Measuring Closing Time and Tripping Time of Breaker

03/22/2010 2:08 AM

Hello all,

While during overhauling of our breakers recently(MOCB) ,we measured closing time and tripping time of the breaker using an apparatus.for measuring the same,we made a shoring b/w bottom of r-pole to the top of y-pole,why?.I could not fing anything in the manual,does anybody know the reason?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Jul 2007
Location: Commissariat de Police, Nouvions, occupied France, 1942.
Posts: 2599
Good Answers: 77
#1

Re: Measuring Closing Time and Tripping Time of Breaker

03/22/2010 8:04 AM

Ah! Is this a 3-phase device being tested on a single phase supply, Captain? If so, then it's showing you the earliest opening time of any of the three contacts.

__________________
Good moaning!
Reply
Anonymous Poster
#2
In reply to #1

Re: Measuring Closing Time and Tripping Time of Breaker

03/23/2010 7:11 AM

There is a product called the profile by Kelvatek which measures both single phase and 3 phase circuit breaker trip time. Was this the device you used? If so contact the manufacturer customer service as they know there stuff. There contact should be on their website.

If its a different device then cant help sorry:( but crabtree's comment sounds about right.

Reply
Guru

Join Date: Feb 2006
Posts: 1758
Good Answers: 6
#3

Re: Measuring Closing Time and Tripping Time of Breaker

03/23/2010 10:19 AM

Can you give a simple sketch.

A diagram is much better than thousand words explanation.

How the test-Jig is wired ?

Reply
Power-User
Engineering Fields - Power Engineering - New Member

Join Date: Nov 2009
Location: Abuja, Nigeria.
Posts: 126
#4

Re: Measuring Closing Time and Tripping Time of Breaker

03/25/2010 6:53 PM

Closing time will depend on the activating circuit and the breakers closing circuit (the magnetic cct & the breakers closing mechanisms). The tripping time depends on the level of fault signal. Normal tripping initiations and other faults like phase faults usually takes longer tripping time than earth fault. Actually tripping time depends on the type of circuit breaker and their dependability tripping signal. An earth leakage circuit breaker will vary with the tripping time of the earth fault current levels. A current operated MCB will vary with tripping time of the out of balance current level. A voltage operated MCB will also vary with the operating fault voltage. NOTE: Time is an inverse function of magnitude factor. The more the magnitude factor, the lesser the time. John can fight John and any of them can win after a much longer round. But John Bull will beat john or knock John out in the first round. Dickson.

__________________
There is peace in silence and achievement in plans.