Anonymous Poster

for lt breaker

03/28/2010 8:49 AM

My existing ACB capacity 4000 amps.Some times connected load goes to 4350 amps on jerk load,so please suggest me which capacity ACB is suitable to run safe.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#1

Re: for lt breaker

03/28/2010 7:52 PM

What is the continuous load amps?

Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#2

Re: for lt breaker

03/28/2010 8:52 PM

If any breaker specifically states it is rated for 100%, it is. If it does not clearly state that, you must assume it is rated for 80% of it's stated rating continuously. Continuous is defined as in excess of 3 hours (I believe).

That said, most Power Breakers such as an ACB are purchased in switchgear as 100% rated devices. Check the documentation on the equipment. In any case, you are playing with fire if you are running at nearly 110% of rated, unless by "jerk load" you are meaning a very short duration at that higher value. Typically you will have at the very least a "Long-time" (L) and Instantaneous (I) trip setting. The, L setting will be based on I2t of the rating, with the maximum time value at 110% load being somewhere in excess of 2 hours. You can request what is called a "trip curve" from the manufacturer of your ACB.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply Score 1 for Good Answer
Member

Join Date: Mar 2010
Posts: 5
#3

Re: for lt breaker

03/28/2010 11:27 PM

All ACBs are rated for short duration overloads ranging from 20 % overload to breaking capacity of the breaker.

10 % overload for 1/2 an hour need not be a worry.

Manufacturer's specification ( which generally appears on name plate may be refered.)

Reply Score 1 for Good Answer
Power-User
India - Member - design engineer Engineering Fields - Electrical Engineering - New Member United Arab Emirates - Member - New Member

Join Date: Feb 2010
Location: dubai,mangalore,bangalore.....
Posts: 145
Good Answers: 8
#4

Re: for lt breaker

03/29/2010 4:41 AM

wat s the maximum current the load can take ? i mean is it ok for the load to take 4350 amps ? if so then select acb nw50 (MG)along WIT A MICROLOGIC and set the micrologic to trip after the max current which the load can take to run safely

__________________
shamith gambhir, electrical engineer
Reply
Anonymous Poster
#5
In reply to #4

Re: for lt breaker

03/29/2010 6:41 AM

I didnt understand your logic, please make it clear

Reply
Participant

Join Date: Mar 2010
Posts: 1
#6
In reply to #4

Re: for lt breaker

03/29/2010 6:50 AM

I didnt understand your logic,so please make it clear

Reply
Power-User
India - Member - design engineer Engineering Fields - Electrical Engineering - New Member United Arab Emirates - Member - New Member

Join Date: Feb 2010
Location: dubai,mangalore,bangalore.....
Posts: 145
Good Answers: 8
#7
In reply to #6

Re: for lt breaker

03/29/2010 8:14 AM

K tell me one thing what happens to the load when it gets 4350A.....i want to know whether the load would withstand such current....if it does thn select a acb of rating 5000A .....after selecting tht acb , u need to additonally select a micrologic for tht acb....in tht micrologic u can set the trip current for 0.4, 0.5, 0.6...1 times acb rated current....for more details visit schneider website and search for acb and micrologic....................

__________________
shamith gambhir, electrical engineer
Reply
Commentator
Engineering Fields - Electrical Engineering - New Member India - Member - New Member

Join Date: Dec 2009
Location: Bangalore,India
Posts: 80
Good Answers: 1
#8

Re: for lt breaker

03/30/2010 1:48 AM

Dear Guest,

You have mentioned the load goes to 4350 A on jerk load. what is the duration of jerk load ? regarding the capacity of ACB, there are certain additional factor to be considered : what is the ambient temperature? what is the temperature rise accepted inside the enclosure? if you could furnish the sld/electrical scheme, then the forum members can provide a better solution.

Thanking you


Please Note : it would be nice if could introduce yourself.

Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#9

Re: for lt breaker

03/31/2010 3:21 AM

Has the circuit breaker ever tripped? If the 4350 amp surge subsides quickly, and the continuous load is somewhat less than 4000 amps, and there has been no tripping, then you are probably okay. I agree with the other recommendations to check the trip curve for this unit.

You might also consider some control strategies, such as unloading some other equipment when starting a large motor. Or starting your largest loads first and your smallest loads last.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Anonymous Poster
#10

Re: for lt breaker

03/31/2010 12:28 PM

The breaker size is to protect the wiring or bus, some way of limiting inrush will have to be done

Reply Score 1 for Off Topic
Reply to Forum Thread 10 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); hemantphatak (1); JRaef (1); nagusadasivuni (1); SHAMITHGAMBHIR1 (2); shanbhag (1); Tornado (1); wareagle (1)