My work place using the ABB REF542 plug motor feeder protection relay for the 11 to 6.6 KV motor, and this protection system in serial with instrument protection (motor winding RTD trip function).
Happen few time the motor operate at full load condition, and the RTD protection drive give the false commend to stop the motor .
After check & reset the fault and restart the motor , the motor trip by the ABB REF542 plug motor feeder protection relay by high motor temperature.
Cause by the high motor temperature, need to wait for 1 and a haft hours until the ABB motor protection relay temperature drop to 60 deg C.
trouble shooting found :
Protection Setting :
motor temperature protection for class B insulation is 120 deg C, Protection relay set at 130 deg C and the reset temperature is 60 deg C
Actual motor running at full load current is 45 Amp and the temperature show at the protection relay is 112 deg C ,Once the motor stop or trip. the temperature and the current value still lock by the protection relay and once the motor restart immediately and the starting current value will top up to the old value and cause the motor trip by high motor temperature. ( Actual motor temperature show on DCS is 110 deg C )
I have ON and OFF the protection relay (master reset ), but the temperature still lock by the relay.
Can any one tell me how to quick reset the high motor temperature at ABB REF542 plug motor feeder protection relay ?