Equilibrium Temperature

03/28/2010 2:30 PM

Well someone missunderstood my Question and took it as homework. So i m posting my question again with more explanation and background.

I work in a process industry where water is used for different purposes. Our total requirement of water is 70m3 avg. Water is stored in underground water storage tank where its temperature is appx 25C. About 15 m3 of water is used for cooling purpose in a heat exchanger and wasted in drain. Temperature of which raises to about 35C. I want to return the wasted water back to storage tank and know what effects it could have on the reservoir temperature. Return water will come under gravity head. No pumps will be used. Capacity of reservoir is 670m3.

Waiting for positive response.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
United States - Member - New Member Engineering Fields - Control Engineering - New Member

Join Date: Mar 2006
Location: Washington USA
Posts: 566
Good Answers: 53
#1

Re: Equilibrium Temperature

03/28/2010 3:35 PM

It would increase the temperature of the reservoir!

Register to Reply
Anonymous Poster
#2

Re: Equilibrium Temperature

03/28/2010 4:52 PM

The equation(s) you want are related to specific heats.

Q=mcΔt

Q = heat (rate)

m = mass (rate)

c = specific heat (in your case water)

Δt = temperature differential

I can not further set up the equations because I do not fully understand your problem, that is, you mention you require 70m3 avg, and use 15 m3, but have a reservoir of 670 m3.

Register to Reply
Guru

Join Date: Jul 2006
Location: "Dancing over the abyss."
Posts: 4884
Good Answers: 243
#3
In reply to #2

Re: Equilibrium Temperature

03/28/2010 5:21 PM

In addition, the contaminants picked up from the cooling cycle will concentrate in the main reservoir.

milo

__________________
People say between two opposed opinions the truth lies in the middle. Not at all! Between them lies the problem, what is unseeable,eternally active life, contemplated in repose. Goethe
Register to Reply
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#4

Re: Equilibrium Temperature

03/28/2010 9:04 PM

How much you send back? And how often? It is bad homework. Start with this: 1 m3 of water @35 degr. C and 1 m3 water @25 degr. C - delta t will be 10/2 the rest is for you: 15 m3 ......35 degr. C and 15 m3 @ 25 degr. C = the same. your result temperature will be 25 + (10. 15/670) with no additional losses counted.

__________________
Plenty of room here
Register to Reply
Anonymous Poster
#5

Re: Equilibrium Temperature

03/28/2010 10:09 PM

If it is an actual life scenario, along with what has been explained above,

You want the heat to be dissipated somewhere ? You go in a closed loop and then where is the heat supposed to be lost ?

For this usually we don't have underground reservoirs , rather overground reservoirs and cooling towers, both of them lose heat through evaporation, but with that an amount of water also is lost.

The underground storage will lose heat, at a bit increased rate as the temperature of the water inside rises from 25oC. However soil not beein a good conductor of heat will not be effective in pulling back the temperature, and you will have the temperature inlet to HE rising, that will cause the fluid temperature and the temperature of water at outlet to rise, till it stabilises at some temperature above what is calculated (that calculation assumes the water to be at 25oC and 35oC however after some time it will be 25+ and 35+)

Register to Reply
Anonymous Poster
#6

Re: Equilibrium Temperature

03/28/2010 11:55 PM

Without getting into calculations, the heat picked up in the process has to be dumped somewhere before the water's returned to the tank, else heat will accumulate in the tank, the water therein will heat up, and you'll gradually lose cooling capability.

That being said, that heat can be dumped either to the environment (heat radiating from piping, water-to-air radiator, water-to-water heat exchanger, etc.), to some other place (say another process (including space-heating) through a heat exchanger), or out the underground tank into the surrounding ground.

First things first: your underground tank's likely insulated from the surrounding ground, else you'd always be losing heat to it; either that, or the surrounding ground is a poor thermal conductor (which means that its likely dry) or that something else is heating it (hot plant-equipment above it?). If it's not, please let us know how the water's temperature inside it is maintained at 25 C ... no ground is ever that hot naturally, unless it's near a geothermal source.

Another possibility: take the thermal insulation off of pipes going into the process if the ambient temperature around them is less than 25 C .. that way, the water will enter the process more cooly and will come out the other side more cooly too. Same thing atthe process outlet ... strip off the insulation and radiate the heat into the ambient environment if it's cooler than 35 C.

In addition, you may want to dump the heat into something useful; if you have a process that needs heat or if you need space-heating, use a heat exchanger to pass heat from your process' cooling-outlet to it.

