SIL certificate or prior-use

05/11/2010 4:10 AM

I read some SIS expert answers to some questions and I realized that no requirement for certification of field instruments anywhere in ISA 84.01/IEC61511 for field devices. What about logic solver??.

Also Field devices should be selected based on proven performance "Prior – Use" then why manufacturers pay money to get SIL certificate for their devices?

and how end user know that this device is proven performance in the operating environment simply how to Select field instruments and logic solver for Safety Instrumented?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: SIL certificate or prior-use

05/11/2010 12:36 PM

The SIL certificate is of no value. It is the Report that provides the basis for the SIL certificate that is the thing of value.

As to why manufacturers pay money to get a SIL certificate, one possibility is that they use it to increase sales.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Commentator

Join Date: Nov 2008
Posts: 91
#2
In reply to #1

Re: SIL certificate or prior-use

05/12/2010 2:27 AM

What report you mean?can you show me example (link,or upload)

Register to Reply
Power-User

Join Date: May 2005
Posts: 161
Good Answers: 2
#3

Re: SIL certificate or prior-use

05/12/2010 10:31 AM

I think PWSlack answered the SIL Certificate question.

The issue with prior use, or proven performance, is that in order to be a SIL rated system, there is a requirement for maintenance and testing intervals, and records to be maintained. These records will indicate the frequency of replacement or the reliability of the components, which will give a "proven in use" history. The calculations for the computation of the SIL level treat all instruments (in general) the same, such as all pressure transmitters have equal PFD's, and all Temperature transmitters have the same PFD's. SIL level is changed by adding redundancy, or changing the frequency of testing, selecting different valves, and a few other things.

Logic solvers are classified as triple redundant, double redundant, trip amps, relays, dedicated safety rated PLC, and so on...there are only a few types to choose from, and each brand is treated the same since they have a common PFD range as far as the calculations go.

Selecting field instruments and logic solvers for a SIS depends on whether it is an existing system or a new system. In either case, a LOPA, Layer of Protection Analysis is performed to determine what SIL level is required based on a company's risk tolerance. After the SIL level required is determined, the existing system is analyzed to determine the SIL level and any changes required to raise or lower it are designed. A new system is simply designed to that SIL level. Selection of field instruments may be from a company's current inventory or it may be necessary to specify an instrument to meet the new design conditions.

Register to Reply