What is impedence of a transformer?

05/01/2010 4:00 AM

What is impedence of a transformer?

1.I want to know what is impedence of a transformer.

2.What is the purpose of NGR connected with Alternators

3.When earthing transformers should be include in the circuit?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: What is impedence of a transformer?

05/01/2010 5:23 AM

1. If you mean the percentage impedence of the transformet it means the ratio of the voltage( that if you applie it to one side of the tranfsformer while the other side of the transformer is short cuitcuted, a full load current shall flow in the the short ciruted side), to the full load current.

2. NGR is used to limit the earth fault current.

3. Mainly in case of delta connection where there is no return earth pass

Register to Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#2
In reply to #1

Re: What is impedence of a transformer?

05/01/2010 9:32 AM
__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)