Anonymous Poster

K-rating selection

06/17/2010 12:59 AM

If a 2500KVA transformer connected to 2 nos 900kW compressor with VFD starters, what is the non-linear load we consider?..Since the two 900kW VFDs are there, do we have to consider the VFD load will create the harmonica?..What will be the K-rating of Transformer if we want select the K-rated transformer to withstand the heat due to the harmonics?....

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#1

Re: K-rating selection

06/17/2010 7:49 AM

Please visit this website: www.leonardo-energy.com

They have a wonderful guide on K-Rated Transformers.

Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#2
In reply to #1

Re: K-rating selection

06/17/2010 9:46 AM

Electricalexpert65:

For the curiosity, I was looking the website that you provided and browsed most of the links there but didn't find anything of K-factor selection guide. Is there any specific link you know that I can find it?

Guest:

Did you have chance to look into the immediate previous thread (http://cr4.globalspec.com/thread/55995/K-Rated-Transformer) and go through the links that I provided? Didn't you find your answer there?

Since you have 100% of the loads non-linear, you should select a transformer of K-factor 20 or a regular transformer with almost 30-35% de-rated. However, I would suggest you to consult the VFD vendor for the transformer selection recommendation.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#3
In reply to #2

Re: K-rating selection

06/18/2010 9:38 AM

I am sorry I mentioned the wrong link. It is Copper Development Association's Publication No. 144: "Harmonics, Transformers and K-Factors". The web link is: www.cda.org.uk . Happy browsing.

Reply