Rotork Actuator Problem

04/22/2010 9:59 PM

we have a rotork IQ series actuator, our compressor was shutdown due to our actuator sending out a FULLY CLOSED signal although operators were able to see that it is in a fully opened position.

diagnostics tell us that there is a position error indication.

as per manual limit open/close settings are retained even power supply is removed. is this the same also for its actual position circuit (which has a resolver) ?

what would happen if we move the handwheel when there is no power..how would it affect the position sensor?

i would appreciate any help/comment/suggestions

thanks.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Rotork Actuator Problem

04/23/2010 3:57 AM

According to the manual, the position indications are given by volt-free switches, so the position feedback is independent of power being applied to the valve motor; the contact should operate correctly when the valve is moved by hand.

  • Check out the wiring - are the cables picking up the right contacts?
  • Check out the settings - are the correct switches being operated at limits of travel?
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Participant

Join Date: Apr 2010
Posts: 1
#2
In reply to #1

Re: Rotork Actuator Problem

04/23/2010 5:13 AM

cables aren't faulty , settings are under scrutiny due to power outage

as of now, opened limit indication is not attained. it is stuck on intermediate position indication, while the lcd display is on 00% opening.

the last time, when the power supply was cut off, operators turned the hand wheel manually then the power was restored.

how will this affect the current position indication? from what i understand, current position is constantly being compared to the settings in the EEPROM then output is made.

could it be that actuator was unable to determine its actual position during the power interuption?

thanks

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3
In reply to #2

Re: Rotork Actuator Problem

04/23/2010 5:43 AM

<...as of now, opened limit indication is not attained. it is stuck on intermediate position indication, while the lcd display is on 00% opening....>

It sounds as though the set-up procedure, given in the manual, needs to be carried out again.

<...could it be that actuator was unable to determine its actual position during the power interuption?...>

Unlikely.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Active Contributor

Join Date: Apr 2010
Location: Sohar Refinary OMAN
Posts: 16
#4

Re: Rotork Actuator Problem

04/28/2010 1:21 AM

you have to do a function test for the actuater by seding signal to the actuator while the machine is down.

1-opening signal and you have to go 25%,50%,75% and 100% and watch the actuator response.

2- closing signal 25%,50%,75% and 100% and also watch the actuator response.

if you found there is adifferent so you have to re-setting or adjust opening and closeing value by the instrument people.

Reply
Anonymous Poster
#5

Re: Rotork Actuator Problem

04/30/2010 2:17 AM

Try using the Auma Actuators..

Reply