Air Handling Unit - Cooling Coils Calculation

04/30/2010 10:49 AM

please can anybody send me the details of how the cooling coil selection for air handling units and rows of cooling coil if any calculation is there please send me the details

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Commentator
Australia - Member - New Member

Join Date: Apr 2010
Location: Western Australia
Posts: 92
Good Answers: 7
#1

Re: Air Handling Unit - Cooling Coils Calculation

04/30/2010 11:42 AM

Your question is not well defined.

I suggest you purchase or borrow a book called "Process Heat Transfer" by D. Q. Kern, and read the relevant section.

Register to Reply
Guru

Join Date: Jan 2010
Posts: 2446
Good Answers: 60
#2

Re: Air Handling Unit - Cooling Coils Calculation

04/30/2010 1:11 PM
Register to Reply
Power-User

Join Date: Mar 2009
Location: O'er looking the silvery Tay
Posts: 255
Good Answers: 18
#3

Re: Air Handling Unit - Cooling Coils Calculation

05/01/2010 5:58 AM

Hi,

Contact the manufacturer of the AHU. They have the software to size the battery in terms of air flow rate, required off-coil temperature and working temperature of the cooling media. You must also know the ambient (on-coil) conditions as there may well be a de-hum function to consider, therefore both sensible and latent heat loads can be present.

You will save time and get a more realistic outcome if you follow this path.

Massey.

__________________
If it ain't broke,leave it well alone .........until it comes looking for you!
Register to Reply
Power-User
United States - Member - US Citizen - Born & Raised Engineering Fields - Control Engineering - HVAC/R Simplified Using PLC Controls Engineering Fields - Instrumentation Engineering - HVAC/R Simplified Using PLC Controls Engineering Fields - Energy Engineering - HVAC/R Simplified Using PLC Controls

Join Date: Mar 2007
Location: Brick, NJ (USA)
Posts: 110
Good Answers: 5
#4

Re: Air Handling Unit - Cooling Coils Calculation

05/01/2010 7:11 AM

In order to size a thermal transfer coil (hot water, chilled water, refrigeration), the design engineer is required to know the following:

1. CFM of the air handler

2. Thermal load in BTU/Hour

3. Design temperatures including internal set points, outside air design, building U values, building orientation, etc.

4. GPM required for the load or pounds of refrigerant required for the load.

What are your design requirements? Once these are known, you can utilize the ACCA Manual J or N calculations to size your coil. Once the tonnage or heating BTU/Hour is known, the coil manufacturer can build the appropriate coil to fit your AHU.

__________________
"Memorize the calculations, you look like a fool searching your notes while teaching class"
Register to Reply
Commentator
Australia - Member - New Member

Join Date: Apr 2010
Location: Western Australia
Posts: 92
Good Answers: 7
#5
In reply to #4

Re: Air Handling Unit - Cooling Coils Calculation

05/01/2010 7:26 AM

BTU, CFM, GPM, OMG.

I am sure your advice is well founded in practice, but one has to feel sorry for you guys working in these antiquated units. Heat transfer coefficients are one of the best examples of the awkwardness of the Imperial measurement system.

India has had the metric system for more than 50 years, as I understand it.

Register to Reply
Guru

Join Date: Jun 2008
Location: Oman
Posts: 612
Good Answers: 14
#6

Re: Air Handling Unit - Cooling Coils Calculation

05/01/2010 7:33 AM

I presume that you are from India. Based on load calculations refer Voltas or blue star handbook or their software to select the AHU and coils. If you want to design a coil you have to understand the design of heat exchanger either by LMTD or Effectiveness NTU method.

Register to Reply
Anonymous Poster
#7

Re: Air Handling Unit - Cooling Coils Calculation

10/19/2010 1:29 PM

if anyone send the same pls forward me at

CR4 Admin - email address removed
From the Site FAQ: Do not post phone numbers or email addresses. The CR4 Admin will delete all phone numbers posted in threads or comments, and we strongly urge you not to put up email addresses.