Motor Burned Without Tripping My ELCB Circuit Breakers

04/24/2010 3:21 PM

Dear friends,

I am facing a problem, actually I cannot explain what happen. I encountered fire in the apartment without tripping my circuit breakers. Actually this is what happen, I have a protection to my socket outlet in the kitchen which protected with 32A.ELCB installed in a distribution board, what happen is there was a fire incident in the socket outlet connected with a water heater without a water ,then suddently the water heater motor was burned ..my question is why my 32A.ELCB did not trip.

pls help me regarding this matter

sean

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: motor burned without tripping my elcb circuit breakers

04/24/2010 5:07 PM

On overheated element such as this would in time burn through some insulation, resulting in arcing between parts. An arc does not necessarily draw a large current, so a regular CB might not trip. Various types of ground fault detecting CBs exist that can respond to such faults.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Member

Join Date: May 2009
Posts: 5
Good Answers: 1
#2

Re: Motor Burned Without Tripping My ELCB Circuit Breakers

04/24/2010 11:21 PM

IT IS SIMPLE TO UNDERSTAND. AN ELCB, IF PROPERLY INSTALLED AND TESTED, WOULD ONLY OPERATE IN CASE OF AN EARTH FAULT. A THROUGH FAULT OR OVERLOAD OF ANY INTENSITY WILL NOT OPERATE IT, BUT A SMALL EARTH FAULT OR LEAKAGE CURRENT OF 30 TO 300 mA WOULD OPERATE IT INSTANTANEOUSLY TO ISOLATE THE FAULTY CIRCUIT. IT IS PRETTY SURE THAT NO EARTH FAULT WAS INVOLVED IN YOUR CASE. BUT IF EARTH FAULT WAS INVOLVED, THE ELCB WAS NOT PROPERLY INSTALLED/TESTED. NORMALLY PROPERLY RATED CIRCUIT BREAKERS ARE CONCURRENTLY USED TO TAKE CARE OF OVERLOADS AND SHORT CIRCUITS IN THE DISTRIBUTION BOARDS.

Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3
In reply to #2

Re: Motor Burned Without Tripping My ELCB Circuit Breakers

04/24/2010 11:29 PM

1. Please turn off the all-caps.

2. Every sentence of that is incorrect in some respect.

3. Sorry, but not very.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply Off Topic (Score 6)
2
Member

Join Date: May 2009
Posts: 5
Good Answers: 1
#4
In reply to #3

Re: Motor Burned Without Tripping My ELCB Circuit Breakers

04/25/2010 12:16 AM

Dear Tonado,

I am sorry if 'all-caps' bothered you. "ELCB" , as I understand is 'Earth Leakage Circuit Breaker' which is meant to operate in case of an Earth Fault and is rated 32 Amps, 60 Amps, 100 Amps etc. Tripping current normally starts from 30 mA to 300 mA. Higher/lower rated ELCB's may be in the market. And there may also be combined Over-current/ Earth leakage circuit breakers available too. My comments were about ELCB's non operation as being due to no earth fault having occured or faulty ELCB.

I hope I have cleared the controversy if any.

Mqureshi

Reply Good Answer (Score 2)
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#8
In reply to #4

Re: Motor Burned Without Tripping My ELCB Circuit Breakers

04/25/2010 6:47 AM

Right on the button and a GA from me.

__________________
"What others say about you reveals more about them, than it does you." Anon.
Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#13
In reply to #4

Re: Motor Burned Without Tripping My ELCB Circuit Breakers

04/26/2010 12:48 AM

Oops, my fault. I'm used to the terminology "GFCI" (ground fault circuit interrupter), and I misunderstood "ELCB" as a conventional circuit breaker, as for overcurrents or short circuits. And my apologies. I should have looked more closely, and and understood "ELCB" correctly. Thanks for setting me straight (GA).

Thanks also to Andy, who pointed out a few posts later that I was wrong (GA).

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#7
In reply to #3

Re: Motor Burned Without Tripping My ELCB Circuit Breakers

04/25/2010 6:45 AM

Wrong.

__________________
"What others say about you reveals more about them, than it does you." Anon.
Reply Score 1 for Good Answer
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#6
In reply to #2

Re: Motor Burned Without Tripping My ELCB Circuit Breakers

04/25/2010 6:44 AM

A perfect answer (except for the CAPS, PLEASE DO NOT SHOUT!!!)

I have given you a GA, someone else gave you an off topic (probably because you were shouting too much!).

