Earth Fault

06/03/2010 8:33 PM

If a line to ground fault occurs the earth from substation and faulty area is shorted they say. So a large current flows and circuit breaker isolate the circuit.my question is does the current really flows from faulty portion to earth in substation. If yes, how much distance current can flow? What happens if substation is not earthed? I studied earth is a sink and it absorbs.

Register to Reply
Pathfinder Tags: fault ground
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Active Contributor

Join Date: May 2010
Posts: 10
#1

Re: Earth Fault

06/03/2010 9:41 PM

yes, the fault current will flow. But fault is random, the type , size are random. Substation mostly earthed with grid method if it is not ground, i think it will be dangerous. Let say, the substation is totally not earthed, my opinion is there will be arching. cmiiw

Register to Reply
Power-User
India - Member - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Apr 2010
Location: Asia/India
Posts: 365
Good Answers: 1
#2
In reply to #1

Re: Earth Fault

06/03/2010 9:49 PM

Dont confuse me saying random,arching blah blah. Tell me technically with explaination.

Register to Reply Score 2 for Off Topic
Anonymous Poster
#4
In reply to #1

Re: Earth Fault

06/03/2010 10:28 PM

good try, but you dont know...read your third sentence again.

Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#3

Re: Earth Fault

06/03/2010 10:10 PM

There is confusion when you use the term earth. Are you referring to earth(dirt) or are your referring the the neutral of the system. An earth(dirt) fault has a high resistance and current flow is a low value. A Phase to neutral(sometimes called ground) fault will have a low impedance and the current flow is a high value. Regarding distance, the fault will flow back to the source. Earth(dirt) is not a "sink hole" and does not absorb the fault current.

Register to Reply Score 1 for Good Answer
Anonymous Poster
#5

Re: Earth Fault

06/05/2010 5:10 AM

The amount of current will depend upon the 'earthing resistance' and the potential difference (i.e. the voltage).

The current really flows to the ground and it can actually be measured by an ammeter (or a tong ammeter) if an experiment is performed.

The horizontal distance is theoretically 'zero' because the current actually flows to the core of the earth. However, this can happen only if one of the terminals of generation of the substation / source is earthed (or, in case of multi phase generation, the neutral point obtained by the star connection of the phases is earthed).

In case the entire system including generation is totally isolated (i.e. and operating in vacuum or humidity air - ensuring 'zero' earthing of the substation at all the points / terminals), there would be no current flowing to the earth at all.

Ashok Shukla

CR4 Admin - phone number removed

From the Site FAQ: Do not post phone numbers or email addresses. The CR4 Admin will delete all phone numbers posted in threads or comments, and we strongly urge you not to put up email addresses.

Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#6

Re: Earth Fault

06/05/2010 5:27 AM

Earth and neutral are bonded at the substation.

Any fault current via earth will be via the neutral and if the current exceeds the breaker trip value (but only then!) the breaker will trip.

In modern installations, it is usual to also have an ELCB or similar that will trip if and when a few milliamps of fault current flows via the earth wire to the neutral at the substation. This is to stop people being electrocuted by a partial fault where the current is not enough to trip the main breaker.....

In some countries, the breaker combines both sensing I believe.

In some countries the earth is via the ground.....this cannot be as safe......but I have no personal knowledge of such systems......I can only speak about what happens in Europe.

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Active Contributor

Join Date: Feb 2010
Location: Australia
Posts: 13
Good Answers: 1
#7

Re: Earth Fault

06/06/2010 7:52 PM

The answer is YES.

Your follow up question is not straight forward. One my function at work is to calculated the current that flows through earth and back to the grid. The following are what I consider:

1. Soil Structure - Not only is the soil resistivity important, but the different layers must be considered. You have to determine the reflective coeifficents between layers to work out the earth potential rise.

2. The tower footing resistance - this can be measured on site or calculated.

3. The line impedance must be calculated under single phase fault. Note that the earth wire or neutral with have considerable influence due to mutal coupling.

