Hello there, my name is Philip and I am from Holland but live/work in California. A year ago my company installed 20 HAF fans in a 2 acre greenhouse. The owner did not start using them till six months ago. After 3 months of use the cable on one of the fans burned true. We found out that wherever the cable was touching the grid it was wearing out really quick. First we thought the cable was just worn out between the housing and the protective grid of the fan. This was a tight fit and we changed it to a bigger space so the cable only touched the grid and not the housing. Now again 3 months later the cables started to wear out again. Since I was sure it was not vibration it had to something else. The cable is sufficient for the power but it almost looks like the cable melts where it touches with the grid. These fans came from Holland so they are 220VAC 50/60htz. To hook them up the local electrician used 2 hot legs of 120VAC. If I measure the voltage between the 2 I measure around 230VAC. The fans are hooked up to a frequency control, so you can also run them anywhere between 140VAC-230VAC. When I did some more research I found out that one of the hot-legs was a stinger-leg. Between neutral and this leg I measure 220VAC, between the other leg and neutral I measure 120VAC. Between the two I still measure 230VAC. I past this information on to a local electrician to take a look at it. He told me the next day that the fans where running of of 360VAC because of the stinger leg... Can some one tell me a little bit more about stinger-legs since we never had those back in Holland?