hI FRIENDS
anybody can give me details about pneumatic valve?
i want to take 4 signals from pneumatic valve
1.ON
2.OFF
3.Electric failure
4.Air failure
is there any possibilities to take these signals
client is asking for these signals
Good Answers: 183
Re: Pneumatic Valve Question
05/17/2010 9:36 AM
It depends on valve type. I assume it is a 2/2 valve with an electric vontrol. For this configuration the logics behind are:
- "ON" you must have a current detector of the coil which gives a "true" signal when the coil is energized and the command is on "ON"
-"OFF" it is the logical contrary of "ON" so that you must have a "false" signal from same sensor when the command is on "OFF"
- "Electric failure" is a problem of definition but if the 2 above controls are not giving a "correct" function indication then the valve is from the electric point of view a failure.
- "Air failure" again it depends on the valve type you can use a pressures sensor at outlet and verify that pressure is present when valve is open and electrical function is OK.
As you see obtaining such an information is neither easy low cost.
Have you analysed if your circuit is fail safe?
02/23/2022 10:47 AM
Yes. The valve manufacturer can. Telephone?