LT Cable Sizing

04/27/2010 7:40 AM

Why isn't short circuit current considered while sizing LT cables?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: LT Cable Sizing

04/28/2010 11:04 PM

This point has been discussed in one of IEEE conferences, and the conclusion was : In case the cable is well mechanicaly protected and the system is redudndunt, the maximum short circuit can be calculated at the end of the cable, otherwise the maximum short circuit shall be calculated at the upstream point.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: LT Cable Sizing

04/29/2010 3:12 AM

It is, in British Standard 7671.