480VAC Question

05/12/2010 2:01 PM

How do you get 480VAC from only phases.

See schematic below.

In the schematic they take two phases of the 480VAC to a control power transformer for control voltage.

Don't you need to pull a neutral?

Phase to phase would be 208 correct not 480?

Please help me understand.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United States - Member - Member Engineering Fields - Electrical Engineering - Electrical Construction

Join Date: Apr 2010
Location: Mid Western USA - The Corn Belt
Posts: 1439
Good Answers: 58
#1

Re: 480VAC Question

05/12/2010 2:41 PM

No, you do not need to pull a neutral. When you ground one side of the control transformer secondary, that grounded secondary side becomes your control circuit neutral.

On a 480 Volt, 3 Phase, Ungrounded System, phase to phase or phase to ground is 480 volts.

__________________
The first 5 days after a weekend are always the hardest................................
Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#6
In reply to #1

Re: 480VAC Question

05/13/2010 6:14 AM

All you said is OK except "Phase to Ground is 480V":

If the system is Ungrounded, you have no Voltage to ground!

Conrol Circuit: If the transformer is of Isolating type(no links to primary like in an Auto transformer). I say that because the PO seems very uncompetent to be handling this issue. Maybe he will start learning or take a course.

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: 480VAC Question

05/12/2010 4:47 PM

Amendment to the foregoing: For 480, phase to ground is 480/√3 ≈ 277 volts.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3
In reply to #2

Re: 480VAC Question

05/12/2010 9:10 PM

Amendment to your amendment: He said 480V ungrounded systems, i.e. delta. 277V is the phase to Neutral voltage on a 4 wire Wye (Star) system, and assuming the neutral is grounded, it would be the phase to ground voltage as well.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#4
In reply to #3

Re: 480VAC Question

05/12/2010 10:14 PM

The control transformer shown in this schematic drawing is very common to the low voltage motor starters used in North America for the starter control and motor space heater supply. The primary of the control transformer is 480 V (line to line) and the secondary is 120 V. The transformer doesn't care about whether its primary supply is line to line or line to neutral. For the low voltage motor starter, the motor space heater (if the motor is => 15 HP) is supplied from the same control transformer. Most cases, this control transformer is CVT (constant voltage transformer – a type of ferroressonant transformer) for maintaining the constant control voltage supply so that the starter doesn't malfunction due to the voltage dip caused by starting of other motors in the vicinity.

Also see these recent postings related to this:

http://cr4.globalspec.com/thread/53729 (the heater mentioned in this question seems to be the motor space heater)

http://cr4.globalspec.com/thread/53686

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#5
In reply to #3

Re: 480VAC Question

05/13/2010 2:01 AM

If nothing in the system is grounded, couldn't the voltage to ground be arbitrary, so long as the phase differences remained in relation to each other?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#8
In reply to #3

Re: 480VAC Question

05/13/2010 8:49 AM

Yes, but...

If the system is not grounded, it is not automatically a "delta" system. In fact, in many instances where a "neutral" is not required by the load, the transformer will be a delta/wye configuration and the star point of the secondary will not be brought out of the transformer nor will it be grounded.

In this case, the transformer may be considered as an ungrounded delta system, and under the Canadian code, would require ground fault indication equipment be installed on the secondary. I assume the NEC is similar in this regard?

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#7

Re: 480VAC Question

05/13/2010 6:21 AM

Phase to phase is 480V (not 208V)

You don't need a Neutral for the transformer or else (The mains Neutral is not needed here)

The secondary is isolated from Primary in your circuit. Therefore, one of the secondary outputs can be grounded and called Neutral if the equipment controlled and supplied by it requires that (for actuating the protection devices mainly).

Finally, you seem to lack a lot on the subject: either consult a local competent electrical engineer if you are doing any repairs or project, OR get a course inthe subject.

Register to Reply
Guru
United States - Member - Member Engineering Fields - Electrical Engineering - Electrical Construction

Join Date: Apr 2010
Location: Mid Western USA - The Corn Belt
Posts: 1439
Good Answers: 58
#9

Re: 480VAC Question

05/13/2010 11:50 AM

My Apologies -

Clarification to my post:

480 Volt - 3 Phase - 3 WIRE - UNGROUNDED - DELTA - System

will result in volt meter readings as follows:

Phase to Phase = 480 Volts

Phase to Ground = 480 Volts

Grounding of one of the control transformer secondary conductors was recommended for proper operation of secondary interface devices/systems.

__________________
The first 5 days after a weekend are always the hardest................................
Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#10
In reply to #9

Re: 480VAC Question

05/14/2010 5:50 AM

"Ungrounded Delta, 3 wires system"!

How can you get 480V between Phase and Ground?

Phase -Phase 480V is OK but not phase-ground 480V ==> means one of the phases has a ground leak or ?? peculiar statement/situation....You have a fault somwhere??

Register to Reply
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#11
In reply to #9

Re: 480VAC Question

05/15/2010 1:30 PM

KJK/USA,

You persist in saying: Phase to Ground = 480 Volts, for an ungrounded three-phase delta supply. The actual voltage from any one phase wire to ground is not inherently determined. In practice it can vary from 0 to 480 volts and can also be higher. The actual voltage will be determined by the amount and balance of current flow, capacitance between the conductors and ground, internal resistance of the meter doing the measurement, mutual inductance with nearby wires, and other unpredictable factors.

If all circuit factors are equal and the meter's internal resistance is quite high compared to the capacitive charging of the conductors, then the voltage phase to ground will tend towards the middle (nominally 277 volts), which is the same as you would see in a properly grounded wye system. Since these factors are seldom equal, then the voltage you measure is unpredictable (in advance), and can easily be different from one moment to another (because of changes in the connected loads, etc.).

Thanks--John M.

Register to Reply Score 1 for Good Answer
Anonymous Poster
#12

Re: 480VAC Question

02/02/2011 10:53 PM

You don't need to pull a neutral based on the diagram you've shown. As a matter of fact, the two feeders were connected before the connections and from the line side of the delta-wye transformer given in the diagram and not after the transformer. There would be in no way the two loads would be in relation to each other and so do not pull the neutral wire of this transformer and connect it to the two phases given. Electrical disturbance shall arise if a reversal would be implemented.

Regards,

Odie

Register to Reply
Register to Reply 12 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!