4. Substation grid impedance

5. Network source impedance

I use a software tool, CDEGS see www.sestech.com , to model the substation, soil and lines. Your model has to be as close as practically possible to the real world.

Third question - substation is always earthed, just in different ways to limit the fault current. Substation is never floating.

Your last question, the earth is a lumped impedance in a ladder network. The current always flows back to the source impedance.

I cannot do justice to this topic in this forum, however I hope this helps.

Register to Reply
Member

Join Date: Jan 2010
Location: JHARKAHND INDIA
Posts: 5
#8

Re: Earth Fault

06/07/2010 11:23 AM

In case of earth fault the earth acts as conductor. The faulty cable / conductor gets connected through the earth to the substation originating point. The earth acts as a retun conductor and depending on the quality of earthing ( earth resistance of earthing electrode) the current flows. The distance can be lage and the quantum of current depends hogood is the soil for conducting. If the terrian is rockey the current will be less as the earth conductivity shall be less. In rainy season the conductivity is better as the conductivity improves.

The distance can be large as depending on the distance the resistance increases and the current accordingly reduces on the return path

Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#9
In reply to #8

Re: Earth Fault

06/07/2010 4:10 PM

That might be true for India, its certainly not true in Europe....

The only places I have heard of with earth return are some 1 wire systems in the Australian outback, where earth is the return of all current as only a single wire is run to the farm or whatever. I was told that some parts of S.Africa use a similar method....

Perhaps an "Outback Aussie" can chime in here and let us know exactly what is done there.

If you use a 3 wire system (Ground, neutral and phase) then having the earth return via the planet earth is going to be exceedingly dangerous......

Here in Europe the earth wire is bonded to the planet at each house (and to the copper water piping etc), but we do not rely on that providing enough of a good path, there is also a good bit of copper taking the earth return back to the substation....

As far as I remember, the only reason that the house earth cable is also bonded to the planet is to stop unbalanced phases causing a rise in the neutral/earth connection relative to the planet.......but I stand corrected if a knowledgeable person can show me differently......its been a few years.

Many people with 3 wire systems "believe" wrongly that the ground wire is conducting via the planet because of the name of the wire......

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
2
Active Contributor

Join Date: Feb 2010
Location: Australia
Posts: 13
Good Answers: 1
#10
In reply to #9

Re: Earth Fault

06/07/2010 6:45 PM

Hi Andy,

I'm a South African working in Australia - Lines Engineer. The 1 wire system you talk about is called the SWER (Single wire earth return) invented in New Zealand. Under normal operation the return path is through the earth. You right we have a lot of it in South Africa and Australia. The rural environment makes it feasible.

I agree with your statement for domestic electrification under normal operating conditions. In this case, the fault current is low to cause any concern. The copper path back to the substation is the logical path for the fault current (some leakage with occur). For transmission systems, with a fault current of say 40kA and a star 3 wire system, a single phase fault will cause current to return via the earth AND the earth wire / netural / ground wire / sky wire call it what you may. This must be true in europe as well.

If you step back in our understanding of power transmission, you would realise that the transmission line and ground is merely a wave guide for the electric and magnetic fields. All metal object like pipelines and fences influenced by the fields would have some leakage currents. However, this is a topic for another discussion.

Enjoy South Africa 2010

Register to Reply Good Answer (Score 2)
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#11
In reply to #10

Re: Earth Fault

06/08/2010 2:43 AM

Great reply, I will give you a GA for bringing me up to speed on single wire transmission again, I sort of knew it about 40 years ago, but was totally unsure till your Post arrived!!!!

Many thanks.

GA.

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Register to Reply 11 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Andy Germany (3); Anonymous Poster (2); hithuanand (1); Indhs (2); meditronhari (1); turonggo (1); wareagle (1)

Previous in Forum: Fuse Question   Next in Forum: lightining

Advertisement