Strange Meter Reading

04/24/2010 8:51 AM

Hi I hope someone can explain this one to me.

I've just come back from fixing a powerless wall socket, the fault was a broken neutral conductor further down the circuit. Now when I first tested the socket with a test screwdriver both terminals lit up this would be explained by an appliance plugged in elsewhere on the same circuit returning the supply down the neutral with no where else to go so giving the appearance of two live conductors. Fine but when I put my multi meter across it Showed 415 volts! this is on a 220v single phase supply.

Once I found and repaired the broken neutral conductor the meter voltage returned to 220v and everything works fine.

Anyone know what could have happened?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster
#1

Re: Strange meter reading

04/24/2010 8:53 AM

additional info this was a radial circuit

Reply
Commentator

Join Date: Aug 2009
Posts: 97
Good Answers: 2
#2

Re: Strange meter reading

04/24/2010 9:05 AM

There was probably a capacitive and inductive load somewhere downstream, or upstream, and you were reading the result of a series-resonant circuit.

Remember, when the neutral is broken all loads are effectively in series, not parallel. so current will be constant, and voltage will vary at different points in the circuit.

HTRN

__________________
I'm too old to know it all, and too young to stop learning.
Reply
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#3

Re: Strange meter reading

04/24/2010 10:46 AM

I assume you used a DVM (?).

A DVM set to measure voltage has a very high input impedance - which is good as it presents a negligible load to the thing you're measuring, but can give misleading results.

The problem is that you can get capacitative and inductive pickup on a 'floating' wire (it acts as an aerial) - particularly if that wire is in the same cable or conduit as 'live' wires. Only a minute current would flow into the meter, so it could measure a considerable voltage, even though there would barely be any power there (power = voltage x current).

I suspect that you'd have measured little if anything using an "old-fashioned" meter such as an AVO.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Reply
Anonymous Poster
#4

Re: Strange meter reading

04/24/2010 11:21 AM

Hi. Thanks for those answers they make perfect sense. I was using a DVM and I was aware of the issues you've metioned, but unfortunatly I found myself questioning my readings only because I was explaining all this to an apparent expert earlier who tried to convince me I was wrong and the readings were impossible!

Many thanks

Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#5

Re: Strange meter reading

04/24/2010 1:31 PM

When you say "radial circuit" are you describing a 3-phase 415/220 delta/star system? If so, there would be some ways you could see 415V.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Anonymous Poster
#6

Re: Strange Meter Reading

04/24/2010 10:46 PM

Hi,

This is a common event in euro / africa /asian systems where grounding and neutrals are not as closely monitored as in the US and UK and you are getting feed back thru a device, over a common neutral, from another phase,

Soy Cowboy

Reply
Guru
Australia - Member - New Member Engineering Fields - Mechanical Engineering - New Member

Join Date: Sep 2006
Location: NSW Australia
Posts: 1101
Good Answers: 23
#7

Re: Strange Meter Reading

04/25/2010 9:43 AM

That is why test lamps are used to confirm voltages on lines where high impeadence meters can be misleading.

If you had an appliance plugged in up line it should have made no difference unless you had left the power supply to the circuit on.

__________________
Dont get on to the roundabout if you dont know how to get off
Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#8

Re: Strange Meter Reading

04/25/2010 3:47 PM

If you have a 3phase distribution circuiy, you have 415V between phase and 220V phase to neutral...OK?

Then if the Neutral wire coming to the socket in question is the one looping to other sockets or points with different pahses, you have had the neutral broken before reaching the particular socket! In this case, the part of the Neutral wire that is looping to other circuits will be at the voltage of the other phase where some appliance was connected to it: hence the 415V reading!

If any other appliance was working or ON, it must have exhibited some anomaly like low voltage or sudden surge or a lamp coming on when you switched something else...The isolated Neutral (from the supply neutral will become FLOATING in voltage sense...

Reply Score 1 for Good Answer
Member

Join Date: Apr 2010
Location: HARTFORD, CONNECTICUT
Posts: 6
Good Answers: 1
#9

Re: Strange Meter Reading

04/26/2010 10:03 AM

When troubleshooting, never use a test screw driver, use a moving coil tester it will give real voltage readings.

The reason why you are getting this 415v reading is because the original wiring most likely used the same neutral for another load with a different line supply which is against good wiring. I think this is against code.

So, you'll read between twoi line supplies without the neutral.

Test screw driver is an instrument just for testing the presence of voltage, never for determining how to fix circuits.

Live and learn.

__________________
GOD BLESS AMERICA
Reply
Reply to Forum Thread 9 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (3); EZStreet (1); garth (1); huchin (1); JohnDG (1); LAA_Lucke (1); Tornado (1)

Previous in Forum: Resistor Value Calculation Needed   Next in Forum: Motor Burned Without Tripping My ELCB Circuit Breakers

Advertisement