Testing Of Package Substation

06/21/2010 3:18 AM

Can anybody tell what all are the Factory Acceptance Tests done for a Package Substation?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#1

Re: Testing Of Package Substation

06/21/2010 4:14 AM

I know it's obvious to some, but have you first tried the supplier of the package substation? I would have thought that they would supply good documentation as part of the package, including factory acceptance testing. What about the company website?

Best to start here first as this is a very specialised application. For basic advice you need to go back to the applicable electrical standards and test to those guidelines (one piece of equipment at a time, then linked systems, then protection schemes, I/O, etc, then overall system).

Are you familiar with the applicable electrical standards the substation and site need to comply with?

__________________
jack of all trades
Register to Reply
Anonymous Poster
#2
In reply to #1

Re: Testing Of Package Substation

06/21/2010 7:37 AM

Thanks for your reply. This is just for information I am asking. I know that the vendor has to conduct the Factory Acceptance Test. But I dont know the applicable standards. Can you provide the testing methods?

Register to Reply
Power-User
Fans of Old Computers - ZX-81 - New Member

Join Date: Feb 2008
Location: Beirut Lebanon
Posts: 197
Good Answers: 8
#3
In reply to #2

Re: Testing Of Package Substation

06/21/2010 10:58 AM

Hello

As I see, you are in Qatar, in Qatar the applicable standard is the BS,which is now a part of EN standards very similar to IEC

There is no specific standards for the package substation but you can check the individual standard for each component.

main components are:

Power transformer ( IEC 60076)

Medium voltage parts ( switchgear, fuses, SF6, etc....) ( IEC 600298)

Low voltage switchgear and distribution ( IEC60439)

Greetings

__________________
dont say it, write it