Control valve hunting

04/16/2010 8:28 PM

I have a installed control valve on the discharged line of flare and valve open at 2% but it was hunting... I done auto calibration and valve optimized... any other option or suggestion on how to illiminate the hunting. my positioner is Fieldvue DVC6000

__________________
X-2per
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Control valve hunting

04/16/2010 10:20 PM

Apart from control tuning, another problem may be erosion or "wire-drawing" in the valve parts, so that it can no longer modulate smoothly.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Member

Join Date: Apr 2007
Posts: 9
#4
In reply to #1

Re: Control valve hunting

04/17/2010 10:37 AM

ive did travel stabilize/optimise but still same. I dont think thrs nothing to do with the wire-drawing. only around 2% opening valve is hunting at 3% valve is stable. what is it in my mind is maybe due to HP steam that 2% opening cannot hold the pesssure plus steam temp.

__________________
X-2per
Register to Reply
Guru
Canada - Member - Specialized in power electronics

Join Date: Feb 2008
Location: Montreal, Canada.
Posts: 1372
Good Answers: 80
#11
In reply to #4

Re: Control valve hunting

04/18/2010 10:42 AM

Most flow control valves are unstable at low percentage because the gain of the valve is much higher than at larger opening. To tune it properly to operate at 2%, you must reduce the gains that you obtained while tuning at higher percentage.

Once you make it stable at 2%, you will have a very sluggish response at higher opening. This is the nature of the beast unless you use a specially linearized valve aperture.

We usually avoid operating flow controllers at less then 5-10% of valve opening. If we do, we usually install a smaller control valve in parallel to do the fine control while the large one is closed.

__________________
Experienced is earned, common sense is taught, both are rare essentials of life.
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Control Engineering - New Member

Join Date: Mar 2006
Location: Washington USA
Posts: 566
Good Answers: 53
#2

Re: Control valve hunting

04/16/2010 10:34 PM

Is the valve sized properly for the application?

Is the controller PID, have you tuned the controller?

Register to Reply Score 1 for Good Answer
Member

Join Date: Apr 2007
Posts: 9
#5
In reply to #2

Re: Control valve hunting

04/17/2010 10:48 AM

I think valve sized is for that application. Ive done the preselected tuning set. by using gain value setted... at 2% only valve is hunting above 2% opening it is stable.

__________________
X-2per
Register to Reply Off Topic (Score 5)
Guru
Hobbies - Musician - Engineering Fields - Chemical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Instrumentation Engineering - New Member

Join Date: Jan 2007
Location: Moses Lake, WA, USA, Thulcandra - The Silent Planet (C.S. Lewis)
Posts: 4216
Good Answers: 194
#3

Re: Control valve hunting

04/17/2010 12:06 AM

Hi julius_8,

If your process requires the component supplied by the valve when the valve is open around 2%, it is way oversized - Ace Boeringa was on to something. The valve cannot operate well in this region because the errors at this level will create a very wide range of read errors in your Process Variable.

Sizing of the valve should be optimized for at least 50% open operation. What I mean by this is that; if your process requires around 50 litres/minute, your valve should be capable of providing 0 - 100 litres/minute (this is an example).

It may be that you need to acquire another valve.

Best Regards,

Mike

__________________
"Reason is not automatic. Those who deny it cannot be conquered by it. Do not count on them. Leave them alone." - Ayn Rand
Register to Reply Score 1 for Good Answer
Member

Join Date: Apr 2007
Posts: 9
#6
In reply to #3

Re: Control valve hunting

04/17/2010 11:02 AM

Hi Mike,

Ive done optimizing the valve by using the preselected gain value . meaning by using tuning set B-M (for selected proportional gain integral gain and feed back gain). but still same. So one thing i need to do more is to use travel tuning to EXPERTs by user define but how to use it? Is it advisable to assume value using the preselcted travel tuning sets?

Otherwise, it need to acquire another valve.

thanks once again.

__________________
X-2per
Register to Reply Off Topic (Score 5)
Participant

Join Date: May 2009
Posts: 3
#7

Re: Control valve hunting

04/18/2010 1:34 AM

Normal range of opening of control valve is between 30% to 70%- As in this range it will give you the best control and will maintain the setpoints- so definitely your controlvalve is oversized.

to eliminate this problem, you can provide properly sized Restriction Orifice at the upstream of the controlvalve which gives you some pr.drop and by that way you can have some more opening of the same Control Valve.

For sizing of any controlvalve , you have to provide the right process data - like Min. and Max. flowrate and pressure and temperature at that flowrate and range of opening of control valve so that it gives you better controllability.

Register to Reply
Associate

Join Date: Jan 2010
Location: USA
Posts: 27
#8

Re: Control valve hunting

04/18/2010 5:03 AM

Definitely go back and start from the beginning to see if the valve was sized properly. With operating specifications put into order with differential taken into consideration, then your safety factor. See what you come out with and what you have. Also make sure all aspects that go into sizing are true. Just because process is written one way, that doesn't necessarily mean that is what is in process always, sometimes changes are overlooked and not always changed or noted. What has changed? Why possibly were things changed? Just make sure you try to cover all bases, sometimes the obvious is the answer. Good luck...........

__________________
always find time to do it right the first time or.............................
Register to Reply
Commentator

Join Date: Mar 2009
Location: Georgia mountains
Posts: 64
#9

Re: Control valve hunting

04/18/2010 9:13 AM

Julius 8,

The problem is that the valve is only open 2%. Manufacturing precision for valve trim parts are not good enough at only 2% open to assure smooth operation in that region. Can you get a valve trim set with the same flow capacity and open at least 10% of travel? I assume that you did confirm that the flow characteristic is equal percentage for the valve trim installed. Fast opening or linear would not be good for the service you are describing.

Regards,

Luther M

__________________
There are old pilots and there are bold pilots, but there are no old bold pilots.
Register to Reply
Associate

Join Date: Jan 2010
Location: USA
Posts: 27
#10

Re: Control valve hunting

04/18/2010 9:27 AM

Good point Luther which brings me to a new question. I may have misseed it but is this rotary or linear? (6010-6020)

__________________
always find time to do it right the first time or.............................
Register to Reply
Anonymous Poster
#12

Re: Control valve hunting

04/23/2010 5:59 PM

try calibrateing the valve opening at 3.5%-4% that might solve the hunting problem.

Register to Reply
Register to Reply 12 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Ace Boeringa (1); Anonymous Poster (1); julius_8 (3); Luther M (1); marcot (1); Mikerho (1); rdbuch (1); Tornado (1); TRICKYDIC (2)