Switch disconnector alignment

05/15/2010 2:40 AM

in most of the drawings i ve seen , the switch disconnector is aligned in the main incomer such tht the protective devices r connected on its load side........but when i saw schneider catalogue they r suggesting an upstream protection for switch disconnector.......now my question s what s the correct alignment? breaker- disconnector or disconnector- breaker........if the answer s 2, then can anyone explain the sc or overload protection for disconnector?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#1

Re: Switch disconnector alignment

05/15/2010 6:35 AM

Protection for the switch disconnector (and the wiring to it) is assumed to have been installed at the distribution panel (or in a fused spur etc. en route).

__________________
"Love justice, you who rule the world" - Dante Alighieri
Reply
Member

Join Date: May 2010
Location: Guargaon, Haryana, INDIA
Posts: 5
#2
In reply to #1

Re: Switch disconnector alignment

05/15/2010 7:12 AM

Yes, I try to simplify. If you want the breaker to be repaired / serviced, you need not to go to Out-going of the up stream panel to isolate the panel, rather switch off the breaker, disconnect the isolator/ fuse link.

this is better in terms of engineering practice. In any case if you have selected the fuse & the breaker with type 2 co-ordination, the breaker trips in case of a fault within the range of kA rating of the breaker. Schneider uses a patented technology, thermal energy release to achieve this.

hope, I could answer your question.

__________________
thanks
Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#3

Re: Switch disconnector alignment

05/16/2010 12:09 AM

A switch-disconnector does not have inherent protection. As defined in IEC, it is capable of making and breaking normal current, capable of carrying short-circuit current, but not able to break it. When open, it will provide isolating distance. So, upstream short-circuit protection is a must.

The breaker itself is quite often the withdrawable type, so that any maintenance on it can be carried out by withdrawing it from its cradle to the isolated position.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply
Member

Join Date: May 2010
Location: Guargaon, Haryana, INDIA
Posts: 5
#4

Re: Switch disconnector alignment

05/16/2010 12:37 PM

Thanks, i partially agree, normally switch disconnects are provided before MCCBs, these are not draw out type. by giving the term disconnector ( and not breaker) we try to explain that the device is meant for operation under no-load or normal operation. thus a short ckt. is an abnormal condition. In any case a up-stream protection should be always present for a device to make other feeder work with same breaking capacity in co-ordination.

__________________
thanks
Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#5
In reply to #4

Re: Switch disconnector alignment

05/18/2010 7:10 AM

Just curious ... MCCBs not being maintainable, what is the need for an upstream switch-disconnector? It is usual to have an appropriate ACB at the transformer end, and have the sub-circuits fed through MCCBs. Co-ordination between the ACB and subsequent MCCBs is important of course, whether discrimination or cascading is used.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply
Member

Join Date: May 2010
Location: Guargaon, Haryana, INDIA
Posts: 5
#6
In reply to #5

Re: Switch disconnector alignment

05/19/2010 11:59 AM

Tricky.... Ha Ha, Type-2 Co-ordination or total discrimination asks for Protecting device & isolator. Normally manufacturers' do guarantee for co-ordination within the same switch board, not between an O/G ACB in PCC and an incoming MCCB in MCC.

I have seen ABB giving cascading through communication between these two but not electrically. Schneider guarantees the same electrically but at a higher cost.

By the way I thing the guest who raised the issue has not seen these at all, or has found his answer any way.

__________________
thanks
Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#7
In reply to #6

Re: Switch disconnector alignment

05/19/2010 12:04 PM

i am curious about Type 2. As far as i knew before, Type 2 coordination is in reference to motor starters and SCPD. The relay characteristics must not get changed after clearing the SC tests. i haven't come across Type 2 coord between isolators and breakers, would appreciate it if you can enlighten me a little on this...

__________________
Nothing worthwhile can ever be taught, it can only be learnt.