Limit of Capacitors Connected on a Transformer

04/11/2010 1:07 AM

Dear All,

I am facing a situation where there are two transformers connected to the supply source. One is a furnace transformer and the other is a distribution transformer. The overall power factor needs to be corrected to unity to avail the maximum PF incentive offered by the supply company. The furnace transformer secondary is an odd voltage (850V). The distribution transformer is 630kVA, 33kV/433V which is for the auxiliary equipments.

Now, with 400kVAr, 440V capacitors connected (8 nos. x 50 kVAr) to the distribution transformer secondary, the overall P.F. is 0.97, still short of unity. Theoretically, to improve the P.F. to 1.0, additional capacitors required are 260 kVAr (Furnace rating is 2200kW)

Finally, the question : Is it safe to connect a total of 660 kVAr capacitors on a 630 kVA transformer ? Is there any guideline for the maximum capacitor load allowable on a transformer ?

__________________
We Are In Current Control !
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster
#1

Re: Limit of Capacitors Connected on a transformer

04/11/2010 8:27 AM

its not safe.......total power kva= real power in kwatts+ apparent power in kvar...so according to yo specification total power s less than apparent power ..tht shouldnt happen........so either u increase kva or decrease kvar......or u do one thing , there s a software to calculate kva or kvar when u use a capacitor bank.....jus google free power factor correction software.......

Register to Reply Score 1 for Good Answer
Member

Join Date: Dec 2009
Posts: 5
#4
In reply to #1

Re: Limit of Capacitors Connected on a transformer

04/12/2010 2:09 AM

Kvar does not stand for apparent power, it is Inductive Reactance (varsL), or Capacitive Reactance (varsC), Total or apparent power in a RLC circuit equals the difference between Inductive and Capacitive reactances plus your pure resistive TRUE power.

If there is more Inductance in the circuit then the power factor lags, otherwise it leads.

VA/ WATT=PF

Register to Reply
Anonymous Poster
#5
In reply to #4

Re: Limit of Capacitors Connected on a transformer

04/12/2010 3:02 AM

sorry .....i meant reactive power but in a hurry i wrote apparent power ......my bad...............apparent power in kva= real power in kw+ reactive power in kvar

Register to Reply
Power-User
India - Member - design engineer Engineering Fields - Electrical Engineering - New Member United Arab Emirates - Member - New Member

Join Date: Feb 2010
Location: dubai,mangalore,bangalore.....
Posts: 145
Good Answers: 8
#9
In reply to #4

Re: Limit of Capacitors Connected on a transformer

04/12/2010 5:13 AM

watt/VA=pf ....not VA/watt.................@vicman

__________________
shamith gambhir, electrical engineer
Register to Reply
Anonymous Poster
#11
In reply to #9

Re: Limit of Capacitors Connected on a transformer

04/12/2010 8:09 AM

that is true, i guess that is why we use software to do the math for us

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: Limit of Capacitors Connected on a Transformer

04/11/2010 3:55 PM

I don't think your utility is very knowledgeable. PF correction to 0.97 ought to be deemed quite satisfactory. PF correction is kind of a "moving target" that depends on which motors are running and which capacitors are switched on. It is not practical to hit 1.00 PF exactly. Furthermore, if you overcorrect into a leading PF, I think you can get into positive feedback situations that are unstable. Thus the more usual criterion is to correct to maybe 0.95 or 0.97 PF.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Score 1 for Good Answer
Guru
Canada - Member - Specialized in power electronics

Join Date: Feb 2008
Location: Montreal, Canada.
Posts: 1372
Good Answers: 80
#12
In reply to #2

Re: Limit of Capacitors Connected on a Transformer

04/12/2010 11:57 AM

I was going to answer the same...

