Inadequate Power

05/14/2010 5:34 PM

3 CAT gen. sets, synchronised, each gen. is 95.9 amps, they have to power a 600kw electric motor, but the starting current for starting the motor is 450-600amps, the user cannot abandon the power station , is there any thing that can be done to amplify the power just for 17 seconds to start the electric motor, having in mind that each gen set is 1460kw, at 1825 kva.

Awaiting your reply

Best of regards ,

Mahdi H.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#1

Re: Inadequate Power

05/14/2010 6:37 PM

If you can maintain synchronization, you should have enough capacity to start and run the motor. Generally, you need about 2 to 3 times the full load kw of the motor.

Register to Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#2
In reply to #1

Re: Inadequate Power

05/14/2010 8:12 PM

First of all, read this thread: http://cr4.globalspec.com/thread/52712/RATTING-FOR-ALTERNATOR for required generating capacity for the motor starting.

Then,

1. As Wareagle already indicated, you can synchronize the generators and your total generating capacity is 1460 x 3 = 4380 KW which is enough to start the 600 KW motor.

2. You didn't mention the voltage; it seems the voltage is 11 KV (1825 / (1.732 x 95.9) = 11). The full load current (FLA) of 600 KW motor is then in the range of 50 A (600 / (1.732 x 11 x 0.8 x 0.8) = 49.2, with 80% efficiency). The maximum starting current may be 50 x 6 = 300 A (it is very common that starting current is 6 times of FLA). Why does the motor need 450-600 A starting current then?

3. However, if you have other loads in the system and need to start the motor with other loads running, I would suggest you to use VFD (Variable Frequency Drive) or Soft Starter for the motor. The selection of VFD or Soft Starter depends on other existing running loads in the system during the motor starting and the economic consideration.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply
Participant

Join Date: May 2010
Posts: 3
#5
In reply to #2

Re: Inadequate Power

05/15/2010 6:49 AM

Thanks for your swift reply, please still explain to me how you got the max. starting current, where did you get this formula?

best of regrds,

Mahdi.

Register to Reply
Guru
Engineering Fields - Instrumentation Engineering - New Member

Join Date: Dec 2009
Location: San Antonio, TX USA
Posts: 844
Good Answers: 29
#3

Re: Inadequate Power

05/14/2010 9:55 PM

First, WE and MS, Good shots! Now, where'd you get that 17 secs and why can't you delay each start to minimize the inrush to the overall load? Jim

__________________
"Do not worry about your difficulties in Mathematics. I can assure you mine are still greater". - Albert Einstein
Register to Reply
Guru

Join Date: Jul 2008
Location: Anywhere I may be at the time
Posts: 661
Good Answers: 16
#4

Re: Inadequate Power

05/15/2010 6:38 AM

1- Synchronization

2- VFD (soft starter)

3- Remove all load from motor (un-couple) upon start-up via pneumatic clutch for instance.

Register to Reply
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#6

Re: Inadequate Power

05/16/2010 12:31 AM

Apart synchronizing the generators try using a soft starter which can ensure gradual rise of current where u can set minimum value to 3or4PU .But whta is the driven eqipment .How long does the motor take to reach full or rated rpm.these are very important in any motor application

__________________
To avoid crticism do nothing,say nothing,be nothing
Register to Reply
Anonymous Poster
#7
In reply to #6

Re: Inadequate Power

05/16/2010 8:29 AM

The driven equipment is an electric motor 600kw, and it needs 17sec. to acheive full rated RPM.

Register to Reply
Guru

Join Date: Jul 2008
Location: Anywhere I may be at the time
Posts: 661
Good Answers: 16
#8
In reply to #7

Re: Inadequate Power

05/16/2010 8:44 AM

No, the question was "driven" not driver.

What is the 600kw motor turning? What work is the 600kw motor accomplishing?

If it requires 17 seconds to come up, it is likely starting under a heavy load

Register to Reply
Anonymous Poster
#9
In reply to #8

Re: Inadequate Power

05/16/2010 9:08 AM

The electric motor is driving a huge fan.

Register to Reply
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#12
In reply to #9

Re: Inadequate Power

05/18/2010 9:47 AM

Fan is a high inertia drive and will need a prolonged acceleration time.17seconds is a lot of time.Is it under DOL starting Pl? with a soft starter u can have a smooth starting but minimum starting voltage point needs to be calculated.this will require Torque vs speed curve of Fan superimposed on motor T_s curve.I suggest refer with fan details to motor and also to genset suppliers .A combined study will give a correct solution.

Regards

__________________
To avoid crticism do nothing,say nothing,be nothing
Register to Reply
Participant

Join Date: May 2010
Posts: 3
#10
In reply to #8

Re: Inadequate Power

05/16/2010 9:15 AM

Its actually a FORCED DRAFT FAN.

Register to Reply
Guru

Join Date: Jul 2008
Location: Anywhere I may be at the time
Posts: 661
Good Answers: 16
#11
In reply to #10

Re: Inadequate Power

05/16/2010 9:54 AM

OK a BIG fan.... So right back where we started, first be certain you are optimizing your power supply. Second look into a VFD, third you can look at mechanical solutions to lessen the start up torque spike. Third option has endless possibilities, just depends on your dimensional, time, and funds limitations.

Being a gear head, I would personally much prefer the later solution

Register to Reply