does the system look like? Nearly all motors have a rating plate on them, which gives its maximum power consumption and may give an idea of the power factor you can expect from it. The lighting loads are going to have a power factor as well, ranging from near-unity for incandescent lighting to something far off for fluorescents. You need to factor in the diversity, which means that not all loads are on at any time. Power factor correction equipment, if present, will help. Meter readings off the transformer will help, but it's a huge pain gathering all the data together.

If it doesn't exist yet, then you need to add up all the design loads and apply a diversity factor. Are you putting power factor correction into the design? Then you need to add a bit more on to allow for future expansion to obtain a preferred transformer size. Then go to the next-one-up at the transformer vendors' literature. Good luck!

__________________
Good moaning!
Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#2

Re: Transformer Sizing Calculation

03/17/2010 12:13 PM

You can use this formula:

Transformer Capacity in MVA =

(Total Continuous Load in KW + 60% of Total Intermittent Load in KW + Largest Standby Load in KW + Future Reserve Capacity in KW) / (0.8 x 1000)

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Reply Score 1 for Good Answer
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#3
In reply to #2

Re: Transformer Sizing Calculation

12/15/2010 6:50 AM

Dear sir

For sizing of the transformer the formula indicated by you is in order.Can you substantiate this by giving some IEC/IEEE reference.

I have a problem with one of my vendors, he is not prepared to accept this.If the same thing indicated in any of the standards I can reproduce then my job will be easier.

Please help.

__________________
Ramesh,Freelance Electrical/automation Consultant
Reply
Reply to Forum Thread 3 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Crabtree (1); msamad (1); ramvinod (1)

Previous in Forum: Utility Bill and System Load   Next in Forum: CT Saturation Current

Advertisement