Star Delta Starter Contactor Coil 440V Connected in A1

06/06/2010 1:18 PM

in the star delta stater the contractor coil havining 440v [ A1 & A2] it is connected in two phase[i,e R phase ans B phase] in that sitution it is corret connection or not plz tell me procedure

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster
#1

Re: in the star delta stater the connecter coil havining 440v it is connected in A1

06/06/2010 1:24 PM

Mr Chari, this is the third time you are asking this, and there are plenty answers in the first one, please go and read. You should not post duplicate threads, and here you are posting triplicate???

Yes, it is ok to connect a 440V coil between R and B and also between Y and B or R and Y. These are line voltages and the contactor will work. Do you really get 440V? You are lucky.

Please improve your English. Many people are having fun at your expense.

Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Jun 2010
Posts: 14
#2
In reply to #1

Re: in the star delta stater the connecter coil havining 440v it is connected in A1

06/06/2010 1:28 PM

thanks for your sagetion i can improve my english knowldge

Register to Reply
Anonymous Poster
#3
In reply to #2

Re: in the star delta stater the connecter coil havining 440v it is connected in A1

06/06/2010 1:55 PM

I can free give you mine .tution for taking english emprroving, withot ani phees . pleese replay if my sagetion is goodh for knowldge.

Register to Reply Score 2 for Off Topic
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#4

Re: in the star delta stater the connecter coil havining 440v it is connected in A1

06/06/2010 7:51 PM

If the contactor coil is actually a 440v coil, the A1/A2 (or R/B) connection is correct. However, it is also possible to use a control transformer if the coil and circuitry are some other voltage, such as 120 or 24. This is often done for safety reasons, especially in wet environments.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Score 1 for Good Answer
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#5
In reply to #4

Re: in the star delta stater the connecter coil havining 440v it is connected in A1

06/06/2010 7:59 PM

GA, for giving a patient, sane and correct answer to a question.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply Off Topic (Score 4)
Anonymous Poster
#6
In reply to #5

Re: in the star delta stater the connecter coil havining 440v it is connected in A1

06/06/2010 10:21 PM

Did you read the answer properly. Are you clear from the question that voltage between R and B is 440 Volt.?...Until it is not said how can the connection will be OK theoritically.?...why did you give unnecessary GA?...Please dont be slave of Ameriiis...you are the only one giving free GAs to all Ameriis without analyzing the answer.

Register to Reply Off Topic (Score 6)
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#7
In reply to #6

Re: in the star delta stater the connecter coil havining 440v it is connected in A1

06/06/2010 10:35 PM

Only a fool would have a motor voltage with a step-up control transformer to a 440v coil. The OP's context is clear that this is a 440v system. By the way, no one likes anonymous cowards, no matter what country they are from.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Score 1 for Good Answer
Anonymous Poster
#9
In reply to #7

Re: in the star delta stater the connecter coil havining 440v it is connected in A1

06/07/2010 1:09 AM

Message from CR4Admin: Insults like these are not tolerated, even if we have to use a translator to understand them. Please see the FAQ regarding language use.

Register to Reply Score 1 for Off Topic
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#10
In reply to #9

Re: in the star delta stater the connecter coil havining 440v it is connected in A1

06/07/2010 2:24 AM

10-4, good buddy.

That was even more offensively stupid than your previous post.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Off Topic (Score 5)
Anonymous Poster
#11
In reply to #10

Re: in the star delta stater the connecter coil havining 440v it is connected in A1

06/07/2010 3:13 AM

Message from CR4Admin: Insults like these are not tolerated, even if we have to use a translator to see them. Please see the FAQ regarding language use.

Register to Reply Score 1 for Off Topic
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#12
In reply to #11

Re: in the star delta stater the connecter coil havining 440v it is connected in A1

06/07/2010 3:37 AM

No, you're not. I prefer that the admins do not pull your scurrilous posts, because I would rather bash the dickens out of you verbally myself. This is now your third anonymous and insulting post.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Off Topic (Score 5)
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#13
In reply to #12

Re: in the star delta stater the connecter coil havining 440v it is connected in A1

06/07/2010 3:58 AM

Hi Tornado...is that Russian or something ? Do you understand it ? Anyway, with your record, why do you let this bug you ? Life is too important to be taken seriously.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply Off Topic (Score 5)
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#16
In reply to #13

Re: in the star delta stater the connecter coil havining 440v it is connected in A1

06/07/2010 4:50 AM

I'm not sure that "bugs me" is quite the right concept. On one level, perhaps yes, but at another level it is a fun opportunity for wordplay, even if only about feeble Russian insults. However, this whole thread might crash and burn pretty soon.... We'll just have to see.

