Current Carrying Capacity of Solid Bus Bar

06/26/2010 1:16 PM

What is the maximum current carrying capacity of a solid bus bar 30x6mm Tin plated copper Ambient Temperature 50 Dec C

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#1

Re: Current Carrying Capacity of Solid Bus Bar

06/26/2010 1:59 PM

Per NEC, the current rating is 1.55 Amps per sq. mm (1000 Amps per sq inch) for copper bar.

These links will also help (though the busbars here are dimensioned in inches).

http://www.husseycopper.com/production/products/bar/

http://www.copper.org/applications/busbar/ampacity/bus_table3.html

There are also many threads available in this forum on the same topic, please search.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Reply
Anonymous Poster
#3
In reply to #1

Re: Current Carrying Capacity of Solid Bus Bar

06/27/2010 12:05 PM

msamad,thanks for your post.

As you said ,according to NEC the current rating is 1000 Amps per sq inch,so at 500A the area should be 1/2 sq inch.

But the tables you referred to show for 500A the area should be only 1/4 sq inch.

Why that difference?

Reply
Anonymous Poster
#6
In reply to #3

Re: Current Carrying Capacity of Solid Bus Bar

06/27/2010 2:26 PM

The difference is because of

The current ratings mentioned in the links are most probably considered in open air but the NEC mentioned the current ratings of the copper bars in the sheet metal gutters. See the NEC quote

"The current carried continuously in bare copper bars in sheet metal auxiliary gutters shall not exceed 1.55 amperes/mm2 (1000 amperes/in.2) of cross section of the conductor. For aluminum bars, the current carried continuously shall not exceed 1.09 amperes/mm2 (700 amperes/in2) of cross section of the conductor."

- MS

Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#7
In reply to #6

Re: Current Carrying Capacity of Solid Bus Bar

06/27/2010 3:07 PM

The above post (#6) has been submitted without the login and posted by Guest. I had to restart (hard stop) my laptop after it was frozen and somehow the cookie was lost.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Reply
Power-User
India - Member - design engineer Engineering Fields - Electrical Engineering - New Member United Arab Emirates - Member - New Member

Join Date: Feb 2010
Location: dubai,mangalore,bangalore.....
Posts: 145
Good Answers: 8
#2

Re: Current Carrying Capacity of Solid Bus Bar

06/27/2010 4:18 AM

I= (7.7 *(A^(0.5))*(P^(0.39))))

for an ambient temp of 40-50c

where

A - Cross sectional area of conductor in sq.mm

P - Perimeter of conductor in mm.

__________________
shamith gambhir, electrical engineer
Reply Score 1 for Good Answer
Anonymous Poster
#4
In reply to #2

Re: Current Carrying Capacity of Solid Bus Bar

06/27/2010 12:31 PM

Is this formula for AC or DC current ?

Reply
Anonymous Poster
#5
In reply to #4

Re: Current Carrying Capacity of Solid Bus Bar

06/27/2010 2:11 PM

Good question.

Reply
Power-User
India - Member - design engineer Engineering Fields - Electrical Engineering - New Member United Arab Emirates - Member - New Member

Join Date: Feb 2010
Location: dubai,mangalore,bangalore.....
Posts: 145
Good Answers: 8
#8
In reply to #4

Re: Current Carrying Capacity of Solid Bus Bar

06/28/2010 12:11 AM

both

__________________
shamith gambhir, electrical engineer
Reply
Anonymous Poster
#9

Re: Current Carrying Capacity of Solid Bus Bar

06/28/2010 3:28 AM
Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#10

Re: Current Carrying Capacity of Solid Bus Bar

10/04/2010 1:33 AM

You should know the quality(conductivity) and emissivity of material and refer manufacturer's literature

__________________
pnaban
Reply
Reply to Forum Thread 10 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (5); msamad (2); pnaban (1); SHAMITHGAMBHIR1 (2)

Previous in Forum: Electrical Engineering - Calculate kwh/year   Next in Forum: Earth Fault Tripping

Advertisement