Lighting Design

06/11/2010 8:10 AM

The question is When i use an RCD for an industrial lighting Distribution board at its incomer which is 3 phase 4 wire system. i am goin to use only one phase for each of the lighting devices and distribute the 3 phases accrding to my needs. when there is a load imbanlance in t 3 phases wont the Sum of t currents in the 3 phases change and cause my RCD to trip at the incomer everytime? then in that case can i correct the prob using ELCB??

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#1

Re: Lighting Design

06/11/2010 9:08 AM

The three phases AND the neutral MUST go through the ELCB. The vector sum of all three phase currents + neutral is zero. When there is any earth fault/leakage, that current will flow outside the summation CT in the ELCB, so it will trip. As long as there is no current flowing to earth, it will not trip. You can relax.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#2
In reply to #1

Re: Lighting Design

06/11/2010 9:16 AM

Sorry for the incomplete answer.. RCD and ELCB operate on the same principle, that they sum up vectorially all healthy currents - the three phase currents and the unbalanced part through the neutral. Any aberration from this indicated an earth leakage, and it will trip.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply
Anonymous Poster
#3
In reply to #2

Re: Lighting Design

06/11/2010 1:17 PM

this is theory. not the answer for my question. well, you said RCD and ELCB works on same princople. Then what is the difference between them and why they called so??

Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#4
In reply to #3

Re: Lighting Design

06/11/2010 1:33 PM

Oh sorry ... i didn't know you wanted that. There are earlier threads in CR4 which touch on this..

Here is a link anyway .. http://en.wikipedia.org/wiki/Residual-current_device

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply
Anonymous Poster
#5

Re: Lighting Design

06/12/2010 4:11 AM

u jus cant use rcd at the incomer. it has to be connected in series with a mcb.....if u r talking abt rcbo then i take back my point.................now abt phase unbalance.......if phase unbalance s more thn 4% then it s really a bad thing.....so the circuit has to be opened........the rcd has setting of 30mA , 100mA, 300mA, 500mA and 100mA ......based on tht if there s unbalance in the phase currents around this range then certainly it will trip...and u should be happy for tht....also before rcd , your mcb will trip due to overcurrents as a result of unbalances......

Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#6
In reply to #5

Re: Lighting Design

06/12/2010 6:25 AM

Are you sure RCD/RCBO/ELCB will trip on unbalanced currents ?

My knowledge is that all four wires (RYB&N) pass through the core of the summation CT. The vector sum of all four currents, even with unbalance, is always zero. If an earth leakage happens (usually due to insulation failure) the vector sum of the 4 currents is no longer zero, and the power is cut off.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply
Participant

Join Date: Sep 2009
Location: HN, VN
Posts: 4
#7
In reply to #5

Re: Lighting Design

08/31/2010 2:37 AM

Im design electric for the building but I dont no arangement the emegency lingt in basement 1 and 2 of the building-21 floors. Do you hepl me?

Reply
Reply to Forum Thread 7 comments
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); ddung (1); kvsridhar (4)