Some people may shy away from robust verbal exchanges, but I rather enjoy them.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Off Topic (Score 5)
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#18
In reply to #16

Re: in the star delta stater the connecter coil havining 440v it is connected in A1

06/07/2010 5:39 AM

okay, i will practice a bit too just in case .. let's see.. Pulp Fiction would be a nice place to start i guess...

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply Off Topic (Score 5)
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#19
In reply to #18

Re: in the star delta stater the connecter coil havining 440v it is connected in A1

06/07/2010 6:40 AM

That sounds like a pretty good assessment. Or maybe Plop Fiction.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Off Topic (Score 5)
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#8
In reply to #6

Re: in the star delta stater the connecter coil havining 440v it is connected in A1

06/06/2010 10:45 PM

i felt the answer was GA because :

  • it was technically correct
  • the author did not give in to the temptation of having fun at the OP, like others have.

Anyway, i think CR4 is a truly a forum of "Engineers sans frontiers" and we are all here to share knowledge and learn from each other. The mention of a member's country in the profile is of course as a matter of pride, but that should not come in the way of appreciating others. i also never look at the person to whom the GA is due. Only the answer, and the context.

Anyway, you are entitled to your opinion and anonymity...it is your privilege.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply Off Topic (Score 4)
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#14

Re: Star Delta Starter Contactor Coil 440V Connected in A1

06/07/2010 4:01 AM

For those who don't know Russian, our honorable guest's post 9 (in Google translation) leads to a lengthy and amusing anecdote about the rectal self-administration of carrots. Not for everyone's taste, I'm sure, but I thought it was a hoot! His further post 11 Google-translated to "I'm gonna get ya, sucka." I have reported these to the Admins, with the suggestion that I be allowed to bash this dolt myself.

I mention this so that you can understand the nature of my replies, which normally might seem untoward, but not in these circumstances.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Off Topic (Score 5)
Anonymous Poster
#15
In reply to #14

Re: Star Delta Starter Contactor Coil 440V Connected in A1

06/07/2010 4:45 AM

Wow, give that 'fundament' a jackfruit in the place of the carrot...

Register to Reply Off Topic (Score 5)
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#17
In reply to #15

Re: Star Delta Starter Contactor Coil 440V Connected in A1

06/07/2010 5:19 AM

Yeah, that looks about the right size! A watermelon would be overkill.

That guy is incontinent enough already.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Off Topic (Score 5)
Anonymous Poster
#20
In reply to #17

Re: Star Delta Starter Contactor Coil 440V Connected in A1

06/07/2010 2:00 PM

Kvshasidar,

Don't try to save your fellow Indian by putting the blame on Russians. All these stupid posts are made by Indians with poor english . You can make out the anonymous Indians by their english (all caps, bad grammar, etc ). I have good experice handling Indians.

I don't like to see the posts these days some stupid Indians are freaking out!

Don't give offtopic if you have some sense

Register to Reply Off Topic (Score 5)
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#21
In reply to #20

Re: Star Delta Starter Contactor Coil 440V Connected in A1

06/07/2010 4:47 PM

If you wish to speak with kvsridhar, why did you reply to post 17? He didn't write that one.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#22
In reply to #20

Re: Star Delta Starter Contactor Coil 440V Connected in A1

06/07/2010 9:21 PM

Dear Guestsky(to distinguish you from the other million guests),

"shasidar" is also a good Indian name, for Lord Shiva, the God of destruction (of evil). (Do not insult him, he is short tempered )

i tried to see where i have defended Indians by blaming Russians, you can help me here.

Yes, English being a foreign language, many Indians are not good at it, but our electricity is the same as everywhere, and their doubts are quite often genuine. Some are pretty stupid i grant you, but not all. As CR4 members, it is our duty to help anyone we can in our field of expertise.

You don't like to see such posts? There is no compulsion to see them, is there? You can relax with your Vodka rather than read them and get incensed.

i actually feel sorry for you...so much anger...for what purpose? The most useless emotion in man... please use your energy for some pleasurable pursuits.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply Off Topic (Score 5)
Register to Reply 22 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (7); jvsnlchari (1); kvsridhar (5); Tornado (9)

Previous in Forum: Star Delta Contactor   Next in Forum: Convert 50 Hz Clothes Dryer to 60 Hz

Advertisement