Anonymous Poster

Motor-Generator Set

04/05/2010 5:30 AM

Hi all

I want to install the motor generator set in order a constant output voltage. The motor which is coupled to the alternator is 110kw, 189A name plate readings. The utitlity power supply cable which will be the input to this motor is 35mm sqr. Will this cable be able to supply this three phase motor or does the motor draw full load current indicated on the name plate.

Regards

Dickson Mtonyole

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
2
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#1

Re: Motor-Generator set

04/05/2010 4:03 PM

For a motor load, the cable selection must be based on motor full load current, even if the motor draws less current during normal run condition. A single 35 mm2 cable is not able to carry 189A current, so the cable size is not enough. If you want to run the motor continuously, you need a cable of ampacity for at least 189 x 1.25 = 236A (intermittent run requires minimum 189A). There are also many other factors need to be considered for the cable selection such as voltage drop, ambient temperature, cable raceway etc.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Reply Good Answer (Score 2)
Commentator
Engineering Fields - Electrical Engineering - New Member India - Member - New Member

Join Date: Dec 2009
Location: Bangalore,India
Posts: 80
Good Answers: 1
#2

Re: Motor-Generator Set

04/06/2010 1:34 AM

Dear Mr. Dickson,

Further to the good suggestion by Mr. Msmad, i would like to add a further points :

In order to select the cable sizes, following factors need to be considered :

1) Voltage rating and 3 phase/1 phase

2) frequency of supply

3) Voltage drop

4) load current

5) Thermal current( which will decide the heating of cable and subsequent thermal equilibrium the conductors will reach)

6) Protective device( if the current rating of protective device is much higher than the actual load current in the cable, derating factor needs to be considered. it is recommended that the rating of protective device is as close as possible to the actual load current flowing in the cable)

7) ambient temperature

8) short circuit current of the source and the fault clearing time of the protective device. Higher the fault clearing time , higher cross-section of conductor is required.

9) Most important : whether copper conductor or aluminium conductor.

10) Method of cable laying and grouping

11) Length of cable

The above points mentioned is incomplete, but the above points which are mentioned, i am of the opinion is that are most important and major. In some cases, even harmonic current needs to be considered for cable sizing( for case to case basis)

For much better information and tools for calculation of cable sizing please check this site : http://myelectrical.com/pages/cables/cableSizing.aspx.

Thanks and Regards

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: Motor-Generator Set

04/06/2010 3:04 AM

→ British Standard 7671.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Anonymous Poster
#4

Re: Motor-Generator Set

05/26/2010 2:51 AM

i m working on Dc motor ,means i m giving suppy to dc motor in motor generator set ,so how to load dc motor in motor generator set.

Reply
Reply to Forum Thread 4 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); msamad (1); PWSlack (1); shanbhag (1)

Previous in Forum: Making an AC Generator Head   Next in Forum: Heater Makes My Fluorescent Light Dim!

Advertisement