Anonymous Poster
|
|
IS DG shall with stand 150% transient over loading for a duration of 15 sec?
i had the calculation for DG sizing
| Total Connected Load | TCL | : | 1486.75 | KW |
| Rating of Largest Motor | RLM | : | 426 | KW | ( chiller ) |
| Power Factor | PF | : | 0.8 |
| Demand Factor | DF | : | 0.8 |
| Efficiency of load | h | : | 0.9 |
| De-Rating factor for DG | DR | : | 0.9 |
|
I) STEADY STATE |
| Maximum Demand kVA | MD | = | TCL / PF / h * DF |
| MD | = | 1651.94 | KVA |
| Maximum Demand kVA | MD | = |
1651.94 |
KVA |
| Minimum capacity of DG required | = | MD/DR |
| = |
1835.49 |
KVA |
------ (1) |
|
II) TRANSIENT |
| Base Load in kW | BL | = | TCL-RLM |
| = | 1060.75 | KW |
| Base load in kVA | BMD | = | BL / PF / h * DF |
| = | 1178.61 | KVA |
| Rating of largest motor in kVA - |
| Steady state | RLMS | = | RLM / PF / h |
| = | 591.67 | KVA |
| Rating of largest motor in kVA - |
| When starting | RLMT | = | RLMS x 2.5 | (Soft starter) |
| = | 1479.17 | KVA |
|
| Total transient kVA | TMD | = | RLMT+BMD |
| = | 2657.78 | KVA |
| (The DG shall with stand 150% transient over loading for a duration of 15 sec.) |
| Minimum capacity of DG required | = | TMD/1.5/DR |
| = |
1968.724 |
------ (2) |
|
From (1) & (2), the requirement of DG set is 1968.724 KVA, hence provided 1 no. 2000 KVA
the calculation above is correct or not? if it is wrong please correct me |
|
|
Reply
|
|
|