High Pressure Flame-Gas Tank Safety

03/29/2010 11:00 AM

I'm hoping for either some discussion or education on a possible saftey implement to help protect property and emergency responders. I'm traditionally a biologist, so excuse the layman's language. I appreciate the help, Thank you.

Background: I'm looking into Boiling Liquid Expanding Vapor Explosions (BLEVEs). This happens in a flaming site situation where a High pressure Propane tank or something similar heats up to the point the metal fails and there is a pressure release based explosion. Its apparently very dangerous for fire fighters because of the delayed explosion. Normally the pressure relief valve lets off pressure but in a BLEVE situation, the explosion can take place below the pressure needed to activate the release valve because of the weakened structural integrity.

My Question: In recent years I'm hearing more about in-place sensors that can detect in real time, if a structural material is weakening. I'm wondering if by running a small electric current (I'm told it might be an "eddy" current?) through the Hull of a large 90-ton propane tank and checking for variances in resistance, could you detect the failing strength quick enough to automatically blow a secondary release valve for the tank. Furthermore, I'm wondering if this sensor could work off simple batteries and be cost effect for industry to actually be implemented.

Thanks

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: High Pressure Flame-Gas Tank Safety

03/29/2010 7:49 PM

Look at pictures of bleves. The tank is usually enveloped in flames long before any failures occur. Nothing on the outside of the tank will survive. Electrical resistance would be increasing with tank temperature. Forget batteries and wires, they're vaporized long ago.

Train car explosion bleve

Register to Reply Score 1 for Good Answer
5
Guru
Safety - Hazmat - New Member Engineering Fields - Retired Engineers / Mentors - New Member Engineering Fields - Piping Design Engineering - New Member Hobbies - DIY Welding - New Member Fans of Old Computers - PDP 11 - New Member

Join Date: Feb 2007
Location: Stronger Than The Storm
Posts: 2394
Good Answers: 203
#2

Re: High Pressure Flame-Gas Tank Safety

03/30/2010 12:54 AM

EVERYTHING HAPPENS TOO QUICKLY FOR ANY INSTRUENTATION OR SENSORS TO ACTIVATE A SECONDARY RELIEF VALVE.

The BLEVE usually occurs because the flame is impinging on the vapor portion (upper) of the tank (latent heat of the vapor is much lower that the liquid). Without the liquid to absorb the flames heat the metal weakens very rapidly. When the tank ruptures the rapidly escaping Boiling Liquid Expands and forms a rapidly expanding vapor. It expands so quick that it expands quicker than the speed of the flame propagation. When the flame catches up the Vapor Explodes with a rapid expansion of the combustion gasses. It is the "pressure front" from this that does most of the damage for a considerable distance.

The best action for a situation like this is to put some unmanned monitors (large flow water nozzles) aimed on the tank at the early stages before things get worse. Be sure they don't put the flame out! Next put plenty of distance between everyone and the tank. Let the situation do it's thing and call the professionals.

I have worked in the chemical industry for 40yrs, much of it in the safety and emergency response function. Now that I am retired I am the fire chief of a volunteer fire dept. I survived a railcar BLEVE about 30 years ago, although I was 1/4 mile away it knocked me down on my butt! The guy next to me has hit by schrapnel and has a pretty nasty scar on his arm. After that I swore that 3/4 mile wasn't enough distance.

The US Chemical Safety Board has some good information on BLEVE's. Several years ago there was a big exposion in W VA (I think) that killed several persons and it was only a small bulk tank.

One big disadvantage with the instrumentation and sensors would be that people would become over confident about them because they would never see them operate until it was probably too late.

__________________
Any day on the green side of the grass is a GREAT DAY!, --- me +++++++++. I believe creativity is an inherent part of everyone. --- Kermit T. Frog
Register to Reply Good Answer (Score 5)
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3
In reply to #2

Re: High Pressure Flame-Gas Tank Safety

03/30/2010 1:53 AM

Nicely put. I've only seen pictures. That's enough for me.

