How to Calculate Conductor Size

03/19/2010 6:08 AM

if i have a pdb at switch yard and my mcc panel is located at a distance of 50 mt and my load pf is 0.85 and load is 800kw what would be the cable size

How can i calculate for any other application.

Register to Reply
This discussion was "closed" on 03/20/2010 9:38 AM. No new comments are allowed.
Message from admins:
CR4 is not a homework help site - some answers have been provided.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: How to caliculate the size of the conductor

03/19/2010 6:15 AM

British Standard 7671.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Off Topic
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: How to caliculate the size of the conductor

03/19/2010 6:23 AM

It depends particularly on what the voltage is. (Half voltage requires double current.)

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Member

Join Date: Mar 2010
Posts: 5
#3
In reply to #2

Re: How to caliculate the size of the conductor

03/19/2010 7:44 AM

the voltage for the system is 3-phase 415v

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#4

Re: How to Caliculate the Size of the Conductor

03/19/2010 9:32 AM

It always depends on site location and the variety of environmental concerns. These will be spelled out in the wiring standards for your location. But knowing what cabling reference is required and being authorized to select from the reference those cables are two different things. Hire a licensed electrician or electrical engineer to do this work. To many facilities have burned to the ground because untrained people thought that they understood these cryptic codes.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#5

Re: How to Caliculate the Size of the Conductor

03/19/2010 11:32 AM

It would be unprofessional and irresponsible to do the math for you, since you obviously are not qualified to perform the work.

I agree with redfred but would add that people's lives are at stake here. Do you want to be responsible for that if your wiring burns the building down.

Ask your insurance carrier, if you have one, what they think of unqualified people performing electrical installations.

Register to Reply
Member

Join Date: Mar 2010
Posts: 5
#8
In reply to #5

Re: How to Caliculate the Size of the Conductor

03/20/2010 12:10 AM

hello boss if u know the answer tell me or else no need to give such advices for me anyway thanks for ur valuable suggestion

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#11
In reply to #8

Re: How to Caliculate the Size of the Conductor

03/20/2010 8:21 AM

tel4fun,

This web site has for a good reason a rule against doing student's homework. Now the members do occasionally answer a student's question when the student clearly shows that the student is doing most of the work already and just needs a little guidance. You've not demonstrated this.

Now your question might not be homework. In this case there are a variety of wiring standards that are location specific. There are also a collection of logistic questions that need to asked and answered for a proper installation. You've not mentioned any of these concerns. The only information that you've offered is the length of your cable run and that this is a lethal amount of power. You don't even identify what voltage you have at your source or how much of a voltage drop you can accept at your load. This does demonstrate that you know nothing about electricity. This is why you need a licensed electrician or electrical engineer to help. Anybody around this work can be killed by a poor installation.

As I typed this long reply, it dawned on me that there is a third possibility. You may have a bar bet that there's a simple formula for calculating which cables are needed for this run. Well there isn't one, you lose the bet. Pay the bar tab.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Anonymous Poster
#6

Re: How to Calculate Conductor Size

03/19/2010 11:21 PM

First Calculate the Current of the Load (i.e) 800kW from the Power Equation P = 1.732 V I Cos(theta) in Watts, convert to kilo watts accordingly. Then take the distance (i.e) 50 mtrs. Calculate the Voltage drop from MCC to PDB for the distance.

If there is a voltage drop, then work accordingly to the new voltage reducing the voltage drop. Now your current will go up.

Now Refer any reputed Cable manufacturer's data sheet for the final current you arrived after the voltage drop calculations. Confirm your cable laying medium (Air, Ground or Concealed in pipes) which decides your derating factor.

From the Mfr's Cable Selection Tables, now can get the Cable Size.

Also you have to consider the Short Circuit kVA or MVA and Short Circuit Current that is going to be involved in that Cable route.

I am sure, but you can take 3 to 6 times the current value you got after voltage drop calculation as Short Circuit Current. For the Short Circuit kVA / MVA you have to consider the kVA / MVA and Voltage rating of the Power Transformer.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Apr 2006
Location: Cincinnati, Ohio, USA
Posts: 662
Good Answers: 49
#7
In reply to #6

Re: How to Calculate Conductor Size

03/19/2010 11:47 PM

DISREGARD THIS POST.

While the basic calculations are correct, LITTLE things like the available short circuit current and the required appropriately sized breakers/switches cannot be guessed at or use rules of thumb.

Go back to the two previous posts and DO THE RIGHT THING. There is no way ANY engineer should try to do what he/she is not qualified to do, and reading a manual on how to do it DOES NOT QUALIFY YOU TO DO DESIGN WORK. It will help you assist the qualified designer to do their work for you.

This is just like an attorney representing himself- he has a fool for a client. However, in this case, foolishness can really hurt someone else.

__________________
NO MATTER HOW WELL YOU HAVE DONE SO FAR, ALWAYS TRY TO BE BETTER TOMORROW.
Register to Reply Score 1 for Good Answer
Member

Join Date: Mar 2010
Posts: 5
#10
In reply to #6

Re: How to Calculate Conductor Size

03/20/2010 12:15 AM

Thankyou very much

Register to Reply
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#9

Re: How to Calculate Conductor Size

03/20/2010 12:13 AM

I think you'd better calculate the size of your load, then according to where you use it, find a suitable size in the cable, or conductor wire catalogs of suppliers. You will need stiff or more flexible, isolation X,Y,Z. The conductors have been calculated for you. Take one that handles your load.

__________________
Plenty of room here
Register to Reply
Register to Reply 11 comments
This discussion was "closed" on 03/20/2010 9:38 AM. No new comments are allowed.
Message from admins:
CR4 is not a homework help site - some answers have been provided.

"Almost" Good Answers: