Calculate CT Burden

06/23/2010 9:04 AM

Hi

I have a protection CT dismantled from 33 kv busbar. I am trying to plot the frequency response of that CT. Unfortunately there is no information about the CT apart from CT ratio which is 200/5 A. Since I don't have the VA information I am not able to proceed to calculate the burden value in ohms. What I can do is plot the V-I (Excitation Characteristics). My question here is from V-I characteristics and CT ratio, Is there any methods to get CT burden?

Thanks in advance

Faisal

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User

Join Date: May 2010
Location: longo tempo dos macaco do pilas. Felizment.
Posts: 251
#1

Re: Calculate CT Burden

06/23/2010 4:42 PM

A CT will measure Current not frequency.

The CTR is the amount of current from source to device (The CT.)

CT is a current transformer and a CT ratio (CTR.) is a Current Transfer Ratio.

A CT from a 33KV bar will probably be wound for 50 or 60 HZ.

You can check the frequency response by testing the Q of the CT.

__________________
I am a deeply religious nonbeliever - this is a somewhat new kind of religion. Albert Einstein
Register to Reply
Participant

Join Date: Jun 2010
Posts: 3
#2
In reply to #1

Re: Calculate CT Burden

06/23/2010 5:02 PM

Thanks

Of course CT can't be used for measuring frequency.All devices has its own frequency response.Frequency response of CT depends mainly the core material's initial permeability. My requirement is How to get the CT burden from V-I characteristics and CT ratio.

Cheers

Faisal

Register to Reply
Power-User

Join Date: May 2010
Location: longo tempo dos macaco do pilas. Felizment.
Posts: 251
#4
In reply to #2

Re: Calculate CT Burden

06/24/2010 8:16 AM

There will be a current transfer ratio.

Pass 1 amp into the source measure the output of the CT and then pass 10 amps through the source and measure the output CT's I think have a fairly linear output and you can plot the expected graph.

__________________
I am a deeply religious nonbeliever - this is a somewhat new kind of religion. Albert Einstein
Register to Reply
Power-User

Join Date: Oct 2008
Location: Jakarta Indonesia
Posts: 123
Good Answers: 7
#3

Re: Calculate CT Burden

06/23/2010 9:48 PM

Dear all,

The CT is for protection and 200/5A, excitation curve is available.

Let me say, half of knee point voltage (V) x 5 (A) is your practical and usable CT burden.

My assumption is that at the half of the knee point voltage, the CT is not saturated yet, and this voltage is induced when the above VA load is connected to the CT and when the secondary current 5A.

Regards

__________________
Akihito Shigeno @ JGC-Indonesia
Register to Reply Score 1 for Good Answer
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#5
In reply to #3

Re: Calculate CT Burden

06/24/2010 9:20 AM

A agree with Akihito Shigeno. But there is one major concern here. Is this CT to be used for the purpose of measuring or protection? If it is measuring, half of knee point voltage can be considered but if it is protection CT, at best 10% of knee point voltage (for nP10 class or 5% for nP20 class etc., where n is the accuracy level) shall be considered. However, without knowing detail data for the CT, I wouldn't recommend to use this CT for the protection purpose. You can use this CT if it is a course measuring purpose (where the accuracy is not so important).

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply Score 1 for Good Answer
Participant

Join Date: Jun 2010
Posts: 3
#6
In reply to #5

Re: Calculate CT Burden

06/24/2010 9:49 AM

Hi Msamad

Many Thanks

I understand from your reply that , under normal operating condition ,protection CT is allowed to operate 10 % of Knee point region in the excitation characteristics. Which means when the fault current is 10 times more than the normal operating current , CT won't saturate. Is that what do you mean?

Regards

Faisal

Register to Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#7
In reply to #6

Re: Calculate CT Burden

06/24/2010 10:46 AM

Yes, you understood correctly. However, the % value depends on CT class. As I mentioned earlier it is 10% of the knee point voltage for class nP10, 5% of the knee point voltage for class nP20. See http://cr4.globalspec.com/thread/43440 for more detail about the CT class.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply
Power-User

Join Date: Oct 2008
Location: Jakarta Indonesia
Posts: 123
Good Answers: 7
#8
In reply to #5

Re: Calculate CT Burden

06/24/2010 9:11 PM

I agree with msamad.

If a half of knee point voltage is selected to calculate CT secondary load, as is assumed above, and a fault current is 20 times the CT rating, CT will be saturated very much.

So, I take the 5% of knee point voltage x 5A as practical burden.

Thank you for pointing out my error.

Regards

__________________
Akihito Shigeno @ JGC-Indonesia
Register to Reply
Register to Reply 8 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Akihito Shigeno (2); msamad (2); pfaisalbe (2); portugalphilip (2)

Previous in Forum: 400V 3ph / 415V 3ph   Next in Forum: Induction Motor Efficiency Vs Its Power Factor

Advertisement