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#4

Re: High Pressure Flame-Gas Tank Safety

03/30/2010 3:47 AM

BLEVEs can also occur without flames, such as with rupturing boilers or refrigerant vessels. For instance, steam expands by about 1600:1 compared to liquid water. Around 1980(??) there was an incident in Everett, WA, USA, in which a boiler ruptured, tore itself away from its piping, and rocketed 300 feet along the ground. It crashed into a building, crushing a victim.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Power-User

Join Date: Nov 2008
Location: Port Glasgow, Free Republic of Scotland
Posts: 360
Good Answers: 30
#5

Re: High Pressure Flame-Gas Tank Safety

03/30/2010 4:13 PM

I GA'd oldsalts answer as it covers most things but just a couple of things

Vapour doesn't have a latent heat thats why there is a reduction in heat conduction and the metal temperature rises.

Initially the fire impinges on the liquid surface, and heats it eventually starting to boil the liquid at the relief pressure. Vapourising liquid takes a lot of energy and boiling liquids have a very high heat transfer coefficient, the combination of which means that the heat of the fire is quickly transmitted through the steel to the liquid and absorbed by the change of phase.

Once some of the liquid has boiled away in part and the fire impinges on the gas part of the vessel, heat transfer rates fall and the gas can only absorb energy by rising in temperature. This causes the steel temperature to increase. So long as there is still boiling liquid in the vessel it will be at the relieving pressure. The vessel fails because the vessel has a design pressure / temperature pair and if you exceed the design temperature the strength of the steel fails and can rupture at the notional design pressure. At the fire temperature the bursting pressure of the vessel can be below its design pressure for the design temperature.

Also I am curious - why would you use monitors and not put the fire out? I see the whole cooling idea. Drenching the area in water absorbs the energy of the fire by boiling the water and either keeps the steel vessel in its design temperature range or cools it. I guess the fire indicates the presence of hydrocarbons and if you put the fire out without addressing the leak you will end up with a pool of flammable liquid, possibly a cloud - propane vapourises at cold ambient temperatures which would give you the risk of a fuel air explosion which is not to be sniffed at. (Or am I down the wrong path here)

In my experience this problem is addressed with a separate blowdown system. This is an automated system which has the risks addressed above however the intention is:

You have a simple block valve in a vent line from the vessel. (Typically of the size of the relief valve outlet). You have a fire and gas safety system - including IR / UV sensors, big red buttons for the operators etc. If these are tripped (or say 2 out of 3 are activated) then the valve opens and depressures the contents of the vessel to the flare. Remember BLEVEs occur in pressurised normal temperature storage vessels. This valve is not spring loaded and so once open provides a free path to the flare dropping the pressure to atmospheric or thereabouts.

However it is automated so there are risks. However normally these valves have a spring acting on the closure mechanism trying to open the valve. On the other side is the plant instrument air holding the valve closed. If there is a failure of the electronics the Inst Air cylinder is depressured and the spring acts to open the valve. These valves always fail to the open position which hopefully gets round the being consumed by fire problem.

In this way you drop the pressure of the vessel whilst it is hot - obviously there is a down side in losing all the product but having seen pictures of BLEVEs I don't want to be within 5 miles preferably 50 of one going off

__________________
Free advice guaranteed or your money back
Register to Reply
2
Guru
Safety - Hazmat - New Member Engineering Fields - Retired Engineers / Mentors - New Member Engineering Fields - Piping Design Engineering - New Member Hobbies - DIY Welding - New Member Fans of Old Computers - PDP 11 - New Member

Join Date: Feb 2007
Location: Stronger Than The Storm
Posts: 2394
Good Answers: 203
#6
In reply to #5

Re: High Pressure Flame-Gas Tank Safety

03/30/2010 11:38 PM

Monitors are used to keep the tank cool so that the steel doesn't heat up to its weakening point. It is also used to keep the temperature and pressure of the contents down, less heat to shell-->less heat to contents-->less pressure and temperature of product-->less stress on steel tank-->less dangerous situation-->more time to solve the problem.

