what is the implication of fault current on lt busbar
Re: busbar s.c. rating
05/22/2010 4:56 AM
busbar could overheat and melt.
Charlie don't surf.
05/22/2010 10:44 AM
Also, large currents create magnetic forces that can bend the bus bars if they are not properly braced.
Good Answers: 170
05/23/2010 7:42 AM
Fault current has two-fold effect on busbars:
i) Thermal stresses - proportional to I2Rt - which would melt the bus bars.
ii) Electrodynamic stresses - proportional to i2 - which would deform the bus bars
Good Answers: 244
05/23/2010 10:43 AM
For detail of the mechanical stress that the bus experiences due to fault current, see this thread:
http://cr4.globalspec.com/comment/553378
-MS
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)