If you've after all this you still have heat to dissipate, use a water-to-air radiator (natural draft or forced-air, depending on how much cooling you need) or a cooling tower if the air temperature is below 25 C, or use a water-to-water heat exchanger if you have a river, a lake, or a cooling pond nearby.

Hope this helps. Cheers! DZ

Register to Reply
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#14
In reply to #6

Re: Equilibrium Temperature

03/29/2010 1:00 PM

I never have been able, to reach water out of the ground, lower than 25 degrees celsius on the caribbean islands. This has been a costly experience, because our water cooled A/C systems did not perform. In Europe I had 16 degrees.

__________________
Plenty of room here
Register to Reply
2
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15602
Good Answers: 982
#7

Re: Equilibrium Temperature

03/29/2010 12:06 AM

The reason that I felt that you had a homework problem was that you were not presenting enough information to even attempt a reasonable answer, you still don't. You mention the one time withdrawal of less than 1% of your reservoir capacity at 25C and then a return of this volume with only a 10C rise in temperature. If absolutely no other thermal transfer was possible then I believe some very sophisticated temperature measuring devices maybe capable of measuring a small temperature rise in the reservoir. But I refuse to give you any more of hint why I feel this way because you seem to still be hiding something critical from us. Specifically how often does this exchange of cool and warm water happen, once a year, day, hour, minute, second? You do not give us any idea about the flow rate.

But even if you now do inform us about the flow rate, I'm not sure this is wise to answer your question. You see 15 cubic meters of water is 15,000 liters of water. This has a mass of 15,000 kilograms. This is not an insignificant amount of mass and should not be moved by somebody that doesn't know what is going on or what is critical. I'm sorry to say but by not knowing how quickly this much mass leaves and reenters your reservoir, or knowing and not thinking that it is relevant to inform us this at two different postings tells me that you are not qualified to question any of the engineering happening at this place.

I do hate to be harsh but you don't sound qualified.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Good Answer (Score 2)
Member

Join Date: Apr 2009
Posts: 5
#12
In reply to #7

Re: Equilibrium Temperature

03/29/2010 11:46 AM

@ redfred.

never mind your comments, and also your harsh behavior, let me fill the space information that might be left

1. Water is continuously refilled in the reservoir and continuously withdrawn at average rate of 70 m3/hr.

2. Flow mentioned is per hour for all values.

3. there is no contamination of particles in the return water.

4 The reservoir is made of cemented concrete and top is covered with fibre glass sheet.

5. The temperature of reservoir i mentioned (25 C) is almost equal to the temperature with which water comes out of ground, i don't know the geothermal details of this.

6. Certainly the returning water will increase the temperature of the reservoir, reducing the cooling capability of water but what i wanted to know is upto what value, how can it be calculated, there must be some equilibrium temperature above which the temperature will not rise.


If you don't understand the question it doesn't mean the person asking the question is not qualified or don't have engineering knowledge, it may be other way.

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15602
Good Answers: 982
#16
In reply to #12

Re: Equilibrium Temperature

03/29/2010 1:34 PM

Wait a minute, now I see the problem. As you mentioned you have a working cooling system that continuously draws a certain amount of water from an underground reservoir and the same water after being heated by 10C returns to this reservoir. You expect this reservoir to over time to have warmer than 25C water coming out of the ground eventually but this doesn't happen. Well obviously the amount of thermal energy you are dumping into the underground reservoir of water, container and earth that this reservoir resides in is insignificant compared to the energy you are adding. You have for your application a virtual infinite heat sink.

Remember, thermal insulation slows down the transfer of heat, it does not slow it down. Your 35C water is trying to heat all of the mass of earth you are standing on. While 15,000 kilograms of water is a lot of mass, it pale in comparison with the denser earth itself.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Member

Join Date: Apr 2009
Posts: 5
#17
In reply to #16

Re: Equilibrium Temperature

03/29/2010 2:01 PM

yes you are probably rite,

even if i consider the reservoir as thermocline as someone mentioned, the rise in temperature of 2.7 degree C will occur after approx 44 Hrs. This time is more than enough for thermal heat dumped to water reservoir to be transferred to earth and loss to atmosphere.

After all these comments and suggestions i suppose that it is better to re-circulate the cooling water inspite of wasting it without any considerable effect on system.

Register to Reply
Anonymous Poster
#8

Re: Equilibrium Temperature

03/29/2010 2:50 AM

Is this tank 670 m3 capacity constantly refilling against use?

Or a tank emptying over time, then being refilled?

Either way the water in temperature, if different to 25 C, is also factor.

