Solid State Relay vs. Electromechanical

04/27/2010 2:17 AM

In a harsh environment, when should an AC solid state relay (SSR) be used instead of an electromechanical relay (contactor) for a 3-phase 20KW power supply load?

Thanks for your assistance,

DN

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#1

Re: When to prefer solid state relay over electromechanical

04/27/2010 5:46 AM

Really depends on the environment and stress. Vibrations, Intrinsic situation, Weather, Corrosion, Temperature, Character and type of the load. Elaborate your question pls.

__________________
Plenty of room here
Register to Reply
Power-User

Join Date: Aug 2007
Location: Lahore
Posts: 369
#2
In reply to #1

Re: When to prefer solid state relay over electromechanical

04/27/2010 6:58 AM

There are many conditions to use the SSR. Mainly there are two reasons;

1) When a load switches too frequently, we use SSR to beware of arcing problem.

2) When we want to switch the load for a very short moment (jogging).

__________________
Don't assume any thing, always check/ask and clear yourself
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3

Re: Solid State Relay vs. Electromechanical

04/27/2010 1:22 PM

Depends on what you mean by "harsh environment".

SSRs are good for long lasting, high speed solutions, but they reject heat that must be dissipated, approx. 1.5W per amp per phase. So if they need to go into a sealed enclosure in a harsh environment, then you must deal with that heat, i.e. extreme over sizing of the enclosure (if there is a low enough ambient temperature to allow convection dissipation) or an air conditioner, but A/Cs do not usually last long in "harsh" environments. You can sometimes use other means of external cooling (vortex cooler etc.), but there are other trade offs, such as a need for instrument air.

If by "harsh environment" you mean explosion proof, then often times the extra enclosure size is so expensive you may have to look for other alternatives.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: Solid State Relay vs. Electromechanical

01/19/2012 9:43 AM

"Harsh environment" conditions can be abated by using equipment enclosures with the correct Ingress Protection rating, then regular equipment can be installed within.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856