VFD Pump Control

05/17/2010 4:54 PM

GOOD EVENING

YESTERDAY we were discuss a complicated design from our design department for irrigation system consists of 8 pumps(165 kw each)(5 duty and 3 standby)

we found that the design like that:

  1. 4 big PPLC panels (pump protection logic controller) 1 for each 2 pump because the designer put (4 vibration sensors+ 1 flow switch+ and 8 RTD sensors 2 motorized valves) for each pump.
  2. 2 big PGC panels (pump group controller) to control the VFDs through PT (pressure transmitter)set points and to organise (or program) the exchange between pumps (because pumps will operate all the day and exchange each others with the standby ones (3 out 3 in))
  3. redundant servers and 2 printers and 2 workstations for scada system
  4. big DLP display unit for reservoirs and pumps
  5. big control console for move operation

i want to ask please:

  1. is it too much to use all this component for this small system ?
  2. those pumps really want vibration and RTD sensors?
  3. what kind of programs can exchange between pumps to give them equal rest and duty?
  4. scada system good for this system ?
  5. control VFDs with pressure transmitter PT is a good idea?
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
2
Guru
United States - Member - New Member Engineering Fields - Control Engineering - New Member

Join Date: Mar 2006
Location: Washington USA
Posts: 566
Good Answers: 53
#1

Re: VFD Pump Control

05/17/2010 9:35 PM

As I see it.

1. Too much is a relative term, as is small. It seems reasonable for protection and control of more than 1000HP worth of pumps.

2. The pumps do not want anything, the organization that is responsible should want to be able to sense a problem before it becomes a catistrophic failure.

3. Lead - Lag programs can accomplish this.

4. Scada would be my preference, it is good for many control applications.

5. If you want to control the pressure you should measure it.

Register to Reply Good Answer (Score 2)
Guru

Join Date: Feb 2008
Location: Large hole formally occupied by furry woodland creature.
Posts: 3385
Good Answers: 97
#4
In reply to #1

Re: VFD Pump Control

05/18/2010 5:18 PM

Ace,

My first thought was SMALL???

Although there is no mention of what is to be irrigated, it must be of high value and the system must be critical.

You get my vote.

__________________
CRTL-Z
Register to Reply Off Topic (Score 5)
2
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#2

Re: VFD Pump Control

05/18/2010 9:43 AM

Hi Nourbe

Seems you have a big project... what type of pumps are you using, how are they mounted, skid type or something else and the flow rate required? That would be my first set of questions.

However, as I have installed and commissioned many surface and downhole pumps I can tell you the following

Your designer is correct... you need the valves, flow switches and vibration sensors for the following reasons.

Valves: if a pump stops and others are running, the the back pressure will feed back through the tripped pump causing it to "backspin"(you make no mention of non-return valves). If the PPLC then tries to start the pump as it is back spinning it WILL break the motor or pump shaft. Back spin sensors attached to the motor might help here and a GOOD motor controller will help.

Flow Switches: Yep you need them as if you have a required flow rate, then you need to automatically start another pump if the flow rate drops or a pump trips out. You need to know if each duty pump is running or you are producing your required flow rate. A simple controller will monitor this situation and switch in another pump if required

Vibration Detection: Do not operate without these..... if you do and your installation is not alined correctly there is a real good change that you will destroy it and the pumps. Furthermore if something mechanically happens to the pumps/motor, then the vibration switches will detect it and trip out the damaged pump. Better safe than sorry. I have further info on vib switches if you require. The acid test is when your pumps are running you can stand a coin on the pump or pipework.. it should NOT fall over.

Pressure Transmitters: If you have VFD/VSD then providing you have the PT is set up correctly to your discharge pressure, then your flow rate will be constant PER PUMP. You cannot have ONE PT controlling ALL your VFD's. The beauty of having a PT connected to a VFD is that as the pump wears it's efficiency decrease (discharge pressure drops) and the VFD will speed up to correct the losses, a good way of telling when you need to replace a pump, that and a motor amp chart. NOTE OF CAUTION: ensure that the max Hz output from your VFD does not make the pump exceed the OR of the pump. With VFD's you can set the max Hz

SCADA..if you want 100% automatic or you just need to monitor the system, to monitor would be the easier solution, having it control automatically would be complexed, however SCADA systems I've worked with give you monitoring AND remote control of each pump and valve

I suggest you work with your designer as I suspect you are now trying to second guess him, mainly because the system he has suggested might be expensive.. would I be right?

If you want a cheaper system you will have to get your operators to work harder, spend more time with the pumps, monitoring flow rates, duty cycles and pump efficiency, spend more time open and closing valves, maintenance staff spending more time checking the motors.... and the HUGE possibility of operators NOT getting something right, which will cost you in the long term.

__________________
The square root of nothing is what you make it!
Register to Reply Good Answer (Score 2)
Guru

Join Date: May 2007
Location: Ohio. USA
Posts: 578
Good Answers: 30
#3

Re: VFD Pump Control

05/18/2010 9:58 AM

The sophistication of the controls and fault sensing depends on: the cost/impact of break downs, the ability of the system to be operated and repaired by its users, available capital funds, can the system operate properly with less sophisticated controls, labor costs, etc.

Simple systems that can be tended by an operator and have low negative impact if it is temporarily shut down certainly have there place.

Automated and backed up systems have their place also where costs and impacts are high such as power generation.

The first step to system concept are defining and understanding the real needs and real constraints.

__________________
Everything I know about opera I learned from Bugs Bunny
Register to Reply