Difference Between Relay and Contactor

04/27/2010 7:12 AM

Dears,

What is the difference between a control relay with 5A contact rating like OMRON MY2N and a 5A rated motor contactor? Both contact rating are the same. Can we use a relay to switch the motor.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#1

Re: Diffrence between relay and contactor

04/27/2010 7:17 AM

As long as it's a single phase motor drawing less than 5 amp, I don't see why not. The starting current will be higher than running current, but should be OK as it only lasts a short time. Might be worth checking with supplier to be sure.

Cheers..........Codey

__________________
Give masochists a fair crack of the whip
Reply Score 1 for Good Answer
Commentator

Join Date: Sep 2009
Location: INDIA
Posts: 92
#2

Re: Diffrence between relay and contactor

04/27/2010 7:43 AM

Basically relay are used for controling the power where as contctor is used for switching on off the power.

Reply Score 1 for Good Answer
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#3

Re: Diffrence between relay and contactor

04/27/2010 7:45 AM

The life of the device in it's application. Motor contactor is design for the high currents of the inductive load of a motor at start up. The relay is not it is design as a control circuit switching device. The springs and armature of the contactor are design to reduce the amount of time that it takes to open and close. Which reduces the arc upon opening and closing. Some of what helps this is the motion of the contacts as they make or break. A relay usually swings in a arc a contactor straight. There may also be arc reduction device around the contacts of a contactor.

If you do decide to use a relay use a two pole and switch both the hot and the neutral to the motor.

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#4
In reply to #3

Re: Diffrence between relay and contactor

04/27/2010 8:06 AM

He doesn't say what size of motor is involved. On e.g. domestic heating systems the recirc pump is switched on/off direct from contacts on thermostats, which works OK for years. More complicated systems may include relays as well.

Cheers........Codey

__________________
Give masochists a fair crack of the whip
Reply
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#5
In reply to #4

Re: Difference between relay and contactor

04/27/2010 8:33 AM

Your right he doesn't say what the motor load will be. Just asked the difference between the two. The HVAC manufactures have years of experience with what will work and what will not. They know what the motor loads will be in designing a system to make that decision. We were provided very little on what he is trying to do.

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#6
In reply to #5

Re: Difference between relay and contactor

04/27/2010 10:27 AM

OK, agreed......Codey

__________________
Give masochists a fair crack of the whip
Reply
Guru
Engineering Fields - Instrumentation Engineering - New Member

Join Date: Dec 2009
Location: San Antonio, TX USA
Posts: 844
Good Answers: 29
#7

Re: Difference Between Relay and Contactor

04/27/2010 11:52 AM

If you're going to use a control relay to operate a motor instead of a contactor, where are you getting your overload protection?

__________________
"Do not worry about your difficulties in Mathematics. I can assure you mine are still greater". - Albert Einstein
Reply
Guru
India - Member - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Oct 2006
Location: India, 200 Km. North of Delhi.
Posts: 1393
Good Answers: 53
#8

Re: Difference Between Relay and Contactor

04/27/2010 12:33 PM

Even if they are of same rating there is a difference. Contactor offer you auto reset facility on power failure and also have over current safety features. You will have to add some electronics if you want to this with a relay.

Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#9

Re: Difference Between Relay and Contactor

04/27/2010 1:26 PM

Contactor's typically have an inductive rating, relay contact ratings are typically resistive. If you look at the specs for your "5A" relay, it will likely tell you that the inductive load rating is only 1A, and if you look at the "5A" contactor, it may tell you that the resistive rating is 9A. Those are just examples, not rules, what I am saying is do not consider specifications flippantly, it bears scrutiny.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply Score 1 for Good Answer
Anonymous Poster
#10

Re: Difference Between Relay and Contactor

04/27/2010 9:25 PM

As my ol' buddy Ray used to say..... " A relay spanks a contactor " The short of it is....a relay generally tells a contactor to go to work....

Reply
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#11

Re: Difference Between Relay and Contactor

04/27/2010 11:52 PM

In my opinion the relay can not be used for motor control in the power circuit.

Relays contacts will not withstand the starting current .The number starts per hour is also matters.

The stalled current flow also to be taken into consideration for using the relay.

__________________
Ramesh,Freelance Electrical/automation Consultant
Reply
Reply to Forum Thread 11 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); Codemaster (3); JRaef (1); luv123 (1); ozzb (2); rakesh_semwal (1); ramvinod (1); RDGRNR (1)