__________________
Experienced is earned, common sense is taught, both are rare essentials of life.
Register to Reply
Member

Join Date: Dec 2009
Posts: 5
#3

Re: Limit of Capacitors Connected on a Transformer

04/12/2010 2:00 AM

It is not practical to correct the PF to unity or 100%, 95% is by most standards the satisfactory PF correction for circuits containing large amounts of induction. When we actually calculate this by the book it would look something like this:

VA=P/PF

VARS(L)=square root of the square of VA- the square of P

VARS(C)=VA-VARS(L)

Xc=square of E/VARS(C)

Capacitance =1/(2)(3.1416)(f)(Xc)

Register to Reply
Active Contributor

Join Date: Feb 2010
Posts: 14
#6

Re: Limit of Capacitors Connected on a Transformer

04/12/2010 3:57 AM

since transformer is major source of reactive power(lagging) its compensation particularly during no load condition is very much necessary. again system power factor correction=load power factor correction + transformer power factor correction

as you have 400 kvar capacitor banks ,are they kept off during no load ? if so then you have to be some capacitors across secondary of transformer during no load to compensate .the exact kvar depends on impedence of the transformer but generally 3-7 percent of the transformer kva should be the right choice in your case. you have not explained about second transformer?

Register to Reply
Anonymous Poster
#8
In reply to #6

Re: Limit of Capacitors Connected on a Transformer

04/12/2010 5:06 AM

This is not correct.

The transformer no load reactive power consumption is only the magnetising current load which is not so important and does not affect the PF so much as to need correction.(unless you have a real bad transformer...)

No need to keep a capacitor in parallel on an open transformer connection.

Register to Reply
Active Contributor

Join Date: Sep 2008
Location: Mumbai, India
Posts: 14
#15
In reply to #6

Re: Limit of Capacitors Connected on a Transformer

04/13/2010 8:59 PM

Dear Shekhar,

Your analysis is right. The lagging PF is due to furnace transformer inductive load.

The furnace transformer is 33kV/850V, 3000 kVA. It is difficult to connect capacitors across the primary because of cost and across secondary because of odd voltage and harmonics. When furnace is off, we are switching off 200 kVAr.

Regards

__________________
We Are In Current Control !
Register to Reply
Commentator

Join Date: Oct 2009
Location: Dubai,UAE
Posts: 62
Good Answers: 2
#7

Re: Limit of Capacitors Connected on a Transformer

04/12/2010 4:55 AM

Yes It is safe and you have calculated the required KVAr to achieve unity PF in your system...It is hard but not impossible to achieve the unity,however you will get atleast 0.99.

more,you have to match your capacitor steps with your loads.I suggest you to have smaller steps,so that you will not get over capacitance.

correct me guys If I am wrong....cheers

__________________
There are no shortcuts on the road to a great experience.
Register to Reply
Member

Join Date: Jan 2007
Posts: 8
#10

Re: Limit of Capacitors Connected on a Transformer

04/12/2010 6:49 AM

Hi

Your 0.97 is excellent .

Don't change it .

Regards

Frome Morocco

Register to Reply
Anonymous Poster
#13

Re: Limit of Capacitors Connected on a Transformer

04/13/2010 11:13 AM

With 400kVAr, 440V capacitors connected (8 nos. x 50 kVAr) to the distribution transformer secondary, the overall P.F. is 0.97, still short of unity but sufficient for maximum PF incentive offered by the supply company as above 0.95 they can give 2% rebate (maximum) and below 0.95 only 1% .Theoretically, to improve the P.F. to 1.0, additional capacitors required are 260 kVAr (Furnace rating is 2200kW) which can be switched on separately with furnace and close watch on PF should be kept, or we can take trial with 200 kvar capacitor and pf recorded.

thanks

MANOJ KUMAR SINGH

GENERAL FOREMAN - URANIUM CARPORATION OF INDIA LTD.

NARWAPAHAR

Register to Reply
Participant

Join Date: Oct 2009
Location: JAMSHEDPUR, INDIA
Posts: 3
#14

Re: Limit of Capacitors Connected on a Transformer

04/13/2010 11:57 AM

With 400kVAr, 440V capacitors connected (8 nos. x 50 kVAr) to the distribution transformer secondary, the overall P.F. is 0.97, still short of unity but sufficient for maximum PF incentive offered by the supply company as above 0.95 they can give 2% rebate (maximum) and below 0.95 only 1% .Theoretically, to improve the P.F. to 1.0, additional capacitors required are 260 kVAr (Furnace rating is 2200kW) which can be switched on separately with furnace and close watch on PF should be kept, or we can take trial with 200 kvar capacitor and pf recorded.

thanks

MANOJ KUMAR SINGH

GENERAL FOREMAN - URANIUM CARPORATION OF INDIA LTD.