When propane is leaking out of the outlet of the safety valve due to over pressurization and is on fire the propane is burning where it is. If the flame is not impinging on the tank it is slowly comsuming itself and its inherent dangerous properties. Should the flame be eliminated but the leak continues you still have the dangerous properties of the propane present. As the propane leaks it migrates to the surrounding areas (of course dependent upon rate of flow, temperature, wind direction, wind speed, geography, etc.) as the form of a flammable cloud. Since the density of propane liquid and vapor is greater than air it follows the contour of the ground as it travels with only minimal dispersion. The result is a very big explosive cloud that is waiting for a source of ignition. When it finds that source of ignition it ignites with explosive forces due to the rapidly expanding gasses of combustion. This is the same type of explosion that is denoted in "BLEVE" as the V and final E.

Systems such as you have mentioned have been developed but are most are not reliable enough to be utilized for the storage of flammable pressurized gasses or flammable pressurized liquids that would vaporize at atmospheric conditions. The most common system utilizes two units. First is a spring loaded pressure relief valve (a very simple system) that is set to open at the lower of two pressures and close when that pressure has been reduced down to it's set pressure. The second is a fracture type rupture disk which will break at the higher of the two pressures. When this breaks it releases the contents of the tank at a precalculated rate determined by the size of the piping or a restriction in the piping. It's rupture causes the remaining contents of the tank to be dumped of course. This is installed so that the material relaease is directed in the least dangerous direction (usually to a flare tower or up and away from the tank).

There are very few "fool-proof" components for this type of system. Even the spring loaded pressure relief valves I have mentioned can be compromised and fail to open, thats why the redundant rupture disk is used. When there is human life at stake the risk factor has to be extremely low. Careful and complete foresight in engineering and risk analysis is needed. A good axium is "Odds of a million to 1 are great, unless you are the 1".

Go to youtube and do a search of BLEVE or explosion. Many of them are very humbling.

All of this is accomplished through good engineering and excellent risk analysis.

__________________
Any day on the green side of the grass is a GREAT DAY!, --- me +++++++++. I believe creativity is an inherent part of everyone. --- Kermit T. Frog
Register to Reply Good Answer (Score 2)
Power-User

Join Date: Nov 2008
Location: Port Glasgow, Free Republic of Scotland
Posts: 360
Good Answers: 30
#7

Re: High Pressure Flame-Gas Tank Safety

03/31/2010 5:20 AM

I am glad I managed to work out why you don't want to put the fire out.

One thing we should have mentioned is that the ground under an LPG or similar tank should be sloped to a controlled area. This way any leaks are directed away from the tank so if they ignite it reduces the fuel available at the tank. However as Propane/Butane vaporise it will not control vapour releases and so the sloped floor may just move the hazard.

As to the Emergency Blowdown System I was trying to describe. It essentially comes from API 521 and so I think I would challenge your comment about its lack of reliability. However my experience is just as a Process Engineer. We have recently installed these systems on the refrigerant accumulators for a Propane and Mixed Refrigerant Chilling system for some very large refrigerated atmospheric tanks in the mid east. These vessels were 4 - 5 m diam, 15 - 20m long running at up to 35 bar so are similar to pressurised LPG storage vessels. The blowdown system described was the key BLEVE protection.

I see the merit of installing a bursting disk although I haven't had that experience myself. However this system has the flaw that if the spring loaded relief valve operates as designed then the vessel is kept at its design pressure and so will fail. The key to BLEVE protection as I understand it is to get the pressure of the system down as quickly as possible if the vessel is under fire. The bursting disk achieves this but if the relief valve works the bursting disk will never open. I accept there are risks with the blowdown valve but they are designed with as many fail safes as possible. A loss of power, air, control signal will all cause the valve to open. Sometimes the air supply is routed through a short plastic tube that will melt in a fire causing the air actuator to depressure and allowing the spring to drive the valve fully open. Obviously it is key that these events occur before the fire fully develops as the heat may warp valves and paths and so the valve may stick in the closed position.

