GFCI 50Hz

06/21/2010 11:04 PM

can I use GFCI 250V, 50Hz to a power supply of 230V, 60Hz

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: GFCI 50Hz

06/21/2010 11:22 PM

This should work. You are not exceeding the voltage rating, and the current measuring principle is the same whether at 50 or 60 Hz.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#2

Re: GFCI 50Hz

06/21/2010 11:25 PM

Have you checked the data sheets and/or manual as the information should be in there?

Have you talked with the supplier?

Alternatively, please provide more detailed information on your application and what a GFCI is (and the model number and brand of the one in question).

__________________
jack of all trades
Register to Reply
Participant

Join Date: Sep 2007
Posts: 4
#3
In reply to #2

Re: GFCI 50Hz

06/21/2010 11:59 PM

The exact data as follows:

Brand: Power Breaker RCD

Rated Voltage: 230V, 50Hz

Max. operating current: 13A resistive 3A inductive

Max. load: 3KW

Rated trip current: 30mA Trip speed: 40mS

In our country we are using, 220V, 60Hz

What are the difference between RCD and GFCI

Thank you for your reply

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#4
In reply to #3

Re: GFCI 50Hz

06/22/2010 12:27 AM

RCD = residual current device (?). GFCI = ground fault circuit interrupter. Different words for essentially the same thing. The RCD's rating of 30ma (suited to an industrial breaker) is not as sensitive as residential GFCIs rated at 6ma, but the idea is identical.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Participant

Join Date: Sep 2007
Posts: 4
#5
In reply to #4

Re: GFCI 50Hz

06/22/2010 12:58 AM

Thank you,

We will use the RCD for small power tools. Is there any problem if I use 230V, 50Hz to a power supply of 220V, 60Hz?

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#6
In reply to #5

Re: GFCI 50Hz

06/22/2010 1:44 AM

If your application involves timer motors, or other like items that depend on frequency, your speeds will be off by a factor of 5:6 or 6:5.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#7

Re: GFCI 50Hz

06/22/2010 11:34 AM

Besides the question of if the device will work... there may also be a legal issue with using this device.

In Canada, you could only use this device "legally" if the device was dual rated for use with a supply source of 50 and 60hz. If it does not carry certification for use on a 60hz source, you would not be allowed to use it.

This may or not be an issue for you. Only referring to your local rules and regulations will answer this question.

As this is a life safety device, you may want to have your ducks in a pretty little straight line.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".