NARWAPAHAR

Register to Reply
Active Contributor

Join Date: Sep 2008
Location: Mumbai, India
Posts: 14
#16
In reply to #14

Re: Limit of Capacitors Connected on a Transformer

04/13/2010 9:09 PM

Dear Manoj ji,

We are ready to take the trial but are worried about the distribution transformer safety when we connect 400kVAr + 260kVAr = 660 kVAr as the transformer rating is only 630 kVA. The load on the distribution transformer is only cranes, pumps, lights and fan totaling 200 kW

It is difficult to connect capacitors on furnace transformer secondary due to odd voltage (850V) and harmonics and on primary (33kV) because of cost.

Regds,

__________________
We Are In Current Control !
Register to Reply
Anonymous Poster
#18
In reply to #16

Re: Limit of Capacitors Connected on a Transformer

04/14/2010 11:01 AM

dear sunilji

you can take 30kvar ,1.5kv capacitors in 6 numbers and connect it pairly in star connection with furnace switchgear.

1500v/1.732 =866 v ,that is near to 850 v.

this is the best solution .

thanks.

manoj

Register to Reply Off Topic (Score 4)
Power-User

Join Date: Mar 2010
Location: BHOPAL, INDIA
Posts: 201
Good Answers: 20
#17

Re: Limit of Capacitors Connected on a Transformer

04/14/2010 5:02 AM

It would not be safe to correct the power factor to unity nor it is required. Unity power factor means adding as much capacitors as much inductance in the circuit. This would result in resonance. The voltage across transformer as well as capacitors would be high and may harm the insulation.

Register to Reply
Member

Join Date: Dec 2009
Posts: 5
#19
In reply to #17

Re: Limit of Capacitors Connected on a Transformer

04/14/2010 8:03 PM

That is totally true, I am surprised no one mention this yet; at unity, the transformers and the capacitor banks become a huge tank circuit achieving resonance.

Register to Reply
Commentator
Engineering Fields - Electrical Engineering - New Member India - Member - New Member

Join Date: Dec 2009
Location: Bangalore,India
Posts: 80
Good Answers: 1
#20

Re: Limit of Capacitors Connected on a Transformer

04/16/2010 4:25 AM

Dear Sunilji,

I have analysed your question and also the opinions expressed by forum members and guests. Since the electricity is being used for a critical industrial application, I recommend that you conduct harmonic analysis and energy audit which will give details about the energy consumed, active KVA, reactive kVAR, power factor of the load(when capacitors are not used) and other energy details and the harmonic analysis will give the predominant harmonic present in the system. the above two analysis will provide you the capacitor kVAR along with the % of detuned filter to be considered for each transformer.

As per you problem, you have an odd voltage of 850V. that may not be a problem while selecting capacitors. you can contact EPCOS/ABB or any other reputed capacitor manufacturer for the correct solution.

As regards energy audit and harmonic analysis, you can contact CONZERV which is based in bangalore and is a Schneider group company. Infact for one of our projects, we had taken the services for the above companies.

Register to Reply
Anonymous Poster
#21
In reply to #20

Re: Limit of Capacitors Connected on a Transformer

07/07/2010 6:22 AM

I do agree on Harmonic study approach. Crompton Greaves Ltd., Aurangabad has an independent Power Quality Solutions division which can help in providing a comprehensive solution through their wide range of services & equipment. Please contact CGL at 9673333523.

Register to Reply
Anonymous Poster
#22

Re: Limit of Capacitors Connected on a Transformer

08/24/2010 12:44 AM

It is common problem in any process industry, where you have different loads and different voltage. In that Case, You need to consider Capacitor on HT side, there is no meaning of going for LT Capacitor when the PF is already maintained at the required and over saturation should not happen at any level. The power factor should be maintained at each voltage level. Necessarily, You Should consider Capacitor on Primary Side of the transformer to reduce the demand and to get incentive........

Reagrds

K.V.Imayavaramban

CR4 Admin - phone number removed

From the Site FAQ: Do not post phone numbers or email addresses. The CR4 Admin will delete all phone numbers posted in threads or comments, and we strongly urge you not to put up email addresses.

Register to Reply
Register to Reply 22 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!