DROOP

03/31/2010 12:10 AM

Hai

what is the meaning of "DROOP"

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru

Join Date: Sep 2007
Location: Defreestville, NY
Posts: 1072
Good Answers: 87
#1

Re: DROOP

03/31/2010 12:20 AM

In an electrical context a simple explanation can be found here : http://en.wikipedia.org/wiki/Voltage_droop

__________________
Charlie don't surf.
Register to Reply
Anonymous Poster
#2

Re: DROOP

03/31/2010 12:32 AM

when a generator is put in parallel and synchronised to the other generator which already running at full load,then there is a "speed droop" meaning frequency/load mismatch of the two generators which gives rise to reverse power condition.

Register to Reply
4
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#3
In reply to #2

Re: DROOP

03/31/2010 10:57 AM

There are two types of droop: Voltage droop and Speed droop. Voltage droop is a setting of AVR (Automatic Voltage Regulator) for generator voltage control (eventually the VAR control) and Speed droop is setting of governor for frequency control (eventually the KW control). Both are expressed in % value. Generally, the AVR droop setting is 2% and governor droop setting is 4%.

Droop = (No Load Speed - Full Load Speed) x 100 / No Load Speed

For more details, see these links:

http://cr4.globalspec.com/thread/42805

http://cr4.globalspec.com/thread/49551/DROOP

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply Good Answer (Score 4)
Member

Join Date: Mar 2010
Location: Australia
Posts: 8
#4

Re: DROOP

04/01/2010 4:22 AM

Droop in a simple term, is either, generator voltage droop or speed droop. Voltage droop is the drop of no-load rated voltage to full load voltage. For Example, its 480VAC no-load voltage may drop to 470VAC when loaded depending on the droop setting of generator AVR. Speed droop is for the generator speed or frequency. Depending on the setting of governor/speed controller, You may have 61HZ at no-load and drop to 60HZ when loaded. These two droop setting of generator are important in parallel operation of two or more generators. The load sharing capabilities of generators depend on its droop characteristics.

__________________
Bangsamoro Gagandilan.....
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5

Re: DROOP

04/06/2010 3:22 AM

Something that happens after a long session at the pub?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#6

Re: DROOP

02/07/2013 12:19 PM

DROOP is defined as the ratio of variation of VOLTAGE (In the Elec. Circuit) from NO-LOAD VOLTAGE to FULL LOAD VOLTAGE i.e.(Vno-load - Vfullload) x 100 /Vno-load %

DROOP is defined as the ratio of variation SPEED (in the Mech.Field - Prime Movers) from NO-LOAD SPEED to FULL LOAD SPEED i.e. (Nnoload - Nfullload) x 100/Nnoload %

BOTH DROOPs i.e. for Electrical - VOLTAGE DROOP as well as Mechanical - Prime Movers,SPPED DROOP IS VERY ESSENTIAL for SYNCHRONISING THE SYSTEM, for PARALLEL OPERATION.

DHAYANANDHAN.S

Register to Reply
Register to Reply 6 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); dhayanandhan (1); msamad (1); PWSlack (1); spiral88 (1); stevem (1)