Cable Size for 7.5 KW motor

03/28/2010 11:37 PM

We installed 7.5 Kw Induction Motor. We used 10 mm 4 core cable for it. Motor is 40 m far from the MCC. I think cable size is a little bit over rated . Can some explain and calculate that what is the exact size of cable require for this application.

Reply
User-tagged by 1 user
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Participant

Join Date: Mar 2010
Posts: 1
#1

Re: Cable Size for 7.5 KW motor

03/29/2010 1:30 AM

By applying derating factor as 0.7 to 0.75 to 3Cx4Sq.mm, u may get derated cable ampacity of 30 to 35 amps withstand capacity from the rated value of 40 to 44 amps.

7.5kW rated current is 18 to 20A & starting may be 105 to 112 amps based on yr area rated voltage & starter timing.

So u want to run 1ly for 40M, if it is in air 3Cx4Sq.mm is more than sufficient to run the motor sucessfully, note that u can go upto 120M long there won't be any pbm with the 3Cx4Sq.mm.

Then whatever the cable size u r mentioned as 4Cx10Sq.mm is suitable for 22kW Motor with 40M distance.

Rgds,

Karthick...

Reply Score 2 for Off Topic
Anonymous Poster
#2
In reply to #1

Re: Cable Size for 7.5 KW motor

03/29/2010 1:57 AM

Follow a simple rule

"KW and Cable size should be same for a distance up to 300 Feet"

" KW = Size of conductor in mm "

If motor is of 10 KW use cable of size 10mm

If motor is of 5 KW use cable of 6 mm.(5 mm cable is not available so use 6 mm cable)

If motor is 15 KW use cable of 16 mm (15 mm cable is not available)

If motor is of 30 Kw use cable of 35 mm

Reply Score 1 for Off Topic
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3

Re: Cable Size for 7.5 KW motor

03/29/2010 4:15 AM

For one thing, it depends on the voltage of the motor, which was not specified. Half voltage = twice amperage, so rules of thumb that ignore voltage cannot be accurate. Another problem is failing to distinguish between mm and mm2.

This is not a mere calculation, anyway. It is more like a decision tree (multicore cable, separate wires in air, in conduit, underground, in company with other conductors, etc.) and looking up in a code table.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
3
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#4
In reply to #3

Re: Cable Size for 7.5 KW motor

03/29/2010 11:30 PM

Hi Tornado, In Europe are different standards: a motor of 2 HP may not run in a single phase system. So we have a 3 phase system, the poster speaks of 4 wires, which points in that direction too. Standard grids are 220/380 and the tumb rule he gave counts for a delta net (highest current per phase). When I read the size - it should be mm2,because someone who knows the metric cables thinks: 1,5/ 2/ 4/ 6/ 10/ (12) /16 mm2. Up to 16 mm2 (and 20 mm2 on special order) are 1 solid conductor per phase - in different cable versions. To go from mm to mm2 you just use phi.d2/4 (d in mm)

Metric is just that easy

__________________
Plenty of room here
Reply Good Answer (Score 3)
Participant

Join Date: Mar 2010
Posts: 1
#5

Re: Cable Size for 7.5 KW motor

03/30/2010 3:39 AM

I think ,case by case.

Reply Off Topic (Score 5)
Participant

Join Date: Aug 2009
Posts: 3
#6

Re: Cable Size for 7.5 KW motor

03/30/2010 5:48 PM

you can download a size calculator from the general cable website.

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#7

Re: Cable Size for 7.5 KW motor

04/06/2010 3:29 AM

→ British Standard 7671.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Reply to Forum Thread 7 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); dvmdsc (1); hero (1); J_B (1); Karthickraja (1); PWSlack (1); Tornado (1)

Previous in Forum: Low Voltage   Next in Forum: Using Power Cables as Control Cables
You might be interested in: Cable Laying Services, Cable Assemblies, Cable Trays

Advertisement