Anonymous Poster

400V 3ph / 415V 3ph

06/23/2010 6:48 AM

Dear All:

I have imported Japanese motors which are rates as 400V/3Ph/50Hz. Whereas Indian standard Voltage is 415V/3Ph/50Hz. Can I use these motors? Most efficiently?

Cheers,

Hemant

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Guru
Popular Science - Weaponology - New Member United Kingdom - Member - New Member

Join Date: May 2007
Location: Harlow England
Posts: 16512
Good Answers: 670
#1

Re: 400V 3ph / 415V 3ph

06/23/2010 6:51 AM

It would seem to me that the 3.75% difference is well within the normal supply variation and tolerances of winding inductance/resistance etc.
Del

__________________
health warning: These posts may contain traces of nut.
Reply Good Answer (Score 2)
Power-User

Join Date: May 2008
Posts: 136
Good Answers: 2
#2

Re: 400V 3ph / 415V 3ph

06/23/2010 7:06 AM

hi dear!

I think the motors in question will work without any problems, but, why don't you try out one of them?

Regards...........

__________________
Just live and .. Learn!!
Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#3

Re: 400V 3ph / 415V 3ph

06/23/2010 7:20 AM

415V is usually nearer 400V in most places, unless you have HT supply from the utility. You need not worry. Use good protective relays and contactors though.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply
Associate

Join Date: May 2010
Posts: 31
Good Answers: 3
#4

Re: 400V 3ph / 415V 3ph

06/23/2010 9:41 AM

Usually in small L V motor we have tolerance of 10 % in Voltage variation. In HT this

Tolerance in Voltage variation is very less than 10 % ( approximately 3%)

( What is the Nameplate Rating of Ur motor ?)

In Ur case U have 400 V/ 3 P h /50 Hz motors. These motors can be operated at 360

V to 440 V. If these voltage limits are to be crossed either Power consumption will

increases or motor will loose the torque. However motor gives their best efficiency at

the rated voltage.

In Ur case the variation is 3.75 % which is highly acceptable.

I think there will no effect on the efficiency of the motor.

At 415 V

Motor RPM will increases slightly ( Up to 10 RPM with respect to RPM against 400 V)

Power Factor of the motor decreases slightly. ( Up to 0.02 with respect to P.F

against 400 V )

Current will increases very slightly.

These motors can safely be used at 415 V system

Reply Score 1 for Good Answer
Associate

Join Date: Mar 2010
Location: vinh city. VIET NAM
Posts: 36
#5

Re: 400V 3ph / 415V 3ph

06/23/2010 9:52 PM

i think 415-400=15v < 5% of 415 you can use motor for production, if you worry about that try with one with full load and check current ( I)

Reply Off Topic (Score 5)
Reply to Forum Thread 5 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Ali18 (1); kvsridhar (1); Salar (1); user-deleted-1105 (1); vankhoa226 (1)

Previous in Forum: What is the Maximum Rating of a Diesel Generator?   Next in Forum: Calculate CT Burden
You might be interested in: DC Motors, Stepper Motors, AC Motors

Advertisement