60 Hz to 50 Hz Conversion

05/09/2010 3:44 AM

We are looking for conversion of about 40 Kw of power from 480 V 60 Hz to 415 V 50 Hz.

Can anybody suggest me about the Systems available for this conversion. The load included Motors, lighting, battery charger.

Is static vonverter ok to run motive loads? or MG Set is required?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: May 2007
Location: Geelong, Australia
Posts: 1084
Good Answers: 54
#1

Re: 60 Hz to 50 Hz Conversion

05/09/2010 10:28 PM

It's probably cheapest to buy an off the shelf 40kW VFD.

They don't care what frequency is input and will output 50Hz. Plus they have excellent overload protection, V & I monitoring and power metering built in.

__________________
If there's something you don't understand...Then a wizard did it. As heard on "The Simpsons".
Register to Reply
Member

Join Date: Jul 2009
Posts: 5
#2
In reply to #1

Re: 60 Hz to 50 Hz Conversion

05/09/2010 11:22 PM

Thanks for the reply. Our Loads include Motors, Lighting and Battery charger. Can I use a VFD to take 60 Hz input and provide fixed 50 hz output. This fixed power can be further distributed as required. Ofcourse, voltage levels as required.

If this can be achieved, it seems the cheapest option as standard VFDs are available. I have to check with the VFD Manufacturers.

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3
In reply to #2

Re: 60 Hz to 50 Hz Conversion

05/10/2010 12:03 AM

Many if not most or all VFDs can do this; you just program or enter on a keypad the desired output frequency. There may also be a voltage-proportional-to-frequency characteristic. This will fit your case pretty closely; 480V × (50Hz/60Hz) = 400V.

If the VFD cannot produce the required power (kw) at the reduced output frequency, then you can select the next higher size of VFD.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
Engineering Fields - Instrumentation Engineering - EE from the the Wilds of Pa.

Join Date: Feb 2006
Location: middle of nowhere, Pennsylvania
Posts: 2603
Good Answers: 63
#10
In reply to #1

Re: 60 Hz to 50 Hz Conversion

05/10/2010 9:27 AM

You will still have 480VAC, not 415VAC. There is a simple 2 transformer bank we use at our plant to convert three phase 480VAC to 415VAC. (actually about 408VAC, but close enough) See Acme transformer for wiring details. (we use this for simulating European voltages, but don't convert to 50HZ, since all our tested loads for lower voltages, although to be on a 50Hz source, are frequency independant - power supplies/vfd's -if we ever have to run a motor direct w/o vfd, then we too will need to change frequency)

Do you think this in conjunction with the VFD would give the required 415VAC at 50Hz.

__________________
Remember when reading my post: (-1)^½ m (2)^½
Register to Reply
Anonymous Poster
#4

Re: 60 Hz to 50 Hz Conversion

05/10/2010 12:07 AM

Hi

VFD is the best solution in the case where amplitude of voltage and frequency are of significant, in VFD, the ratio of both is significant so VFD is better for motor load,

whereas for lighing and battery load, where the voltage level has prime importance, VFD can't solve the problem.

regards

Divyesh patel

Register to Reply Score 1 for Good Answer
Power-User
Ireland - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: Aug 2007
Location: Northern Ireland
Posts: 197
Good Answers: 17
#5

Re: 60 Hz to 50 Hz Conversion

05/10/2010 1:24 AM

A VFD will certainly do this job but when you mention lighting & battery chargers etc I am beginning to assume you want to feed a distribution board, then take smaller circuits off this.

A VFD produces HF noise on the output which requires you to use screened cable between the VFD and the motor. Usually this is close and not too big a burden. However if you go hooking a standard cable network to this output, you will create a nice big antenna and could end up with HF noise everywhere. Unless the cables concerned are in steel conduit for example.

I have not tried to filter the output of a VFD and don't fancy the results. Just my tuppence 'orth.

__________________
I love deadlines; I love the whooshing sound they make as they pass by. - Douglas Adams
Register to Reply
Anonymous Poster
#6

Re: 60 Hz to 50 Hz Conversion

05/10/2010 1:37 AM

The VFD are better used for Motor drives not for static loads such as lighting and battery charger. we have better frequency converters available in market where a synchronous motor generator set will convert the available frequency to the frequency desired and the voltage can be converted through portable transformers as required. this is the most economical design as VFD's are very costly.

Register to Reply
Member

Join Date: Jul 2009
Posts: 5
#7
In reply to #6

Re: 60 Hz to 50 Hz Conversion

05/10/2010 3:40 AM

I was looking for a MG Set only in the first instance. However, if I can manage with a static converter, it will help in the operation & maintenance part.

Can you give me some vendor details who can supply MG Sets or Static frequency converters in the Middle East or India.

Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#8

Re: 60 Hz to 50 Hz Conversion

05/10/2010 8:00 AM

Which way is the conversion?

1- You have equipment designed to run on 60Hz 480V and you want to use them on 50Hz 415V ? or

2- You have equipment for 50Hz, 415V but power supply is 60Hz, 480V?

If 1) ** Motors will work OK except that the rpm will be reduced accordingly, therefore the output power (kW available on the shaft).

** Ordinary filament lamps will still work OK

** Anything having a choke or transformer will not be 100% OK. Must check the name plates to see if 60Hz is mentioned. Voltages must be considered, but might still be OK.

If 2) A Frequency Inverter for the Motors (3phase motors) OK

The other loads will have a problem mainly on the voltage issue: Transformer to drop the voltage will work for resistive loads.

For battery chargers and lights with chokes, Name plates references will sort some of them. Otherwise, the frequency / voltage combination must be looked at in terms of energy input... more dodgy without proper one by one study.

Register to Reply
Guru
Hobbies - HAM Radio - CE3AM....4X4SW....CE3NSW

Join Date: Aug 2006
Location: Santiago Chile.
Posts: 845
Good Answers: 7
#9

Re: 60 Hz to 50 Hz Conversion

05/10/2010 8:31 AM

To decrease VFD size (price) you can also by-pass all resistive and non frequency sensitive loads if they can support the slightly higher voltage.

Wangito.

__________________
Never trade luck for skill.
Register to Reply
Guru
Canada - Member - Specialized in power electronics

Join Date: Feb 2008
Location: Montreal, Canada.
Posts: 1372
Good Answers: 80
#11

Re: 60 Hz to 50 Hz Conversion

05/10/2010 9:48 AM

An AC drive can cause large problems if harmonics current distortion is an issue on your 480V feeder. Also mentioned above is the fact that the voltage regulation that you need for your loads is not the same as what is used on a motor. You would also need an isolation transformer for many loads as the output will contain large differential voltage spikes around the ground. There are issues about restart and overload that might not work well for you with most AC drive. It would not be a problem free application.

A properly designed AC/DC/AC converter like a UPS will do a better job. UPS are made for this application. You probably don't need the batteries or only a very small pack for added ride through capacity during brown out. If you cannot find a standard one off the shelf, drop me a line and I can make you one meeting your specific needs.

__________________
Experienced is earned, common sense is taught, both are rare essentials of life.
Register to Reply Score 1 for Good Answer
Register to Reply 11 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); BabyGuinness (1); ffej (1); LAA_Lucke (1); marcot (1); Phys (1); ramana_lanka (2); Tornado (1); wangito (1)

Previous in Forum: Circuit Breaker Calculations   Next in Forum: Tubular Bus Bar Correction or Derating Factor Table

Advertisement