Thermocouple & Rtd

05/17/2010 11:52 PM

What is the name "duplex" in thermocouple and rtd mean? Is there any specific conditions to use these duplex type of thermocouples and rtd's? Please help me with some examples?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United States - Member - New Member Engineering Fields - Control Engineering - New Member

Join Date: Mar 2006
Location: Washington USA
Posts: 566
Good Answers: 53
#1

Re: thermocouple & rtd

05/18/2010 12:39 AM

It simply means that two of the same device type occupy the same housing. The most common use is to have one connected to a temperature controller, or indicator and the other connected to an overtemp safety shutdown device. But they can also be used for comparison to tell when one is beginning to go bad, or to have a spare in place for the purpose of a quick changeout on the fly.

Register to Reply
Active Contributor

Join Date: May 2010
Posts: 14
#2
In reply to #1

Re: thermocouple & rtd

05/18/2010 1:00 AM

is there any specific conditions in which this duplex type to be choosed?

Register to Reply
Commentator

Join Date: Mar 2009
Posts: 61
Good Answers: 3
#3

Re: thermocouple & rtd

05/18/2010 1:37 AM

Typically a duplex temperature element is utilized where the temperature measurement is to be used by two different systems; for instance one TE will be wired to the plant DCS (via temperature transmitter or directly to temperature input modules) for indication and/or control and the other TE is wired to the plant SIS (via transmitter) for ESD and safety interlock functions.

Also I have seen duplex TEs utilized for redundancy i.e. to satisfy application SIL requirements. Each TE is wired out to separate transmitters each reporting independently to the monitoring and control system. A side note however; I'm not convinced that this is acceptable, to truly satisfy a SIL 2 requirement I believe that two completely separate installations are required.

Duplex TEs are also not much more expensive than simplex TEs so for new projects they are selected because there is a readily available spare in the event of failure of one TE.

Register to Reply
Guru
Engineering Fields - Instrumentation Engineering - EE from the the Wilds of Pa.

Join Date: Feb 2006
Location: middle of nowhere, Pennsylvania
Posts: 2603
Good Answers: 63
#4

Re: thermocouple & rtd

05/18/2010 8:10 AM

Right now I and another engineer are drawing up designs for a control panel for a pharmaceutical tank that has a duplex RTD in a well on the tank bottom. As Ace Boeringa has noted, one often goes to a local indicator and one goes remote. In this case, one is connected to a local recorder mounted in a panel on the portable tank, and one goes to a transmitter which utimately connects to the plant DCS via an ethernet jack in the panel wall.

This is not real common, and is usually a customer driven option. In 22 years I have seen this applied to pharmaceutical equipment we build maybe a dozen times. It is more common to have a single RTD and use that signal for both the local readout and the plant system.

__________________
Remember when reading my post: (-1)^½ m (2)^½
Register to Reply
Guru

Join Date: Jan 2010
Posts: 2446
Good Answers: 60
#5

Re: thermocouple & rtd

05/18/2010 4:51 PM
Register to Reply
Active Contributor

Join Date: May 2010
Posts: 14
#6

Re: thermocouple & rtd

05/21/2010 4:04 AM

thank u very much for ur valuable comments

Register to Reply
Participant

Join Date: May 2010
Posts: 1
#7

Re: thermocouple & rtd

05/25/2010 11:38 PM

Hi, I am a new member of forum. Would a newcomer be warmly welcome here? Good day you guys!!!

Register to Reply Score 1 for Off Topic
Register to Reply 7 comments
Copy to Clipboard

Users who posted comments:

Ace Boeringa (1); dabdool (1); larryp7639 (1); peterg7lyq (1); Phys (1); saravanamurthy (2)

Previous in Forum: VFD Pump Control   Next in Forum: Z Configuration

Advertisement