Rural Power Line Without a Neutral Safety Issue

06/15/2010 12:17 PM

I have seen here in the Dominican Republic, in very remote areas, power lines with just the hot alone. This hot is probably around 7000VAC. When power is required for a house/houses a transformer is mounted. On the two long high voltage insulators forming the primary the power line is attached to one side and the other side is grounded at the bottom of the pole. This ground also goes to the center winding on the low voltage side of the transformer which leaves to the house as a "derived neutral" along with the 2 120V lines. Is this an acceptable practice? Isn't it very dangerous? It seems to me that if the ground should go open the neutral will have 7000Volts on it. This practice is done to save money on wire. All the return current must flow through the soil/earth, correct? I have heard of many cases where country folk are electrocuted and feel this is the reason.

Thanks for opinions

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#1

Re: Rural Power Line Without a Neutral Safety Issue

06/15/2010 1:58 PM

How does the 7000VAC get through the transformer to the secondary side to place 7000 volts on the secondary neutral? Unless you are talking about a failure of the transform as a short between primary and the secondary. Should be load devices to shut it down in that case. Each house should have the panel grounded which is bonded to the neutral. In the event of one of the connections to ground becomes an open there are many more in the system. Each house is connected.

With out more specific information on each case. It is difficult to make any conclusions as to the cause of these deaths.

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Register to Reply
Power-User

Join Date: May 2010
Posts: 132
Good Answers: 6
#2

Re: Rural Power Line Without a Neutral Safety Issue

06/15/2010 2:39 PM

The situation that you describe is common in the U.S.

Like you, I have wondered about this and guessed that the answer is the one that was previously given: there are many ground points for the system.

However in the case that you describe - where there is but one ground point - suppose the ground wire - typically directed to a rod at the base of the pole - were severed.

It would seem that the primary voltage would appear across the gap and, since the center tap on the secondary is bonded to the same ground point, that it too would be at high voltage.

I'm confident that someone who knows this stuff will explain.

Register to Reply
Power-User

Join Date: May 2010
Location: longo tempo dos macaco do pilas. Felizment.
Posts: 251
#3

Re: Rural Power Line Without a Neutral Safety Issue

06/15/2010 2:50 PM

You speak of single phase I think.

7000 V a.c. this seems very high for even it peak voltage and not RMS.

A single phase is only one "hot" wire until a device is connected then the a.c. can flow.

The Earth is not part of the circuit and can be even connected to the neutral as in some marine applications.

All electricity is dangerous above a certain voltage.

25 v a.c. p-p or 48v d.c. I think danger starts to arrive.

I think the problem might be bad installation.

If you measure the resistance between the pole knocked into the ground and the generating station I would think it is a large number of ohm's.

Do you mean 700 V a.c. p-p ?

__________________
I am a deeply religious nonbeliever - this is a somewhat new kind of religion. Albert Einstein
Register to Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#4

Re: Rural Power Line Without a Neutral Safety Issue

06/15/2010 3:27 PM

Baffled has it pretty much on the money. However, I think you would find that in the US if a single phase is run, there is also a neutral, not just the HV phase. In less developed areas, as OP stated, it is done to save on wire costs by not running a neutral along with the phase. Along with that often also goes a lower value placed on the safety of the public.

7000V is not far from reality. A common distribution voltage is 13.2kV (L-L), which would be 7620V L-G. That would be quite dangerous if there were a break in the neutral grounding wire, with that voltage across the break.

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply
Power-User

Join Date: May 2010
Posts: 132
Good Answers: 6
#6
In reply to #4

Re: Rural Power Line Without a Neutral Safety Issue

06/16/2010 12:42 AM

I may have exaggerated in using the word "common" based on an inadequate sample size, but I can attest that the "SWGR" (to translate the acronym from raw Strine) system is highly popular in Fresno California as well as in Jacksonville Florida. I assumed (without any evidence) that it would be popular in places in-between.

Register to Reply
Guru
Australia - Member - New Member

Join Date: Feb 2008
Location: Australia
Posts: 2181
Good Answers: 255
#5

Re: Rural Power Line Without a Neutral Safety Issue

06/15/2010 6:17 PM

Large areas of central Australia run "SWER" (Single Wire Earth Rethurn) systems, but from my understanding, the earthing at transformer and house box (and other points) ensures the neutral/earth relationship is maintained.