But say it's 25 C

Ignore the tank volume for a moment and imagine it as a pipe and a loop

Then the system output would rise to the ratio of 70 - 15 = 55 @ 25 C in (replenishment water) v.s. 15 @ 35 C (returned water) on initial circulation. I.e. 15 / 55 = 27% rise on 10 C = 2.7 C.

In an insulated pipe system, second circulation is 12.7 C supply to the exchanger plus 10 C gain. Or the effect instantly multiplies.

That you have 670 m3 slows the 27 % rise multiplication.

But ultimately the energy effect is equal to adding exchanger rise to the tank refilling flow.

Imagine this as forming a thermocline, and the exchanger will not see the rise until one tank volume is used. The volume riding above is now 25 + 2.7 = 27.7 C.

The next 27.7 + 27% of 12.7 rise, and so on.

Obviously you now must increase the flow through the exchanger - so the % rise on volume basis ratio changes.

Against this process is the (unknown) heat loss of the tank. Ground is a fairly good insulator. This system will rise, but how much is impossible to estimate on the data supplied.

I would think a simple process engineering move, would be to return the water via another passive exchanger. But I don't know your ambients or if this is 24/7, or if you could run the exchanger circuit at night to dump the heat rise. Or if a bit of evaporative cooling is the path to follow.

Equilibrium is impossible to estimate with out loss data or such information as above.

If I've read it wrong and it is a use and refill tank - the same process applies but obviously the last bit is going to be many cycles hotter.

Kyzine

Register to Reply
Guru

Join Date: Dec 2006
Location: Hop around Toronto, New York & Karachi
Posts: 1876
Good Answers: 19
#9

Re: Equilibrium Temperature

03/29/2010 3:18 AM

Temperature mixed water:

670 x 25 + 15 x 35 = 17275/670 = 25.78 = 25.8C will be the reservior temperature after return of 15 m3 water at 35C.

__________________
I not only use all the brains that I have, but all that I can borrow. Woodrow Wilson
Register to Reply
Guru

Join Date: Mar 2007
Location: City of Light
Posts: 3943
Good Answers: 183
#10

Re: Equilibrium Temperature

03/29/2010 9:21 AM

I shall try to explain how I understand your question and give an answer according to my interpretation:

from a 670 m^3 at 25 °C you use during a given period of time (not specified) 70m^3 from which 15 m^3 are used as coolant and arrive at 35°C. If you direct those 15 m^3 back to reservoir you will compensate in order to stay at same volume only 55m^3 which are I assume at 25°C. At the end of a cycle you have in the reservoir 600m^3 at 25°C, 55m^3 at 25°C (refill) and 15 m^3 at 35°C . The remark about pollution is correct but I do not know the type of heat exchanger you use and how big the risk is.

If we make a balance the result is for the 670 m^3 the temperature will be :

(600+55)/670*25+15*35/670=25.224 °C

Is my assumption OK?

Register to Reply
Guru

Join Date: Apr 2006
Location: Cincinnati, Ohio, USA
Posts: 662
Good Answers: 49
#13
In reply to #10

Re: Equilibrium Temperature

03/29/2010 12:25 PM

I think that you are right on- See my post #11 to get the same result.

__________________
NO MATTER HOW WELL YOU HAVE DONE SO FAR, ALWAYS TRY TO BE BETTER TOMORROW.
Register to Reply
Guru

Join Date: Apr 2006
Location: Cincinnati, Ohio, USA
Posts: 662
Good Answers: 49
#11

Re: Equilibrium Temperature

03/29/2010 10:41 AM

Your issue is straight thermodynamics.

You are adding 15m3 X 10C x 1 (specific heat of water) units of energy to (670-15)m3 of water- I assume from your input that the (70-15)m3 of water returns to the tank at about the 25C starting temperature.

Basically- do the math. The (670-15)m3 of water is 97.8% of total volume. The actual NET resulting temperature will be about ((25C X 97.8%) + (2.2% X 35C)) = 25.22C.

I used "about" because the actual heating temperature difference will be the 35C minus the "final" temperature of the mix, since the mix will be warming slightly, reducing the actual DeltaT. A more accurate calculation would have been to multiply the "35C" used in the earlier calculation by 97.8% to allow for the lost differential.

__________________
NO MATTER HOW WELL YOU HAVE DONE SO FAR, ALWAYS TRY TO BE BETTER TOMORROW.
Register to Reply
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#15

Re: Equilibrium Temperature

03/29/2010 1:06 PM

70-15= 55 What do you do with this water? I tried to give an answer, based on your info. If you give a poor description, you will get a poor answer and keep us busy with guesswork. Analyze your system and provide more correct info if you want reliable answers.

__________________
Plenty of room here
Register to Reply
Register to Reply 17 comments