After installing all of this it is still essential that the emergency crews are fully trained on the mechanism of BLEVE so that the appropriate actions are taken when the worst happens. I have seen the videos read the reports and still too many people are killed.

One further thing for our original questioner - if you google blowdown vlaves most of the hits will be for boiler blowdown vlaves which are to remove a build up of slats and other crap from boiler drums so be careful on your searching. But API 521 is a good place to start

__________________
Free advice guaranteed or your money back
Register to Reply
Guru
Safety - Hazmat - New Member Engineering Fields - Retired Engineers / Mentors - New Member Engineering Fields - Piping Design Engineering - New Member Hobbies - DIY Welding - New Member Fans of Old Computers - PDP 11 - New Member

Join Date: Feb 2007
Location: Stronger Than The Storm
Posts: 2394
Good Answers: 203
#8
In reply to #7

Re: High Pressure Flame-Gas Tank Safety

03/31/2010 8:56 AM

The burst pressure of the rupture disc is spec'd for less than the test pressure of the storage vessel, usually less than the max working pressure. That way the vessel is more likely to be usable after the overpressurization incident (if not damaged by other factors). The intent is that the fracture disc will be replaced due to age having never being necessary and not due to use.

The release point of the spring pressure relief valve is at an even lower pressure than the fracture disc. This way if the spring press vlv should not open the fracture disc will open before the vessel becomes compromised.

An example could be-

Spring loaded press relief vlv- 200psi; Fracture disc 225psi; max operating press of vessel 240psi.

Perhaps I am slanted towards pessimism having done many Haz Ops analysis's for the development of processes and Accident Investigations after things failed but many fail safe things fail and cause deaths. The Titanic was fail safe.

__________________
Any day on the green side of the grass is a GREAT DAY!, --- me +++++++++. I believe creativity is an inherent part of everyone. --- Kermit T. Frog
Register to Reply
Active Contributor

Join Date: Dec 2009
Posts: 15
#9
In reply to #8

Re: High Pressure Flame-Gas Tank Safety

04/27/2010 1:39 PM

Thanks for the responses guys. I especially enjoyed Old Salt's 1/4 mile away experience. Glad to hear you're okay.

I see what your saying about anything with circuitry or wiring possibly failing under high heat or costing to much to shield.

I'm interested in this rupture disk. So following your example: "Spring loaded press relief valve- 200psi; Fracture disc 225psi; max operating press of vessel 240psi." Say you have a bleve scenario where heat has weakened the tank, and the real time tank integrity is down to say 180 psi (below the pressure relief valve. Could you assume the rupture disk integrity would also deteriorated down <180 psi given that the flame is on it? If not I'm wondering if material engineers could work on developing this.

Also I'm assuming most tanks have one of these rupture disk on the top or on one side. Would it be worth the cost to install multiple rupture disk around the sides of the tank where a bleve risk heat source is likely to hit the tank?

Thanks

Register to Reply
Power-User

Join Date: Oct 2009
Location: Central Midwest
Posts: 455
Good Answers: 38
#10
In reply to #9

Re: High Pressure Flame-Gas Tank Safety

05/15/2010 8:14 PM

Con...

I believe that I understannd your line of reasoning....but there are some publications that you should read.

The virtues of a "multiple relief device" design for fire protection is contained in NFPA publications and has been in use for many years......you should particularly review NFPA-30 and its references on tank venting (I think that its NFPA-2000 that you would want)

Many US tanks and vessels in the process chemical industry have multiple protective devices

The site specific requirements for leak collection and "fire zones" are typically reviewed during a detailed HAZOP analysis which is required by US federal statutes.

"Old Salt" hit the nail on the head with all of his comments....bravo !

-MJC

__________________
We have met the enemy....and he is us. POGO
Register to Reply
Register to Reply 10 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: