Level Control Valve Malfunction on Offshore Platform

05/23/2010 4:50 AM

Hello everybody:

I work at offshore platform and last three days,we got plant shutdown due to low level at production separator.

Investigation found Level control valve malfunction, postioner was full of water and oil

I have no new one and order takes time , and this very important valve, so I opened the postioner and cleaned all the parts inside.

The problem I faced that this positioner (Masoneilan SV II) can not be introduced by HATR Commentator the menu I have looks like Transmitter menu Hart screen.

So I used the laptop to calibrate and Auto-tune the valve.

Can anybody till me why positioner can not be checked by the HART.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
2
Power-User

Join Date: May 2010
Location: Cambridge, MA
Posts: 390
Good Answers: 82
#1

Re: Instrument valve postioner SV II

05/23/2010 5:57 AM

Oh dear. I don't know about these valves, but I have had plenty of experience with salt water and electronics. The fact that your valve malfunctioned from the water exposure could mean that its electronics was exposed. Can you disassemble it enough to inspect the circuit board and connectors? Hopefully it's a coated board, but given the failure, perhaps not.

A fresh-water rinse, with immediate aggressive drying may help. But be careful, we don't want the drying temp to get over 70C and perhaps melt some plastic someplace. A hot-air gun is useful. As far as connectors go, sometimes reseating them after cleaning with silicon grease can help. I know that sounds scary, silicon grease? But it displaces the salt-ion moisture and then upon closure the connector contacts should wipe their way to clean metal despite the grease. It's worked for me in mid-ocean. Desperate times can call for desperate measures.

__________________
Thanks, Win
Register to Reply Good Answer (Score 2)
Power-User

Join Date: Oct 2007
Location: Oregon, USA
Posts: 126
Good Answers: 7
#2
In reply to #1

Re: Instrument valve postioner SV II

05/23/2010 11:28 PM

Perhaps if you had a hair dryer, you could use that to dry. Does the CV have a bypass with isolation HV's? If so you should take some pressure off the CV while fixing and run the HV's at about 50% open, but have a man at the station at all times with comm to the control room, making the minor adjustments.

Call the supplier and have them Fed-ex the necessary parts or a new controller.

What really concerns me about offshore activities is the possibility of ground movement anywhere in the world, at any time during earthquakes, psunamies (sp) and the like. Due to operating pressures it is impossible with todays technologies to make junctions flexible to handle all the possible movements. They say it would be cost prohibitive to over design for these situations. Guess what? there are designs out there for fail-safe methods. Ask a process engineer why they don't use them? Then get the answer from the beancounters and Harvy MBA graduates discussing bottom line management. Every plant and industry has one of them.

__________________
Thomas J. Coyne, Jr., President, T.C.Inc., (an international project development/consulting firm).
Register to Reply
Power-User

Join Date: Jun 2009
Location: New Zealand
Posts: 403
Good Answers: 5
#3

Re: Level Control Valve Malfunction on Offshore Platform

05/24/2010 5:23 AM

I do hope that this offshore platform is not an oil rig or any installation that requires Cat 4 installation. If it is a Cat 4 installation, for the safety of the plant and people order a replacment. The problem is if this is the case that after servicing the unit you can not guarantee that the instrumient is still Cat 4 and nor will the manufacturer.

If this is not the case, then rinse the unit in fresh water, allow it to drip dry for a short period of time, then put it in a small enclosure with a de-humidifer for at least 24 hours.

This will let the dehumidifer do the work for you and ensure that the moisture is removed.

But I suppose that by this time your platform has received another delivery.

I am not familar with the term HATR, please explain.

Best Regards

Joe

Register to Reply
Associate

Join Date: Jan 2010
Location: USA
Posts: 27
#4

Re: Level Control Valve Malfunction on Offshore Platform

05/24/2010 6:18 AM

What is being seen on laptop? Is this what you are using to stroke valve and calibrate. Di you have a 275 (with upgrade), 375 or 475 to stroke valve? What is the exact model for the Masoneilan SVI II? Is this remote mounted? Do you have the stainless steel version? If you don't have the stainless version this maybe something to look at. If you have time answer see if you can disclose a little more and I will try and help. I work on the SVI I and II daily.

__________________
always find time to do it right the first time or.............................
Register to Reply
3
Participant

Join Date: May 2010
Posts: 1
Good Answers: 1
#5

Re: Level Control Valve Malfunction on Offshore Platform

05/24/2010 7:39 AM

First: If the positioner is contaminated with water and oil, your instrument air is crappy. At the very first opportunity, put coalescing filters on everything that consumes air. You need a refrigerant dryer in your air system, just after the storage tank.

It's not salt water in the unit, it's fresh water condensed from the atmosphere. When you compress air, it compresses the humidity too, and the relative humidity becomes greater than 100%. That's why you get gallons of water when you drain the receiver, which should be done either daily or (better) automatically.

There is a chance that you have rainwater coming down the conduit. In your environment that would likely have some salt in it, from spray on the platform. It can only get in if the conduit entry is not sealed. If that's the case you are violating the explosionproof rating of the housing. Masoneilan usually puts in a sealed conduit plug with a pigtail for external wiring connection. Your installation guys may have thrown that away.

Blow off the circuit board with (dry) compressed air. If there are any tracks of corrosion clean them with a Q-tip and rubbing alcohol. The rubbing alcohol dries quickly and is not conductive nor corrosive. Inspect the pcb connectors and clean them gently but as thoroughly as possible. They should be gold-plated to resist corrosion, but the gold is very thin and you can scrub it off. A miraculous product called CorrosionX should be sprayed on the connectors to prevent further corrosion. Available at marine supply houses everywhere.

Remove the spool valve and clean it with long Q-tip and alcohol. It should have no oil or grit in it. The spool should move freely and show no scratches on its surface.

Get used to doing this. If the air is bad as I think it is, every pneumatic instrument on the platform is next.

Register to Reply Good Answer (Score 3)
Anonymous Poster
#6

Re: Level Control Valve Malfunction on Offshore Platform

06/03/2010 9:26 PM

When you connect HART communicator, if the device is displayed as generic HART device then that means you do not have DD loaded. When you connect a device to communicator it should display that device type instead of generic HART device.

In this case it should display as SVI II.

Register to Reply
Register to Reply 6 comments