Transformers connection

06/18/2010 8:36 PM

Dear sir how do we connect two transformers of different ratings in parallel,what are the factors to be considered?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#1

Re: Transformers connection

06/18/2010 8:49 PM

I do not consider this a good idea. The primaries don't matter, but connecting the secondaries too should only be done with the right clocking. How big of a difference in voltages and currents you have, and what is the capacity of the transformers?

__________________
Plenty of room here
Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#2

Re: Transformers connection

06/18/2010 9:21 PM

You don't. Transfortmers should have the same KVA rating and the %Z should be the same or very close.

Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#3
In reply to #2

Re: Transformers connection

06/18/2010 9:44 PM
Reply Score 1 for Good Answer
Guru
Safety - ESD - New Member India - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: May 2007
Location: Pune , India
Posts: 875
Good Answers: 42
#5
In reply to #3

Re: Transformers connection

06/20/2010 10:17 AM

GA. You gave a good link on the topic. All important points are covered. Both transformers should be of same vector group same voltage ratio ( the voltage tapping to be checked for same secondary voltage)

Reply
Power-User

Join Date: Feb 2010
Posts: 187
Good Answers: 11
#4

Re: Transformers connection

06/19/2010 3:55 AM

Mmmm:

The necessary for parallel operation

Transformers of unequal kVA ratings will share a load practically ( but not exactly) in proportion to their ratings, providing that the voltage ratios are identical and the percentage impedances (at their own kVA rating) are identical, or very nearly so in these cases a total of than 90% of the sum of the two ratings is normally available.

It is recommended that transformers, the kVA ratings of which differ by more than 2:1, should not be operated permanently in parallel.


Other condition necessary for parallel operation

1- All paralled units must be supplied from the same network.
2- Secondary cabling from the transformers to the point of paralling have approximately equal length and characteristics.
3- Voltage difference between corresponding phase must not exceed 0.4%

Reply Score 1 for Good Answer
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#6

Re: Transformers connection

06/21/2010 8:11 AM

If the transformers have On-Load Tap Changers (OLTC), then paralleling is easily accomplished using Beckwith Electric Company's tap changer controls and paralleling equipment. See the following link for a number of good application notes from Beckwith that explains the most common method of paralleling control (circulating current method) and other options:

http://www.beckwithelectric.com/main/doccenter/doccenter-index.php#tapchanger

Beckwith's technical personnel are excellent to work with, and give great support of their products.

__________________
To get the right answers, first you need to ask the right questions.
Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#7

Re: Transformers connection

06/21/2010 10:43 AM

Hoping that other standard conditions of Parallel Operation - like Same Secondary Voltage Ratings, Same Vector Group, Percentage Impedance Difference within tolerable limits, Same Frequency, Same Phase Displacement, Same Phase Rotation, etc. are taken care - I would wish that the lowest capacity tarnsformer in the group is rated for not less than one third of the highset capacity transformer rating.

Reply
Reply to Forum Thread 7 comments

"Almost" Good Answers: