No-load losses

04/09/2010 10:41 AM

I have a wye delta transformer, and have performed the no load test, I`v connected the source to wye side.

The thing is that when i ground the wye side of the transformer the total no-load losses are greater than the ones when the wye side is not grounded. I know it could be because of the zero sequence current flowing on the delta side. But would like a deeper explanation, ¿could someone help?

Register to Reply
Pathfinder Tags: no-load losses
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Commentator

Join Date: Nov 2009
Location: PA
Posts: 83
Good Answers: 1
#1

Re: No-load losses

04/09/2010 11:10 AM

So what is your reply for Wye Delta Transformer Acting as a Source thread?

Register to Reply
2
Anonymous Poster
#2

Re: No-Load Losses

04/14/2010 9:56 AM

First of all make it clear that zero sequence current flows only in the neutral and as in delta connection there is no neutral point so there is no zero sequence current in delta winding.

Secondly when you ground the neutral point of star winding and measure no load losses,your losses will be higher because the tank body and clamping structure of transformer is grounded the and stray looses occuring in them adds to the no load loss measurement but if neutral is not grounded then you are measuring only the core losses.

Register to Reply Good Answer (Score 2)