Moisture in Instrument Air

06/16/2010 4:15 AM

Hi Guys

Have a good Day.

Last day I was having a job on pressure transmitter of instrument air, unexpectedly we found water inside the tubing, later on as discussed with colleagues this is a normal phenomenon in summer season. But I am still confused why in summer this happens

Is there someone who can explain this phenomenon?

Thanks

__________________
I.A.Khan
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United States - Member - Member Engineering Fields - Electrical Engineering - Electrical Construction

Join Date: Apr 2010
Location: Mid Western USA - The Corn Belt
Posts: 1439
Good Answers: 58
#1

Re: Moisture in Instrument Air

06/16/2010 8:44 AM

The cause is higher humidity in the atmosphere during summer.

Do you have a dryer on the outlet just after the compressor?

Do you have a dryer on the inlet of the instrument?

I have encountered this on occasion. Some instruments in the plant were dry while others (due to air pipe routing) were damp therefore we would add a small dryer at the instrument itself.

__________________
The first 5 days after a weekend are always the hardest................................
Register to Reply
Participant

Join Date: Nov 2012
Posts: 1
#7
In reply to #1

Re: Moisture in Instrument Air

11/29/2012 4:00 PM

Free water condenses any time you compress atmospheric air. That free water is normally removed using a coalescing filter with a liquid dump. If you cool the compressed (saturated) air, it will again condense more water. Sometimes a point-of-use coalescing filter is enough. Don't forget that just a tiny amount of free water will freeze hard at -.5 deg C. and shut down your process until you thaw it out.

In industrial plants, one normally will "dry" the air by refrigeration or a variety of desiccant drying techniques, depending upon your volume and adversity to water. Desiccant adsorbs water vapor from air, preventing condensation and freezing at much lower temperatures (such as -40 deg. C, and industry standard). These can be designed by a professional to meet your needs.

If you have a dryer and still see water downstream, either the dryer is malfunctioning, or the coalesing filter has flooded or failed, or your flow rate has greatly exceeded the filter/dryer design flow rate at some time.

These guys can help: www.instrumentair.com

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Moisture in Instrument Air

06/16/2010 9:14 AM

It usually indicates the air dryer isn't working. Beware of water in instrument air lines. It is a portent of doom for anything in pneumatically-operated equipment that water can corrode and an early indicator of impending mechanical failure, leading to process problems.

In high-end manufacturing facilities, typically -40degC dewpoint instrument air can be found, indicating its high dryness.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Nov 2008
Location: Port Glasgow, Free Republic of Scotland
Posts: 360
Good Answers: 30
#3

Re: Moisture in Instrument Air

06/17/2010 3:57 AM

This sounds very worrying - summer increases the water load in two ways.

Higher temperatures mean the Max Absolute Humidity (water carrying potential) increases

Depending on your location relative humidity increases.

These two effects increase the water load in atmospheric air significantly

I assume you compress and cool the air to a standard temperature irrespective of season which will have a constant humidity. This means that more water needs tbe removed in summer.

The fact that water is found in the system screams a warning your instrument air system is not working properly. I work in the oil/gas/chemical industry and air is dried as mentioned above to -40°C and the vendor has to guarantee performance under the worst humidity conditions to guarantee that there can never be water in the system.

Water in instrument air lines is a problem with corrosion; two phase flow potentially fast moving slugs that act like projectiles; just the weight of water on impulse lines and probably a whole load of other issues.

Do you have a drier on the system or is the air just compressed and cooled and any water knocked out in water trap or KO Vessel. It is worrying that the attitude seems to be oh that happens. Water while essential for life is dangerous in the wrong hands or situation

__________________
Free advice guaranteed or your money back
Register to Reply
Associate

Join Date: Sep 2007
Location: Ohio - 40 miles due West of Pgh International.
Posts: 48
Good Answers: 2
#4

Re: Moisture in Instrument Air

06/17/2010 7:33 AM

The explanations of why the moisture is there were spot-on. One thing I would like to add is that any instrument that relies on a throttling action to control a pressure will also be damaged by the corrosion that accompanies the moisture. Also, the small pieces of corroded material will not allow units such as pressure regulators to properly seat and this will result in the 'regulated' pressure slowly creeping towards the value of the supply pressure.

__________________
The wickedness of a people is great indeed, when noted sinners are men renowned among them.
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Feb 2010
Posts: 103
Good Answers: 2
#5

Re: Moisture in Instrument Air

06/17/2010 4:26 PM

The atmospheric moisture content tends to be higher during summer months. All pneumatic control and instrumentation systems should have a refrigerated drier device in the main air piping from the receiver. It's needed winter and summer. Lou Bindner

Register to Reply
2
Anonymous Poster
#6

Re: Moisture in Instrument Air

06/17/2010 8:38 PM

You state there is water in an instrument air pressure transmitter.If this is transmitting pressure from a gas(air) the transmitter and all tubing should be higher than the tap point on the line, with no pigtails in the transmitter line, then condensate cannot form in line.

If transmitting from a steam line, or liquid line the tap should be below the line, to keep the line full of condensate.

Look at the piping to the instrument, does it come straight down an elbow into the instruments?It should elbow up, over, and then down, or come off of a up leg of a tee on the supply line.The down leg should continue past the instrument supply tap, and be fitted with a trap or manual drain.

All of this is in addition to all of the previously mentioned info on air dryers, etc.

Register to Reply Good Answer (Score 2)
Register to Reply 7 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); KJK/USA (1); Lou Bindner (1); Processs (1); PWSlack (1); simonsd (1); Sparkman (1)

Previous in Forum: Sponge Iron Melting   Next in Forum: Transparent, Temperature Resistant Glass/Plastic
You might be interested in: Plastic Tubing, Rubber Tubing, Tubing

Advertisement