The difference here is that we don't centre tap to get 120V, everything is run as 240V.

Metering has overvoltage protection built in, so if there is a fault, it all shuts down.

In some cases I've seen, it averaged 20km between houses on the lines.

__________________
Just an Engineer from the land down under.
Register to Reply Score 1 for Good Answer
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#7
In reply to #5

Re: Rural Power Line Without a Neutral Safety Issue

06/16/2010 2:52 AM

Yours was by far the best and most accurate answer up to now, therefore a GA from me!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Power-User

Join Date: Jan 2007
Location: Johannesburg, South Africa
Posts: 230
Good Answers: 16
#8
In reply to #5

Re: Rural Power Line Without a Neutral Safety Issue

06/16/2010 3:24 AM

South Africa also uses this in very remote areas. I suppose a search for SWER (single wire earth return) will find something. Or try Eskom's site. It is done for economic reasons, but not at the cost of safety, as pointed out in the Australia example. It allows for grid electrification where it is otherwise not economically justified. And now a farmer can actually have a dairy that is on an even cost base with other farmers, for example. Or you can electrify tiny rural villages. And before you ask, photovoltaic systems here are prone to theft (both the panels & the batteries).

The other rumour I heard (not verified yet) is that they sometimes use steel as the conductor, after all calculations are done. It reduces the massive cable theft issues we have here. The loads probably have to be very low for this, otherwise the cable size will require such strong poles that the economic benefit is lost. Usually ACSR is used successfully.

Register to Reply
Guru

Join Date: Feb 2006
Posts: 1758
Good Answers: 6
#9

Re: Rural Power Line Without a Neutral Safety Issue

06/16/2010 5:10 AM

All Hi-Voltage lines [11KV, 33KV, 66KV, 132KV the Transmission Transformers] run only 3wires [hot]

Nutral is produced in 11KV/220V the Distribution Transformers.

I don't know the distribution transformers' voltage in 110V supplycountries distibtion transformers.

Register to Reply
Power-User

Join Date: Apr 2010
Location: Dominican Republic
Posts: 189
Good Answers: 6
#10

Re: Rural Power Line Without a Neutral Safety Issue

06/16/2010 8:16 AM

OK, Thank you all for your comments. It's interesting to note that this single wire high voltage line is found in many parts of the world. The cases of deaths were related to copper thieves who stole the solid #2AWG ground wire running down the pole to the soil. These "copper bandidos" do this during power failures which are very common here. Unfortunately when the power returns the 7600VAC now appears all over the house on chassis's and ground points electrocuting the user. I was called out to a town near the haitian border where we installed a solar system but with grid power as back up. The grid powered charger had "blown up". Being cautious (I've lived here 42 years and seen some wierd stuff) I use a small, pencil sized, AC voltage sensor. When I got to the site before touching anything I pulled out my sensor and it was beeping when I was 5 feet away from the blown charger. I then went to the power pole and got the same beeping. The ground was gone/stolen. I got a villager to pull the high voltage fuse using a 20' PVC pipe and the trouble cleared. We then regrounded the pole and all was well. I guess I would have been electrocuted if I hadn't done that beeper test. Thanks to all.

Register to Reply
2
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#11

Re: Rural Power Line Without a Neutral Safety Issue

06/16/2010 9:12 AM

A couple of things come to mind...

Earth return systems are in use in many parts of the world. We have them in many locations in the northern regions of Canada and in many rural areas in the central provinces. If done correctly, they are as safe as any other distribution methodology.

The comment about all high voltages being a three wire distribution system, as is often the case, is only true in certain regions of the world. What is considered a high voltage in one location is not in another. Here in Canada, any system over 750 volts potential, phase to phase or phase to neutral, is considered a "high voltage" one.

The standard distribution system for residential and small commercial/industrial consumer services in Canada and many parts of North America is based on a 4160 Y 4 wire system. Phase to neutral gives you 2400 volts. This allows for a lower class of insulation for small pole mounted distribution transformers. So... this is a 4 wire "high voltage" system.

In the distribution systems mentioned above, it has become the utility standard to tie the neutrals of the primary and secondary systems together. There are many reasons to do this, principle amongst them is co-ordination of the protection system.

In the system described by the OP, there is no primary neutral. If the second high voltage terminal on this transformer was connected to the same pole ground that the secondary neutral was connected to and if the panel at the house was also grounded, and if somehow the ground at the pole was somehow broken while the ground at the house remained intact and electrically connected to the high voltage terminal on the transformer, the house panel ground conductor would see the primary current flow at the potential of the SWER system.

Is this dangerous? Only if someone were to come between a grounded object and the primary wire of the SWER system or in between a grounded object and the wire handling return current from the transformer back to the ground electrode at the panel.

Step and touch voltages could also be of a concern here as any impedance differences in the grounding system could result in current flow from a grounded object to a local ground point that has an impedance difference between them.

For these reasons... in this country, on a SWER system, the secondary neutral is never connected to the same grounding conductor as the SWER primary. In this way... a grounded object in the residence will never see the higher potential and in fact forms a separate equi-potential ground plane from the of the primary system.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply Good Answer (Score 2)
Guru

Join Date: Feb 2006
Posts: 1758
Good Answers: 6
#12
In reply to #11

Re: Rural Power Line Without a Neutral Safety Issue

06/16/2010 12:21 PM

Regards.

Earth return systems were in use for Manual telegraphy NOT for POWER DISTRIBUTION.

Can you imagine the danger of Voltage distributed from the Service-Earth & your house????

Specially in rainy days when ground is fairly conductive.

Voltage between both feet while walking.

I have seen this scene on a dog & his handler where Earth was being used as the return path.

And how earthcan replace a conductor.

Astonishing !!!!!

Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#13
In reply to #12

Re: Rural Power Line Without a Neutral Safety Issue

06/16/2010 1:33 PM
__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Guru

Join Date: Feb 2006
Posts: 1758
Good Answers: 6
#15
In reply to #13

Re: Rural Power Line Without a Neutral Safety Issue

06/17/2010 9:08 AM

Please read out of reference :

Safety

SWER violates common wisdom about electrical safety, because it lacks a traditional metallic return to a neutral shared by the generator. SWER's safety is instead assured because transformers isolate the ground from both the generator and user. However, certain groups claim that stray voltages from SWER can injure livestock.[citation needed]

Not only livestock but Men there [Haajee]

Bare-wire or ground-return telecommunications can be compromised by the ground-return current if the grounding area is closer than 100 m or sinks more than 10 A of current. Modern radio, optic fibre channels and cell phone systems are unaffected.

Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#16
In reply to #15

Re: Rural Power Line Without a Neutral Safety Issue

06/17/2010 9:19 AM

What is your point? All installation methods offer some risk if not installed properly. This is just another system that works safely, properly and efficiently if installed as designed.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply Score 1 for Good Answer
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#18
In reply to #16

Re: Rural Power Line Without a Neutral Safety Issue

06/17/2010 9:36 AM

Had to give you a GA for such a fundamental and correct statement.

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#17
In reply to #15

Re: Rural Power Line Without a Neutral Safety Issue

06/17/2010 9:35 AM

Livestock is affected by even the tiniest stray currents, very true.

But provided the earth conductor is buried to the correct depth, I do not believe that people will be injured or even notice it.

I am sure that what you say could be true on a badly installed installation. Like using uninsulated (or should I say, not an insulation for below ground usage!) cable to connect to the ground plane for example......as many electricians would believe that insulation was not a requirement in the ground wire!!!! Which of course it is.....

If you look at the ground connection as a resistor say 50 KM long, and the supply as being 5000 volts, then the voltage per km is 100 volts. Therefore the voltage per meter is around 0.1 volts. If you could span with your body even 2 meter, you might measure around 0.2 volts.....

As I said before, livestock may notice that, but humans???

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#14
In reply to #12

Re: Rural Power Line Without a Neutral Safety Issue

06/16/2010 3:32 PM

Sorry but this is already fact for over 70 years.

Due to the earth return being deeply buried, its simply not a problem.

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Register to Reply 18 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Andy Germany (4); Baffled (2); gideon (1); Haajee (3); JOHN H VAN ALLEN (1); Just an Engineer (1); North of 60 (3); ozzb (1); PeterT (1); portugalphilip (1)