__________________
"What others say about you reveals more about them, than it does you." Anon.
Reply
Power-User
India - Member - design engineer Engineering Fields - Electrical Engineering - New Member United Arab Emirates - Member - New Member

Join Date: Feb 2010
Location: dubai,mangalore,bangalore.....
Posts: 145
Good Answers: 8
#5

Re: Motor Burned Without Tripping My ELCB Circuit Breakers

04/25/2010 1:20 AM

can u provide a little more details abt the installation of the distribution board of ur apartment........havent u installed mcb along with elcb....?if not , then thts the problem ....an elcb will not trip on overcurrent or short circuits........it only trips when current flows through neutral wire (earth fault).......probably there was an overload condition and thts y ur motor heater was burnt......jus provide a lil more details.........nowadays a new type of elcb or rccbs are used which provides protection from overcurrent and earth leakage currents...they r called rcbo....u can use tht

__________________
shamith gambhir, electrical engineer
Reply
Member

Join Date: Jan 2010
Location: JHARKAHND INDIA
Posts: 5
#9

Re: Motor Burned Without Tripping My ELCB Circuit Breakers

04/25/2010 10:49 AM

The problem is related to lose contact and local heating in the socket due to IR loss and heating in the socket. In such cases the burning is not due to over current. The ELCB provides protection against short ckt and over current and not local heating

N.C.AGRAWAL

Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#10
In reply to #9

Re: Motor Burned Without Tripping My ELCB Circuit Breakers

04/25/2010 1:29 PM

Simply not true...

An "Earth Leakage Trip Breaker" provides a trip ONLY when there is a "leakage" to earth.

Some also have "over current" sensing built in as well, I do not know what the full correct name is then, but assuming he had one of these of say 30 amps, then 25 amps can cause a fire, but would not trip the breaker.......

He really needs an "over temperature" sensing built into where the water heater is.....

I expect that the water heater's normal current is well below 30 amps, so he should install a current breaker, just for the heater, dimensioned to trip with say a 10-15% larger current than the heater normally takes.....

__________________
"What others say about you reveals more about them, than it does you." Anon.
Reply
Power-User
India - Member - design engineer Engineering Fields - Electrical Engineering - New Member United Arab Emirates - Member - New Member

Join Date: Feb 2010
Location: dubai,mangalore,bangalore.....
Posts: 145
Good Answers: 8
#12
In reply to #9

Re: Motor Burned Without Tripping My ELCB Circuit Breakers

04/26/2010 12:26 AM

i don think thts completely true...i meant the second part..................elcb doesnt give protection from short circuits or overcurrents.............its rccb which gives protection from overcurrent but not elcb........an mcb is usually connected before the elcb in any distribution system in order to protect frm short circuits or over currents.............

__________________
shamith gambhir, electrical engineer
Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#11

Re: Motor Burned Without Tripping My ELCB Circuit Breakers

04/25/2010 4:03 PM

I am confused a little about the "Motor" ! Where this motor comes in a water heater?

In any case, Check the earthing of the Motor and the water heater body.

An ELCB of the old type that operates on voltage drop when there is a leak to ground can easily become faulty from previous trippings (specially if caused by shortcircuits to ground). A Residual Current Circuit Differential Circuit Breaker is the best because it is not affected by massif short-circuits to ground.

Allways check them once every 3 to six month or when you remember: Press the test button to trip them. If faulty they either do not trip or will not reset!

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#14

Re: Motor Burned Without Tripping My ELCB Circuit Breakers

04/26/2010 3:33 AM

32A @ 240V = 7680W.

What was the power rating of the motor, and why wasn't it protected with a motor overload protective device of lower breaking capacity downstream of the 32A breaker?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Member

Join Date: Apr 2010
Location: HARTFORD, CONNECTICUT
Posts: 6
Good Answers: 1
#15

Re: Motor Burned Without Tripping My ELCB Circuit Breakers

04/26/2010 10:25 AM

Circuit breakers do not protect electrical loads from overheating. They will only trip when the current exceeds its rating by another 10% 0f its designated rating.

The thermostat switch on the the unit should have tripped the power to the unit and motor.

Get a new unit.

__________________
GOD BLESS AMERICA
Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#16

Re: Motor Burned Without Tripping My ELCB Circuit Breakers

04/27/2010 1:39 AM

Despite my earlier misstep, I am still interested in the OP's question of why his ELCB failed to open. The GFCIs I mentioned will trip at around 5 ma of differential current. I think the OP later mentioned ELCB differentials of something like 30-300 ma, which is not as sensitive.

The specific type of fault I mentioned in post 1, an "arcing ground fault" (which is exactly what could occur in an overheated heating element), can take place with stray or leakage currents of less than 30-300 ma. Over time, a low-current spark could melt some wiring or start a fire without being detected by, say, an ELCB. Allen-Bradley, for one, makes an arcing ground fault detection system that may be more sensitive (and more costly) than typical ELCB methods.

This may be a candidate explanation of the OP's problem; or it may be yet something else.

[I too am still wondering about where the motor is in this water heater.]

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#17
In reply to #16

Re: Motor Burned Without Tripping My ELCB Circuit Breakers

04/27/2010 9:13 AM

Yes. What is the motor doing there?

Also, an RCD cb with 30 mA sensitivity is usually good enough for a water heater element leakage. An element failure because of water shortage in the heater is worrying since the heater should have some protection against the heater getting starved from the water (some kind of valve to prevent water going out without replacement...many questions to clarify for a proper advice...

Reply
Reply to Forum Thread 17 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard